As you can see, the temperature looks fine, but Humidity is getting a lot of 'out of range' values. It's not just 1 sensor, this is happening to them all.
Checked the 1-wire bus voltage and it's 4.92v - plenty close enough to 5v.
Checked all the connections are nice and tight (besides, I haven't touched anything in the cabinet).
I refuse to believe that every one of these sensors has developed the exact same fault at pretty much the exact same time.
These devices are represented in Loxone as DS2438 devices and the humidity values are read from the Vad input and scaled appropriately. When I look at the 1-wire monitor I can see Vad being reported as spurious. Ie. in the graph above I can leave the Loxone 1-wire monitor running and wait for a bad value to appear, and when it does can then go look in the 1-wire monitor and find the bad Vad value that was read.
I refuse to believe that somewhere in the wiring there is a fault that causes only the Vad value in transmitted packets to be corrupted and somehow Loxone is still accepting said packet (surely a CRC error would occur in any transmission error and Loxone would reject the entire reading).
Given all this it looks to me that there's something wrong in the Loxone Extension or the Miniserver itself. Either hardware or software, that is corrupting these Vad values. I have no idea why, but that seems the only logical explanation. I did changed the config this morning but hours before this fault started and absolutely nothing to do with these 1-wire inputs.
Any ideas?
Cheers,
Robin