Asurge protector limits the voltage supplied to the electrical devices to a certain threshold, by short-circuiting current to ground or absorbing the spike when a transient occurs, thus avoiding damage to the devices connected to it.

Key specifications that characterize this device are: the clamping voltage, or the transient voltage at which the device starts functioning, the Joule rating, a measure of how much energy can be absorbed per surge, and the response time.


The terms surge protection device (SPD) and transient voltage surge suppressor (TVSS) are used to describe electrical devices typically installed in power distribution panels, process control systems, communications systems, and other heavy-duty industrial systems, for the purpose of protecting against electrical surges and spikes, including those caused by lightning. Scaled-down versions of these devices are sometimes installed in residential service entrance electrical panels, to protect equipment in a household from similar hazards.[2]


In an AC circuit, a voltage spike is a transient event, typically lasting 1 to 30 microseconds, that may reach over 1,000 volts. Lightning that hits a power line can cause a spike of thousands of volts. A motor when switched off can generate a spike of 1,000 or more volts. Spikes can degrade wiring insulation and destroy electronic devices like light bulbs, battery chargers, modems, TVs, and other consumer electronics.


Spikes can also occur on telephone and data lines when AC main lines accidentally connect to them or lightning hits them, or if the telephone and data lines travel near lines with a spike and the voltage is induced.


A long-term overvoltage surge, lasting seconds, minutes, or hours, caused by power transformer failures such as a lost neutral or other power company error, are not protected by transient protectors. Long-term surges can destroy the protectors in an entire building or area. Even tens of milliseconds can be longer than a protector can handle. Long-term surges may or may not be handled by fuses and overvoltage relays.


A building's wiring adds electrical impedance that limits the surge current that reaches the loads when a voltage transient arrives at the service entrance (the point where the supply company's wiring enters a property). There is less surge current at longer wire distances and where more impedance is present between the service entrance and the load.[3]


Category A loads are more than 60 feet of wire length from the service entrance to the load. Category A loads can be exposed to 6 kV and 0.5 kA surge currents. Category B loads are between 30 and 60 feet of wire length from the service entrance to the load. Category B loads can be exposed to 6 kV and 3 kA. Category C loads are less than 30 feet from the service entrance to the load. Category C loads can be exposed to 20 kV and 10 kA.[4]


A transient surge protector attempts to limit the voltage supplied to an electric device by either blocking or shorting current to reduce the voltage below a safe threshold. Blocking is done by using inductors which inhibit a sudden change in current. Shorting is done by capacitors which inhibit a sudden change in voltage or by spark gaps, discharge tubes, Zener effect semiconductors, and metal-oxide varistors (MOVs), all of which begin to conduct current once a certain voltage threshold is reached. Some surge protectors use multiple elements.


The most common and effective way is the shorting method in which the electrical lines are temporarily shorted together (as by a spark gap) or clamped to a target voltage (as by a MOV) resulting in a large current flow. The voltage is reduced as the shorting current flows through the resistance in the power lines. The spike's energy is dissipated in the power lines (and/or the ground), or in the body of the MOV, converted to heat. Since a spike lasts only tens of microseconds, the temperature rise is minimal. However, if the spike is large enough or long enough, like a nearby hit by lightning, there might not be enough power line or ground resistance and the MOV (or other protection element) can be destroyed and power lines melted.


A transient voltage suppressor or TVS is a general classification of electronic components that are designed to react to sudden or momentary overvoltage conditions. One such common device used for this purpose is known as the transient voltage suppression diode, a Zener diode designed to protect electronics device against overvoltages. Another design alternative applies a family of products that are known as metal-oxide varistors (MOV).[7]


The characteristic of a TVS requires that it respond to overvoltages faster than other common overvoltage protection components such as varistors or gas discharge tubes. This makes TVS devices or components useful for protection against very fast and often damaging voltage spikes. These fast overvoltage spikes are present on all distribution networks and can be caused by either internal or external events, such as lightning or motor arcing.[8]


Applications of transient voltage suppression diodes are used for unidirectional or bidirectional electrostatic discharge protection of transmission or data lines in electronic circuits. MOV-based TVSs are used to protect home electronics, distribution systems and may accommodate industrial level power distribution disturbances saving downtime and damage to equipment. The level of energy in a transient overvoltage can be equated to energy measured in joules or related to electric current when devices are rated for various applications. These bursts of overvoltage can be measured with specialized electronic meters that can show power disturbances of thousands of volts amplitude that last for a few microseconds or less.


