Excellent, thanks for your thoughts and recommendation on the NEMA 6-50.
I'm in no way trying to dispute your second paragraph, but just curious
as to the source of that? Electrical code? Underwriters Labs? other EVSE manufacturers? and did you mean above 40 A
continuous (i.e. above 50 A breaker) it must go to hard-wired? or did
you mean over 32 A continuous (above 40 A breaker) it must be hard-wired?
Also
googling a bit more I found a Honda-Leviton Q and A page (not that it
necessarily applies to all EVSEs or to Canada),
https://honda.leviton.com/infocenter/evse-fact-sheet, but it does speak
rather generally about electrical code and says, among other things:
1.
a 50 A outlet is allowed in a garage (which begs the question is a 50 A
outlet allowed outdoors... that page doesn't say, RV examples certainly
exist)
2. if over 60 A, it needs "a disconnect" which I suppose is a big red throw switch to cut the power
3. an EVSE (or at least they're talking about theirs) can only be mounted outdoors if it is hard-wired
So
I'm not sure if point 3 is implying that theirs IS over 40 A, so for it
to also be outdoors, it must be hard-wired (thus it would just be an
application of your point). Or if they mean there is some other
parameter of their EVSE or other rule in the code that prevents theirs
from being used outdoors unless hard-wired.
It sounds like hard-wired is actually likely to make an electrical inspector happier than a cord-and-plug setup, and since I was leaning that way anyway for other reasons, that's fine.
Anyway interesting stuff. Thanks again for your reply.
Martin