But you only add enough oil to replace what was drained. Nothing came
out so they only put 3 milliliters IN!
Mine holds 200 ml but can only drain 100ml.
FSM -
Whenever replacing any component of the system or a large amount
of gas leakage occurs add oil to maintain original amount of oil.
Run system on max cooling, with max fan and engine idling for 20-30
min to return oil to compressor.
Stop engine, discharge system, remove compressor. Drain compressor
from discharge port and measure the amount. Compressor may need to
be warmed to 40-50°C."
/FSM
As it only drains 100ml the amount to be refilled is.
FSM -
If more than 90ml came out put that amount back in. Less than
90ml, put 90ml in.
If oil contains chips or other foreign material. Flush system with
refrigerant, replace drier and fill with 200ml.
If compressor is replaced oil has to be drained from it to allow for
oil in system.....
/FSM
People with automatic air con refil carts are little more than trained
monkeys and only know how to connect it and press the buttons.
So if a lot of oil was lost in the initial leak it's been running with
about 1/2 of what it needs and now it not only has a leak but the
compressor could be wrecked as well.