Jim K <
jk98...@gmail.com> writes:
>> > Am having a hell of a time with nuisance tripping at the moment. =A0It
>> > happens intermittently, and when it does, you can just immediately
>> > flip the breaker back and it works again. =A0So it's very hard to
>> > localise. It's definitely in the kitchen; and I'm fairly sure it happen=
>s
>> > when
>> > the oven's on; but seems it may be more likely when the microwave's
>> > on as well?
>> > When it does trip, it's the main RCD which goes; however sometimes an
>> > individual MCB flips as well. I hadn't particularly noticed which one,
>> > but I this morning I spotted that it was the main ringmain for all
>> > sockets in the house *other* than the kitchen! =A0(the oven has a
>> > dedicated radial, and the kitchen sockets - including microwave - are
>> > on another MCB).
>>
>> > First question - do the above observations add up at all? =A0The MCB
>> > thing makes no sense to me at all; I wonder if today's observation
>> > was just a one-off oddity today?
>>
>> > The first time this happened I thought (well, assumed, as I'd
>> > experienced this before) the problem was a duff element in the oven
>> > and just ordered a new one; when it arrived though (during which time
>> > there'd been no more trips) I checked the old and new with a
>> > multimeter, found identical resistance across terminals (20 ohms
>> > IIRC) and to earth (open circuit) and decided I'd been wrong, so
>> > returned the new element unused. =A0Now wondering if I was incorrect in
>> > doing so. =A0Could there be undetected earth leakage (which I don't
>> > have kit to detect? =A0Could it be somewhere else in the oven? Or the
>> > house wiring? =A0Oven is a built-in one about 10 years old; main
>> > element was replaced about 9 months ago.
>> > Right now I'm really confused - I don't know whether I should be
>> > looking at appliances (which!?) or wiring. =A0I'd happily buy a new
>> > bloody oven if that would definitely solve it, but I am concerned it
>> > might not!
>> > Problem's really made worse by being intermittent, and because it
>> > seems to involve appliances we really can't do without.
>>
>> > Any advice on how to proceed most welcome!
>>
>> Check that the labels actually do match the MCB circuits! And make sure w=
>ho
>> ever resets the MCB when it trips notes which one it is.
>>
>> Any outside circuits on the RCD? I am thinking wet weather and NOT the ov=
>en
>> may be the cause. If it was the oven I would (in most cases) expect it to
>> happen every time the oven was used.
>also if a multi-element oven (fan, conventional top/bottom, grill etc)
>it may be only when a certain (failing) element is in use...
Yes, I have a combination oven which is OK on microwave only, but trips
the RCD on grill or convection settings. Almost certainly a duff
heating element, and as it's an old Comet CombiChef spares may be a
problem.
Elsewhere I have a socket (which I haven't yet checked because it's in a
rather inaccessible place) which probably has an N to E fault as discussed
before on this NG.
The symptoms are that if a vacuum cleaner (which is OK on other
circuits and shows no fault on a multimeter check) is plugged in there,
random trips occur, once when something heavy fell over causing floor
vibration, once when the vacuum was turned on, and once when a light
switch was turned on *elsewhere*.
But nothing except the RCD is affected.
None of this happens after the plug has been removed from that socket.
I'm expecting to find bad neutral or earth insulation behind the
faceplate.
--