> Thanks Dave. I followed your instruction and made required changes as per
> your advice. After making these changes exhaust fan is not getting
> activated:( i tried with everything but not able to make it activated.
> please find an input file for the same.
>
> Any help would be highly appreciated!
>
> On Mon, Jul 16, 2012 at 7:53 AM, Dave McGill <
dwt.m...@gmail.com> wrote:
>
>> Hi Javed,
>>
>> ...
>>
>>>
>>> 1. How can i exhaust the smoke out in ambiance/outdoor?
>>>
>> It appears that the smoke is accumulating in the space above your exhaust
>> vent. If you place OPEN vents on the domain boundaries above the vent,
>> then
>> the smoke will dissipate into the atmosphere. As an alternative, if you
>> placed your existing vent on the outer wall, the same thing would happen.
>>
>> In either case, you should consider adding a source of make-up air to
>> your
>> basement.
>>
>>
>> 2. Is it possible to stop the fire at some point and exhaust should
>>> work continuous to take out stale air outside the computational domain.
>>>
>> Yes, you can control the fire and the exhaust independently.
>>
>>
>>
>>> Dave
>>>
>> --
>> You received this message because you are subscribed to the Google Groups
>> "FDS and Smokeview Discussions" group.
>> To view this discussion on the web visit
>>
https://groups.google.com/d/msg/fds-smv/-/RpC69_sfcywJ.
>> To post to this group, send email to
fds...@googlegroups.com.
>> To unsubscribe from this group, send email to
>>
fds-smv+u...@googlegroups.com.
>> For more options, visit this group at
>>
http://groups.google.com/group/fds-smv?hl=en.
>>
>
>
>
> --
>
>
> Javed Iqbal, LEED AP, CEA
> Energy Analyst
>
> --
> You received this message because you are subscribed to the Google Groups
> "FDS and Smokeview Discussions" group.
> To post to this group, send email to
fds...@googlegroups.com.
> To unsubscribe from this group, send email to
>
fds-smv+u...@googlegroups.com.
> For more options, visit this group at
>
http://groups.google.com/group/fds-smv?hl=en.
>
>
--
You received this message because you are subscribed to the Google Groups "FDS and Smokeview Discussions" group.
To post to this group, send email to
fds...@googlegroups.com.
To unsubscribe from this group, send email to
fds-smv+u...@googlegroups.com.
For more options, visit this group at
http://groups.google.com/group/fds-smv?hl=en.