The Lower OF and Upper OF values are actually temperature differences between inside and outside. You have them set so that the windows opens when the zone hits 20degC from your schedule and the zone temperature is greater then ambient (Lower OF 0) and close again when the zone temperature is more than 1 degree above ambient (Upper OF 1). Make Upper OF higher (EnergyPlus default is 100degC). I've never quite figured why EnergyPlus does it this way. I should make the interface clearer about this and use better defaults. I'll make some changes for v0.7.
Image below is from EP documentation.
As you have no heating applied to the space it's also possible you are not hitting the schedule set-point of 20degC very often either.