On 06/11/2011 17:49,
tonyh...@gmail.com wrote:
> Thanks for the reply. Have checked whole electric system now - it
> would appear there is 200mV showing across the Service box earth (PME
> from road) and a "ground rod" which we've buried (banged 2' into)
> into the ground outside, if you see what I mean. This 200mV shows up
> throughout the house on earth connections in sockets etc and the new
Such voltages are perfectly normal and are generally of no consequence
whatever. I very very much doubt that they're anything to do with your
corrosion problem.
In the PME (aka TN-C-S) system the earth and neutral conductors in the
street mains and your service cable are one and the same, so voltage
drop along the neutral due to normal load current causes a potential
difference between the supply 'earth' and the local 'ground'. This can
reach several volts - 200 mV is 'nothing'.
> There is however only 20mV showing across new Earth and "Neutral" -
> ALL power switched off at Service box, of course.
Your wiring earth and neutral are bonded at the PME earth terminal in
the supply cut-out (the unit containing EDF's main fuse). On no load
the PD should be zero, but stray earth currents flowing quite normally
in your main bonding conductors could cause such a tiny PD - where
exactly did you put the meter probes?
> might be coming courtesy EDF? Is it enough for corrosive
> electrolysis?
That's highly unlikely, IMO. You're measuring with the meter set to AC
volts, I presume? Try putting the meter on DC - any DC offsets in the
earthing and bonding would be far more likely to drive electrolytic
corrosion, but even than you've have to consider what current path is
relevant to the problem. Do you live near anything that could put
significant DC current into the ground, e.g. LV electric railway,
tramway, telephone exchange?
> The immersion element includes a sacrificial anode on our model -
> Ariston just said they don't use them anymore, didn't say why!
Cost reduction, increased spares sales...?
> Thanks! Have taken out immersion (sic, anode)and put "blank" in
> pro-temp - hope the won't make corrosion worse without the anode.
>
> Electronic anti-corrosion device? Will invstigate - but not sure
> Ariston Technical will be able to help - have you any
> knowledge/experience? Would be cheaper than the Thermastore we've
> been looking at online this afternoon!!
The cylinder is a closed surface, electrically. Faraday sayeth that
there can be no electric field in such a closed vessel, unless it's
introduced somehow. The voltage on the surface relative to earth is
quite irrelevant. To get internal currents there would have to be
internal electrochemical PDs (as there will be with those sacrificial
anodes), or else a PD or current introduced through one of the penetrations.
HTH but I've no more to suggest ATM. I'd continue to badger Ariston.
Your water company might help too - is the pH of your water unusually
high or low?
--
Andy