It is possible for a MOV to overheat when exposed to overvoltage sufficient for the MOV to start conducting, but not enough to totally destroy it, or to blow a house fuse. If the overvoltage condition persists long enough to cause significant heating of the MOV, it can result in thermal damage to the device and start a fire.[9][10]


However, in countries without regulations, there are power strips labelled as "surge" or "spike" protectors that only have a capacitor, an RFI circuit, or nothing at all that do not provide true or any spike protection.


A surge arrester, surge protection device (SPD) or transient voltage surge suppressor (TVSS), is used to protect equipment in power transmission and distribution systems. The energy criterion for various insulation material can be compared by impulse ratio. A surge arrester should have a low impulse ratio, so that a surge incident on the surge arrester may be bypassed to the ground instead of passing through the apparatus.


To protect a unit of equipment from transients occurring on an attached conductor, a surge arrester is connected to the conductor just before it enters the equipment. The surge arrester is also connected to ground and functions by routing energy from an over-voltage transient to ground if one occurs, while isolating the conductor from ground at normal operating voltages. This is usually achieved through use of a varistor, which has substantially different resistances at different voltages.


Surge arresters are not generally designed to protect against a direct lightning strike to a conductor, but rather against electrical transients resulting from lightning strikes occurring in the vicinity of the conductor[citation needed]. Lightning which strikes the earth results in ground currents which can pass over buried conductors and induce a transient that propagates outward towards the ends of the conductor. The same kind of induction happens in overhead and above ground conductors which experience the passing energy of an atmospheric EMP caused by the lightning flash.


Surge arresters can only protect against induced transients characteristic of a lightning discharge's rapid rise-time, and will not protect against electrification caused by a direct strike to the conductor. Transients similar to lightning-induced, such as from a high voltage system's fault switching, may also be safely diverted to ground; however, continuous overcurrents are not protected against by these devices. The energy in a handled transient is substantially less than that of a lightning discharge; however it is still of sufficient quantity to cause equipment damage and often requires protection.


Without very thick insulation, which is generally cost prohibitive, most conductors running more than minimal distances (greater than approximately 50 feet (15 m)) will experience lightning-induced transients at some time during use. Because the transient is usually initiated at some point between the two ends of the conductor, most applications install a surge arrester just before the conductor lands in each piece of equipment to be protected. Each conductor must be protected, as each will have its own transient induced, and each SPD must provide a pathway to earth to safely divert the transient away from the protected component.


The one notable exception where they are not installed at both ends is in high voltage distribution systems. In general, the induced voltage is not sufficient to do damage at the electric generation end of the lines; however, installation at the service entrance to a building is key to protecting downstream products that are not as robust.


Also known as the let-through voltage, this specifies what spike voltage will cause the protective components inside a surge protector to short or clamp.[11] A lower clamping voltage indicates better protection, but can sometimes result in a shorter life expectancy for the overall protective system. The lowest three levels of protection defined in the UL rating are 330 V, 400 V and 500 V. The standard let-through voltage for 120 V AC devices is 330 volts.[12]


Underwriters Laboratories (UL),[13] a global independent safety science company, defines how a protector may be used safely. UL 1449 became compliance mandatory in jurisdictions that adopted the NEC with the 3rd edition in September 2009 to increase safety compared to products conforming to the 2nd edition. A measured limiting voltage test, using six times higher current (and energy), defines a voltage protection rating (VPR). For a specific protector, this voltage may be higher compared to a Suppressed Voltage Ratings (SVR) in previous editions that measured let-through voltage with less current. Due to non-linear characteristics of protectors, let-through voltages defined by 2nd edition and 3rd edition testing are not comparable.[12][14]