On Thu, 12 Nov 2015 05:44:01 +0000, westom
<
caedfaa9ed1216d60e...@example.com> wrote:
>replying to Peter Parry , westom wrote:
>For protection of human life, an RCD must trip at 5 milliamps.
Pity that all domestic ones trip at 30mA then.
>Higher
>currents (ie 20 milliamps) are permitted if human protection only requires
>'let-go' or ventricular fibrillation protection. One standard (that now
>applies to North America and will eventually appear in the UK) is UL943.
BS 7671:2008+A3:2015 IET Wiring Regulations Seventeenth Edition came
into effect in July 2015. Residual Current Devices must meet the
standards in BS EN 61008-1:2012.
You are suggesting that these will in some way be replaced by UL943
(Class A, single- and three-phase, ground-fault circuit-interrupters
intended for protection of personnel, for use only in grounded neutral
systems in accordance with the National Electrical Code (NEC)), dated
2006?
You do realise a GFCI and an RCD are functionally identical?. However
a GFCI incorporates an over current trip so is closer to a Residual
Current Breaker with Overload (RCBO) than a RCD. There will normally
be 1 GFCI per socket outlet (Often incorporated into the socket
itself) or small group of radial wired sockets rather than the RCD
covering a ring main which will have many sockets.
Under present UK rules all sockets must have residual current
protection, under the somewhat more lax American NEC rules only those
for use in wet areas need residual current detection.
What on earth makes you think the older UL943 will replace more modern
standards?
>More facts from design standards.
Which design standards?
> Currents less than 0.5 milliamps are
>considered safe. Current between 0.5 and 10 milliamps cause involuntary
>muscle contraction resulting in injuries. Currents between 10 milliamps
>and 100 milliamps can cause breathing difficulties or even fibrillation.
>A 100 milliamp RCD is an inferior safety device.
No it isn't, it has a perfectly valid role to play in TT earthed
circuits.
>Any fault that trips a
>100 milliamp RCD is well above human safety requirements.
That's probably why those installed for protection of the users are
rated at 30mA.
>How does one design equipment to operate without tripping RCDs that do
>human safety (ie 5 milliamps)?
If you are referring to the US wiring system of having one GFCI per
socket - this will allow for the maximum 3.5mA leakage current from
your computer.
>That equipment leaks less than 100
>microamps. One ANSI standard permits leakages up to 500 microamps. BS
>standards will eventually adapt what has long been standard by UL, CSA,
>IEEE, and others. Many BS upgrades eventually use phrases directly taken
>from those other, older, and safer standards. Apparently you need not
>meet international standard.
Do you actually understand the standard naming conventions and the
hierarchy of standards? National standards specify the requirements
for application in the particular country. British Standard – BS
denotes Britain's National Standards which are controlled by the
British Standards Institute (BSI). EN denotes a Standard which is
adopted by the European community and is controlled by the European
Committee for Standardisation (CEN). European standards are aimed at
facilitating commerce between the countries of the European community.
Once a European Standard has been agreed it supersedes any existing
national standard and becomes the new national standard. In Britain
these Standards are then prefixed with BS EN. ISO denotes a worldwide
standard issued by the International Organisation for Standardisation.
Once an International Standard has been adopted as a European Standard
it supersedes the existing European standard. In Britain these
Standards are then prefixed with BS EN ISO.
>Properly designed equipment need not leak more than 100 microamps. Designs
>typically target 60 microamps. JCAHO and NFPA 99 defines less than 50 and
>10 microamps.
Why on earth would you make all domestic equipment conform to medical
equipment standards when there is no advantage in doing so and a
considerable cost increase?
> Another standard permits up to 300 microamps from an
>asssembly of many electronic devices. Another standard for small electric
>motors with only one layer of insulation permits up to 100 microamp
>leakage. All well below an obsolete 3.5 milliamp number that would cause
>problems with current technology 5 milliamp RCDs. Even in the days of
>vacuum valves (tubes) did not leak that much.
You have obviously never worked on an old USA design TV.
However, here is a clue. Old valve equipment didn't use switched mode
power supplies and didn't have to meet any RF emission standards.
Indeed many TV['s were quite effective jammers of short wave radio
bands).
>Now back to the OP's problem. If a 100 milliamp RCD trips,
It is a 30mA RCD which is tripping.
>An informed engineer would not hype on the irrelevant - badly designed
>hardware that leaks 3.5 milliamps. As if obsolete standard are good
>enough.
The "obsolete" standard is several years younger than the American one
you quote.
>Microamp leakages numbers were standard and routinely achieved
>even 40 years ago.
40 years ago switched mode power supplies (SMPSU) were uncommon and
radio frequency interference wasn't an issue. With SMPSU you need
noise filtering to meet the EMC requirements and that introduces
leakage paths.
>A design engineer would target the topic rather than promote obsolete
>safety standards.
.
The standard you are referring to was only published 3 years ago.
I am rather concerned that someone claiming to be involved in the
design of electronic devices seems to never have heard of the
appropriate International standards.
Next thing you will be telling us to switch to 110V because it is
"safer".