I currently have a problem with the simulation of some jet fans in a tunnel.
In a previous simulation I have blown air with a velocity of about 5 m/s into the tunnel by setting a VENT to the entrance of the tunnel. The smoke was blown out of the other side of the tunnel, there was no backflow or backlayering effect.

Now I want to simulate this case with two triplets of jetfans. Each jet fan has a velocity of 5.95 m/s. The problem is, that the smoke flows back against the jet fans and exits at both end of the tunnel.

What is the problem or what is wrong in my simulation?

Thanks a lot!

Greetings
Ronny
jetfan.fds

dr_jfloyd

unread,
Jul 9, 2013, 12:56:15 PM7/9/13
to fds...@googlegroups.com
The two are not at all equivalent. When you specify a 5 m/s inlet on the tunnel, you are saying that no matter what back pressure and ceiling jet the fire creates, that there will always be 5 m/s entering the tunnel. This is not a realistic boundary condition. With the jet fans you are imposing a pressure condition. Each fan can create some amount of pressure and if the fire is more, then back flow will happen.
Message has been deleted

Ronny Olbert

unread,
Jul 10, 2013, 7:56:28 AM7/10/13
to fds...@googlegroups.com
Thanks for your answer!

The situation you described makes sense. I tried it again with a velocity of 15 m/s (exemplary) and there was no back flow or back layering effect.
But in other simulations of my case and in literature disclosures it is said, that back flow and backlayering effect will be avoid by velocities of about 2 - 3 m/s. From these values I am far away.

Is there anything else I'm doing wrong?

Greetings
Ronny

dr_jfloyd

unread,
Jul 10, 2013, 8:02:21 AM7/10/13
to fds...@googlegroups.com
What have you done to validate that your grid size and method of implementing the jet fans results in an adequate model of the tunnel conditions?

Ronny Olbert

unread,
Jul 10, 2013, 10:26:15 AM7/10/13
to fds...@googlegroups.com
Currently I placed the jet fans according to the information from the real fire experiment. The coarse grid size of 0.5 m I have chosen to minimize the computational capacity.



Am Dienstag, 9. Juli 2013 16:04:49 UTC+2 schrieb Ronny Olbert:

dr_jfloyd

unread,
Jul 10, 2013, 10:38:12 AM7/10/13
to fds...@googlegroups.com
You put in some inputs that are supposed to represent the behavior of the jet fans. What have you done to determine if those inputs do indeed represent the behavior of the fans? Have you looked to see if jet fans entrain the correct amount of air? Have you done a grid study to determine if an 0.5 m grid is sufficient?

Nguyen Tuan Ngoc

unread,
Jul 10, 2013, 12:43:52 PM7/10/13
to fds...@googlegroups.com
Hello,
I also used FDS for back layering canculation of one tunnel. the air velocity of jet fan is hight, about 20m/s but it is only correct around the fan area. Far from fan, the air velocity is lower so the smoke back layering could happend. So the position of fans must be appropriate to create the air velocity in every points of cross section that are higher than the critical velocity to prevent the back layering!


On 10-07-2013, at 21:38, dr_jfloyd <drjf...@gmail.com> wrote:

> You put in some inputs that are supposed to represent the behavior of the jet fans. What have you done to determine if those inputs do indeed represent the behavior of the fans? Have you looked to see if jet fans entrain the correct amount of air? Have you done a grid study to determine if an 0.5 m grid is sufficient?
>
> --
> You received this message because you are subscribed to the Google Groups "FDS and Smokeview Discussions" group.
> To unsubscribe from this group and stop receiving emails from it, send an email to fds-smv+u...@googlegroups.com.
> To post to this group, send email to fds...@googlegroups.com.
> To view this discussion on the web visit https://groups.google.com/d/msgid/fds-smv/3ca197e9-cb64-4bc9-ba95-6e5a2abea93b%40googlegroups.com.
> For more options, visit https://groups.google.com/groups/opt_out.
>
>

Mohamed ASSAL

unread,
Jul 10, 2013, 6:27:08 PM7/10/13
to fds...@googlegroups.com
Hi Ronny,

Increasing jet fan air velocity may solve your problem, but you should
think that there are standards for that, and also the human comfort
inside the tunnel is an important factor.

Cheers Mohamed.

2013/7/10, Nguyen Tuan Ngoc <tuann...@gmail.com>:
> https://groups.google.com/d/msgid/fds-smv/2E4006C2-6241-4BD6-B114-4DDA414FAF90%40gmail.com.
> For more options, visit https://groups.google.com/groups/opt_out.
>
>
>


--
Mohamed ASSAL
Manager and Representative of ASCOMP GmbH Switzerland for North Africa.
Rue Hassiba Ben Bouali N°4 Rouiba Algeria.
Tel: +213 790 541 241
Email: as...@ascomp.ch
Company website: www.ascomp.ch
ASCOMP Connecting Science and Technology

Ronny Olbert

unread,
Jul 11, 2013, 3:06:00 AM7/11/13
to fds...@googlegroups.com
Thanks to all for your answers!

After your tips and some reflection, I realized that this can not work. I ignored the degradation of the velocity. If i set a velocity of about 5 m/s, this value will not be constant over the entire tunnel. I think this is what you mean? The 5 m/s I only have close to the jet fans.