Hi,

My immediate problem is no DHW.

I have searched this group and I think I have the following CH/HW
setup

1.“Conventional” gas boiler i.e. Feeds a (poorly) lagged copper
cylinder via an indirect coil from the boiler
2.Supplementary electric immersion heater in HW cylinder
3.Two 2-port ACL Lifestyle valves controlled by the Honeywell
controller
4.Various water tanks in the loft

Now, various pipes connected to the HW cylinder are scalding hot
but the HW delivered at the taps is tepid.

I am thinking the 2-port valve on the HW side has failed. I haven't
yet traced the various water pipes and I need to study more about how
such a system is connected and should operate (and fail) but I need
help on the following.

I am guessing I can determine if the problem is a failed motor /
valve by “forcing” the valve open while the HW setting on the
controller is on. Now, the problem is, I can't find any online
information about the ACL Lifestyle valve. Does anyone know these
devices? There is a little black “switch” on top of each valve – I
would have thought this was a manual override to open or close the
valve but the bit of plastic just “waggles about” when I fiddle with
it – certainly there is no feeling that a switch is being operated
that might cause a motor to open or close a valve.

If I can force the valve open and satisfy myself the motor is the
problem does anyone know of a supplier for the “actuator” part of the
valve? I can't find online a reference and I guess it is an obsolete
device.

If I can't override the motor, can I detach it from the valve and
use a screwdriver to force the valve open?

If by trying to override the valve I determine the HW problem
(probably) isn't due to the valve, what else might be worth looking
at?

Naive question. Are the 2-port valves on the boiler / supply side
of the circuit or the “demand” side of the circuit? I am thinking they
should be on the demand side to enable either circuit to be switched
independently – giving independent HW and CH. I can understand the
operation of a 2-port valve on the sealed loop that goes around the
radiators but I can't understand how such a valve would work on the HW
side. Surely the DHW just comes off the top of the HW cylinder – and
the water removed is replaced by cold water supplied from the tank in
the loft. So what flow is the second 2-port valve controlling?

Clive

unread,
Feb 11, 2008, 1:40:56 PM2/11/08
to
A bit more info.

I think these ACL valves are now supplied by Invensys

On the Inversys Web site is a clear, simple diagram showing the setup
(maybe a bit simplified) of a fully pumped system, with two motorised
(zone?) valves.

The order of components in their diagram is:
Boiler > Pump > T-connection > 1. 2-port valve on flow to HW cylinder
and 2. 2-port valve on flow to radiators

Now on my system the pump is "upside down" i.e. pumping top to bottom
and the valves are below the pump. This configuration "feels" weird to
me but may be perfectly OK.

I have noticed there is a little "lever" to the side of the valve
motor that barely protrudes and certainly can't be moved by me pushing
with my finder tip.

One of the "tags" at the top (bottom?) of the valve motor I slid to
one side and it has now "fallen" flush with the valve motor body. this
tag can no longer be moved and I don't want to break it by fiddling.

This info is just to describe a bit more about the setup in case
someone can help explain how to diagnose / fix the HW supply problem
short term or long term.


Thanks

Clive

geoff

unread,
Feb 11, 2008, 4:54:32 PM2/11/08
to
In message
<86ddda15-52c6-420f...@s19g2000prg.googlegroups.com>,
Clive <clive...@yahoo.com> writes

>
> I am guessing I can determine if the problem is a failed motor /
>valve by “forcing” the valve open while the HW setting on the
>controller is on. Now, the problem is, I can't find any online
>information about the ACL Lifestyle valve.

The ACL Lifestyle actuator heads use standard synchron motors available
fairly cheaply from most CH suppliers

If your actuator head has microswitches in it, check them out, they
often go high resistance, if they haven't melted

--
geoff

PM

unread,
Feb 13, 2008, 8:36:30 AM2/13/08
to

"Clive" <clive...@yahoo.com> wrote in message
news:86ddda15-52c6-420f...@s19g2000prg.googlegroups.com...


Naive question. Are the 2-port valves on the boiler / supply side
of the circuit or the “demand” side of the circuit? I am thinking they
should be on the demand side to enable either circuit to be switched
independently – giving independent HW and CH. I can understand the
operation of a 2-port valve on the sealed loop that goes around the
radiators but I can't understand how such a valve would work on the HW
side. Surely the DHW just comes off the top of the HW cylinder – and
the water removed is replaced by cold water supplied from the tank in
the loft. So what flow is the second 2-port valve controlling?


*****

My setup is:
Boiler flow > pump > 2-port valves > HW/CH > boiler return.

The HW 2-port valve is controlling flow of water from the boiler through the
indirect coil in the HW tank.

The lever that you mention in your other post is to manually open the valve.
They latch in the open position. If the valve is already opened by the
system the lever moves freely, otherwise a bit of force is required. When
the valve is open the boiler should fire.


Roger Mills

unread,
Feb 13, 2008, 2:43:12 PM2/13/08
to
In an earlier contribution to this discussion,
Clive <clive...@yahoo.com> wrote:

Have you still got the problem, or have you fixed it?

