I am just about to pour a foundation for an addition to my house, one
side of which is about 6' away from the base of the tower. The
addition will be 20' X 26' and I have just run about 130' (in two 65'
rows about six inches apart) of 5/8" reinforcing rods in the footer
trenches. Would I be better off grounding the tower to the steel
re-bars in the footers or to a copper grounding rod driven into the
ground at the base of the tower... or both? If both, should I use a
different connecting wire for each and would it be better to drive the
grounding rod into the ground at the bottom of the footer, even though
it is a little further away from the tower or as close to the bottom
of the tower as possible? Any advice and hints would be greatly
appreciated. -Bruce
I put 3, 8' ground rods around my tower. Each spaced about 8' from each
other. The rods are connected to one leg of the tower by short, lengths of
#6 copper wire. Then I ran #6 wire back to the house and connected it to the
house ground. All this was required by building code in my area.
I bonded the shields of the coax to the tower at the point they came away
from the tower and used a lighting arrestor on the rotor cable at the point
it came off the tower. At the point the coax entered the house I put
lighting arrestors on the coax connected to yet another ground rod. Check
out the polyphaser site for good information on how to do this at
http://www.polyphaser.com/. If the tower is aluminum, then when you connect
the ground wires to it, use ground blocks that are rated for aluminum/copper
connections.
--
John Passaneau
Penn State University, State College Pa.
W3JXP
w3...@arrl.net
"Bruce Fraleigh" <brucef...@hotmail.com> wrote in message
news:3fb5609a.02042...@posting.google.com...
Bill KC9CS
"Bruce Fraleigh" <brucef...@hotmail.com> wrote in message
news:3fb5609a.02042...@posting.google.com...
Bill KC9CS
"John Passaneau" <jx...@psu.edu> wrote in message
news:aa3oh7$1b...@r02n01.cac.psu.edu...
I would NOT, under ANY circumstances tie your tower grounding to the
rebar in your foundation footers (or a slab, etc.) ... unless you'd like
them
(the footers, slab, etc.) to explode if you take a strike ... you won't get
much
of a ground through the concrete, and all that energy will be trying to get
(flash)
from those rebars embedded in the concrete to (real) ground ... I can
envision
the results as being VERY dramatic (in a disastrous way).
Carl - wk3c
Actually the rebar makes a pretty good ground. Concrete is a good
conductor. It holds
moisture where the ground around it may be dryer. It can often times
be a better ground than
the ground rods driven in the soil. It is called a Ufer ground system.
Named after the guy that
discovered it. It should not be the only ground but it can greatly
augment your ground rods.
When towers are mounted on concrete they are usually bolted to J
bolts that go down into the
concrete. When a lightning strike occurs a large amount of the current
goes into the concrete by
the J bolts. Some people bury several feet of tower in concrete. Just
because you have ground
rods tied to the tower does not mean that a large amount of the energy
will not also go into the
concrete.
The Polyphaser site has information on Ufer grounds.
73
Gary K4FMX
Polyphaser actually recommends using the rebar in a footer to AUGMENT the
tower ground, the idea being the lower the resistance the better. One way to
lower the resistance is to expand the ground system over many paths --
divide and conquer. In the book by PolyPhaser "Lighting Protection and
Grounding Solutions for Communication Sites", the followup to the book "The
Grounds for Lightning Protection" they make numerous reference to use of
Ufer grounds for augmentation of tower grounds.
Pages 11, 32-33, amongst others. Finally on page 81 is my favorite
reference: " Those who think that three 8 ft ground rods around the base of
a tower is a good grounding system are on the right track only if the tower
will be erected on the beach at high tide".
Finally, from the Ufer ground document on Polyphaser's website in the
technical information section:
"Concrete is a fair conductor and can be used safely and effectively to
augment your tower grounding system."
"It is a common misconception to think that a lightning strike will blow up
a concrete pad. However, consider
first, a myth-perpetuating case of an improperly designed system where the
tower leg "J"-bolts are imbedded
directly into the concrete pad. In this case, due to the poor nature of the
tower ground system, each of these Jbolts
will actually share a significant amount of strike current which in turn
will flow through the concrete. Since
the surface area interface between the J-bolts and the concrete is small,
the surge current density is very large.
The corresponding heat generated by the energy transfer can turn the
concrete moisture into steam and possibly
crack the pad. We have only seen this happen once on a mountain top in the
Nevada desert. However, a
few poorly implemented occurrences can give a valuable technique a bad
reputation.
If during construction, all of the rebar in the concrete pad becomes an
integral part of your ground system, the
overall surge current density will be several orders of magnitude lower than
the myth-perpetuating case above.
With the surge current distributed over all of the rebar there will be
little to no opportunity to develop the
temperatures necessary to vaporize the imbedded moisture. The pad will not
crack."
"As well as the Ufer ground works, it should not be used alone. We always
recommend that radials or radials
with ground rods be used as the main ground system and that the Ufer ground
be used to further reduce the
ground resistance of your system. Many tests have been done, dating back to
1968, which prove that the Ufer
is a safe and very effective way of augmenting a ground system."
My pool deck has a ground connection to the wire mesh in the concrete slab.
Reason? In the event I put up an aluminum screen cage over my Florida pool
( I live in west central Florida...right in the heart of lightning country)
it was to be connected to the ground in the wire mesh. If it was a risk of
'explosion' the design would have been otherwise. By the way...the entry and
exit ladders and handrails are also tied directly to the wire mesh....by
code.
I think perhaps more research by those who don't understand proper grounds
is warranted.
Bill KC9CS
I stand corrected ... Polyphaser has a very good reputation and
if they say it's OK, I trust that ... I had envisioned the currents trying
to flash from rebar through concrete and causing flash steam explosions.
Apparently I was underestimating the ability of concrete to
conduct the current.
I agree that 3 ground rods is not enough ... I just had concerns
about the concrete being part of the grounding equation.
Carl - wk3c
"Bill Otten" <res0...@verizon.net> wrote in message
news:xAkx8.19285$uV.1...@nwrddc01.gnilink.net...
73,
Bill KC9CS
I`ve been on the tops of many high buildings with my microwave
installations. Ubiquitous are the "air terminals" (lightning rods) at
frequent intervals around the edges. Their purpose? To prevent chunks of
building material from being knocked loose by lightning and into the
streets. A lightning strike to concrete may produce instant superheated
steam from moisture retained in all concrete and blast the material
asunder. It happens somewhere every day.
I`ve also erected countless communications towers. I`ve protected the
reinforced concrete bases of these towers by a separate ground rod
connected with a low inductance, low resistance cable or strap to each
tower leg. I made an exception in Tierra del Fuego, which has never seen
a lightning flash nor heard a thunder clap. But, elsewhere, the rebars
got bypassed by external lightning grounds outside the tower bases.
Never had a split tower base. Have heard of unprotected tower bases
built by others that were split. That settles it for me forever.
Best regards, Richard Harrison, KB5WZI