Hi,
Now I'm done with all my CAT7 runs to each room for tree devices door/window contacts (using the spare pairs) I've moved onto 1-wire.
I've seen it mentioned that minimum AWG 22 is recommended for 1-wire, also somewhere it suggested that unshielded cat cable was preferred, but I'm using the CAT7 cable (AWG 23) I have on-site. I am avoiding parasitic wiring.
I have my sensors in clusters of 2-3 and each (Loxone) temperature sensor has a 3m lead. I'm using CAT7 to hop from cluster to cluster creating a "bus with short stubs" topology. The only caveat is that, in most places, the stubs form a small star with 5-way's connected to bus-in, bus-out, and the 2-3 sensor leads.
So far I'm up to about 40m and have connected 8 sensors. I am hoping though, to get a full 20 sensors on the bus and not be limited by length, even if I end up with around 150m.
At the moment I'm using the blue pair for Data/GND and the green core for VDD. I haven't (yet) done anything with the green-white core or the shielding, but I may experiment with this later today.
Loxone discovers and gets temperature readings from all sensors easily, but I'm seeing a fair number of CRC errors from some of the sensors. It seems that the furthest sensors give the most errors, but some of the closer ones also give random CRC errors too.
Any thoughts? Has anyone got a tried-and-tested approach to best using CAT7 cores and shielding to get the best length/reliability? Or has anyone found that unshielded CAT5/6 is actually better?
Thanks!