What you have is a fairly conventional S-Plan system. See the S-Plan section
of http://content.honeywell.com/uk/homes/systems.htm for a schematic and
circuit diagram - which help to explain how it's supposed to work.

The bit you're missing in your question is that the HW cylinder is actaully
a heat exchanger. It has a coil of pipe inside it through which water from
the boiler flows, and indirectly heats the actual domestic hot water without
any mixing of the primary and secondary circuits.

The primary circuit works as follows: Water heated by the boiler flows
through the pump and then splits into two sub-circuits - each controlled by
a zone valve. The CH sub-circuit goes through the radiators, and back to the
boiler. The HW sub-circuit goes through the indirect coil in the HW cylinder
and then back to the boiler. [The two returns may well combine into a single
pipe before they get to the boiler].

As far as controls are concerned, the CH zone valve is controlled by the
programmer and room stat, and opens when there is an unsatisifed demand for
heating. Likewise the HW zone valve is controlled by the programmer and
cylinder stat, and opens when there is an unsatisifed demand for HW. Each
zone valve has a secondary micro-switch - not connected to the motor
circuit - which closes when the valve is fully open, switching on the boiler
and pump. [So the boiler and pump run when there is a demand from either or
both circuit, and switch off when both demands are satisfied].

If you're not getting any hot water, it almost certainly means that the HW
zone valve isn't opening, and isn't turning on the boiler and pump . This
might be for any of a number of reasons:
* Faulty wiring from the HW output of the programmer to the cylinder stat
and zone valve
* Duff cylinder stat
* Zone valve failing to open because of a duff motor in its actuator
* Zone valve opening but not turning on the boiler and pump due to a duff
microswitch [Not very likely because the HW would still be heated whenever
the CH is on]
* Zone valve failing to open because the mechanical part of it is seized.

Armed with a mains voltmeter, you should be able to find out whether the
valve motor circuit is powered - and check back through the cylstat etc. if
it isn't. If it is powered, but still doesn't open, remove the actuator -
whilst leaving it connected electrically - and see whether that moves when
it's not on the valve. If it does, it's a seized valve. If it doesn't, it's
a duff motor.

To answer your question about over-riding the valve, the manual lever on
some valves opens the valve but doesn't move it far enough to operate the
microswitch - so the boiler still doesn't come on. I don't know whether
yours is like that. If you open the valve by rotating its spindle with the
actuator removed, that won't turn on the boiler unless the microswitch in
the actuator also closes.

HTH!
--
Cheers,
Roger
______
Email address maintained for newsgroup use only, and not regularly
monitored.. Messages sent to it may not be read for several weeks.
PLEASE REPLY TO NEWSGROUP!


Clive

unread,
Feb 17, 2008, 11:31:58 AM2/17/08
to
>> Stuff about DHW failure and 2-port valves ...

>
> Have you still got the problem, or have you fixed it?
>

More a "problem gone away" situation.
The Invensys Web site has a simple, and thinking about it obvious,
diagnostic routine. Basically shut CH and DHW to OFF and set
thermostats to low temp. The seperately switch on CH and DHW circuits
and turn at cylinder and room stat until see valves open, pump start
and boiler fire. This now happens reliably. At least I now have a
better understanding of how this all works.

> What you have is a fairly conventional S-Plan system. See the S-Plan section

> ofhttp://content.honeywell.com/uk/homes/systems.htmfor a schematic and


> circuit diagram - which help to explain how it's supposed to work.
>

<< snip >>


>
> If you're not getting any hot water, it almost certainly means that the HW
> zone valve isn't opening, and isn't turning on the boiler and pump . This
> might be for any of a number of reasons:
> * Faulty wiring from the HW output of the programmer to the cylinder stat
> and zone valve
> * Duff cylinder stat
> * Zone valve failing to open because of a duff motor in its actuator
> * Zone valve opening but not turning on the boiler and pump due to a duff
> microswitch [Not very likely because the HW would still be heated whenever
> the CH is on]
> * Zone valve failing to open because the mechanical part of it is seized.

All makes sense and a good checklist if the DHW goes off again

>
> Armed with a mains voltmeter, you should be able to find out whether the
> valve motor circuit is powered - and check back through the cylstat etc. if
> it isn't. If it is powered, but still doesn't open, remove the actuator -
> whilst leaving it connected electrically - and see whether that moves when
> it's not on the valve. If it does, it's a seized valve. If it doesn't, it's
> a duff motor.
>

Again - makes sense now.

<< snip >>

> HTH!
> --
> Cheers,
> Roger
> ______> To answer your question about over-riding the valve, the manual lever on


> some valves opens the valve but doesn't move it far enough to operate the
> microswitch - so the boiler still doesn't come on. I don't know whether
> yours is like that. If you open the valve by rotating its spindle with the
> actuator removed, that won't turn on the boiler unless the microswitch in
> the actuator also closes.
>

> Email address maintained for newsgroup use only, and not regularly
> monitored.. Messages sent to it may not be read for several weeks.
> PLEASE REPLY TO NEWSGROUP!

Ta

Clive