Hello,
I also used FDS for back layering canculation of one tunnel. the air velocity of jet fan is hight, about 20m/s but it is only correct around the fan area. Far from fan, the air velocity is lower so the smoke back layering could happend. So the position of fans must be appropriate to create the air velocity in every points of cross section that are higher than the critical velocity to prevent the back layering!
On 10-07-2013, at 21:38, dr_jfloyd <
drjf...@gmail.com> wrote:
> You put in some inputs that are supposed to represent the behavior of the jet fans. What have you done to determine if those inputs do indeed represent the behavior of the fans? Have you looked to see if jet fans entrain the correct amount of air? Have you done a grid study to determine if an 0.5 m grid is sufficient?
>
> --
> You received this message because you are subscribed to the Google Groups "FDS and Smokeview Discussions" group.
> To unsubscribe from this group and stop receiving emails from it, send an email to
fds-smv+u...@googlegroups.com.
> To post to this group, send email to
fds...@googlegroups.com.
> To view this discussion on the web visit
https://groups.google.com/d/msgid/fds-smv/3ca197e9-cb64-4bc9-ba95-6e5a2abea93b%40googlegroups.com.
> For more options, visit
https://groups.google.com/groups/opt_out.
>
>