Basement ventilation problem

98 views
Skip to first unread message

Javed Iqbal

unread,
Jul 16, 2012, 9:31:48 AM7/16/12
to fds...@googlegroups.com
Hi,

 I am trying to model Basement Exhaust for 10X10X3m room. It works fine and  cross checked through smokeview on the volumetric flow rate (m3/sec) by extending computational domain up (refer pics). i have following doubts:

1. How can i exhaust the smoke out in ambiance/outdoor?
2. Is it possible to stop the fire at some point and exhaust should work continuous to take out stale air outside the computational domain.

Thanks in Advance!



Inline image 2



--


Javed Iqbal, LEED AP, CEA
Energy Analyst   








Picture2.jpg

Dave McGill

unread,
Jul 16, 2012, 10:53:57 AM7/16/12
to fds...@googlegroups.com
Hi Javed,

...

1. How can i exhaust the smoke out in ambiance/outdoor?
It appears that the smoke is accumulating in the space above your exhaust vent. If you place OPEN vents on the domain boundaries above the vent, then the smoke will dissipate into the atmosphere. As an alternative, if you placed your existing vent on the outer wall, the same thing would happen.

In either case, you should consider adding a source of make-up air to your basement.


2. Is it possible to stop the fire at some point and exhaust should work continuous to take out stale air outside the computational domain.
Yes, you can control the fire and the exhaust independently.



Dave

Mohamed ASSAL

unread,
Jul 16, 2012, 2:56:48 PM7/16/12
to fds...@googlegroups.com
Hi Javed
Is it possible to stop the fire at some point and exhaust should work continuous to take out stale air outside the computational domain.

Use the RAMP Option to stop the Fire, 

Mohamed

Javed Iqbal

unread,
Jul 16, 2012, 4:26:49 PM7/16/12
to fds...@googlegroups.com
Thanks Dave. I followed your instruction and made required changes as per your advice. After making these changes exhaust fan is not getting activated:( i tried with everything but not able to make it activated. please find an input file for the same.

Any help would be highly appreciated!

--
You received this message because you are subscribed to the Google Groups "FDS and Smokeview Discussions" group.
To view this discussion on the web visit https://groups.google.com/d/msg/fds-smv/-/RpC69_sfcywJ.
To post to this group, send email to fds...@googlegroups.com.
To unsubscribe from this group, send email to fds-smv+u...@googlegroups.com.
For more options, visit this group at http://groups.google.com/group/fds-smv?hl=en.
Exhaust_fan_Run.fds

dr_jfloyd

unread,
Jul 16, 2012, 4:39:36 PM7/16/12
to fds...@googlegroups.com
Please review the User's Manual and carefully review your input file:

Section 7.2.1 Basics:

If two obstructions overlap at one or more faces, the one listed last in the input file takes precedence over
the one listed first.

Your input file:
&OBST XB=8.5,9.5,8.5,9.5,4.0,4.0, SURF_ID='FAN'/ Obstruction
&OBST XB=0.0,10.0,0.0,10.0,4.0,4.0, SURF_ID='INERT'/ Obstruction

Also your input file contains a few lines later:
&VENT SURF_ID='OPEN', XB=8.5,9.5,8.5,9.5,4.0,4.0/ Vent

so even if you hadn't replaced your FAN with the INERT OBST line, this VENT line replaces it with OPEN.


On Monday, July 16, 2012 4:26:49 PM UTC-4, jd wrote:
Thanks Dave. I followed your instruction and made required changes as per your advice. After making these changes exhaust fan is not getting activated:( i tried with everything but not able to make it activated. please find an input file for the same.

Any help would be highly appreciated!
On Mon, Jul 16, 2012 at 7:53 AM, Dave McGill <> wrote:
Hi Javed,

...

1. How can i exhaust the smoke out in ambiance/outdoor?
It appears that the smoke is accumulating in the space above your exhaust vent. If you place OPEN vents on the domain boundaries above the vent, then the smoke will dissipate into the atmosphere. As an alternative, if you placed your existing vent on the outer wall, the same thing would happen.

In either case, you should consider adding a source of make-up air to your basement.


2. Is it possible to stop the fire at some point and exhaust should work continuous to take out stale air outside the computational domain.
Yes, you can control the fire and the exhaust independently.



Dave

--
You received this message because you are subscribed to the Google Groups "FDS and Smokeview Discussions" group.
To view this discussion on the web visit https://groups.google.com/d/msg/fds-smv/-/RpC69_sfcywJ.
To post to this group, send email to fds...@googlegroups.com.
To unsubscribe from this group, send email to fds-smv+unsubscribe@googlegroups.com.

For more options, visit this group at http://groups.google.com/group/fds-smv?hl=en.

Javed Iqbal

unread,
Jul 17, 2012, 12:53:31 AM7/17/12
to fds...@googlegroups.com
Thanks for your valuable feedback. I will proceed as per your guidance.

To view this discussion on the web visit https://groups.google.com/d/msg/fds-smv/-/6snWEoxU96sJ.

To post to this group, send email to fds...@googlegroups.com.
To unsubscribe from this group, send email to fds-smv+u...@googlegroups.com.

For more options, visit this group at http://groups.google.com/group/fds-smv?hl=en.

Mohamed ASSAL

unread,
Jul 17, 2012, 5:31:57 AM7/17/12
to fds...@googlegroups.com
Hi Javed I will send you the input this weekend.

Mohamed