Google Groups no longer supports new Usenet posts or subscriptions. Historical content remains viewable.
Dismiss

water butt overflow - spigot ?

224 views
Skip to first unread message

sm_jamieson

unread,
Jun 12, 2010, 6:30:19 PM6/12/10
to
I need a water butt overflow that can cope with 12m^2 of shed roof
when the butt is full. I think I'll need something like 32mm drainage
pipe. Can you get a spigot for this size pipe that screws into the
butt and seals with a washer ? I don't think solvent weld would work
on the water butt plastic.
Cheers,
Simon.

Peter Andrews

unread,
Jun 13, 2010, 4:05:39 AM6/13/10
to

"sm_jamieson" <sm_ja...@hotmail.com> wrote in message
news:f8df15a2-a2d1-41d4...@s9g2000yqd.googlegroups.com...

http://www.marleyplumbinganddrainage.com/specifier/product/1515/1666/1608/tank-connectors.html

there is also a push fit version, but I can't immediately find it on their
website - however B&Q do/did stock it (grey only and about �6!) and I have
used them very successfully on my water butts.

Peter


John Whitworth

unread,
Jun 13, 2010, 4:25:54 AM6/13/10
to

"Peter Andrews" <p.an...@blueblueyonder.co.uk> wrote in message
news:nj0Rn.42738$4w7.28753@hurricane...

I want to install a water butt soon, to capture water from the summerhouse.
Must admit, I'd not considered overflow - more whether I'd ever get it
full...but I guess it needs thinking about. Not having bought the butt yet,
is the reason for the overflow because the downpipe going into it is
effectively watertight? And thus any overflow will go back up to the
guttering it is supposed to be draining? I must admit, I'd thought the entry
point was not so watertight, so any excess would have run off the top of the
butt?

JW

Roger Mills

unread,
Jun 13, 2010, 4:48:40 AM6/13/10
to

Yes, it would run over the top of the butt - but it would then
potentially flood the surrounding ground. To avoid that, you need an
overflow which takes the surplus into a drain - and which can handle the
maximum flow rate likely to come down the inlet pipe.

If you already have a downpipe going into a drain, a very effective way
of filling a butt is to use a diverter like the one shown here:
http://www.marleyplumbinganddrainage.com/specifier/catalogue/1419/1651/ancillary-items.html

That cunningly diverts water from the downpipe into the butt until the
butt is full, and then sends it on down the downpipe instead - so you
don't need a separate overflow.
--
Cheers,
Roger
____________
Please reply to Newsgroup. Whilst email address is valid, it is seldom
checked.

Roger Mills

unread,
Jun 13, 2010, 4:57:49 AM6/13/10
to

Err. . the one referenced is only for 21.5mm pipe - which is only any
use for things like toilet cistern overflows.

You need something like this instead:
http://www.diy.com/diy/jsp/bq/nav.jsp?action=detail&fh_secondid=9272087&ecamp=trf-005&CAWELAID=266881356

You can get them in even bigger sizes (40 or 50mm) if you need them.

Peter Andrews

unread,
Jun 13, 2010, 5:04:04 AM6/13/10
to

"Roger Mills" <watt....@gmail.com> wrote in message
news:87jkb7...@mid.individual.net...

In my case the 40mm overflow feeds to another butt further down the garden,
the top of which is below the bottom of the first butt (steep garden) at
this point this lower butt simply overflows onto the garden some 30' from
the house and actually well below the foundations!

...and in my experience a downpipe diverter cannot extract water fast
enough, i.e. if the butt is empty and we have a short heavy downpour the
butt will get very little water from the diverter as it typically has a
15/20 mm pipe, if the main down pipe goes direct into the butt you catch all
the available water, the surplus then runs out the 40mm overflow...

Peter


Peter Andrews

unread,
Jun 13, 2010, 7:43:41 AM6/13/10
to

"Roger Mills" <watt....@gmail.com> wrote in message
news:87jksc...@mid.individual.net...

> On 13/06/2010 09:05, Peter Andrews wrote:
>> "sm_jamieson"<sm_ja...@hotmail.com> wrote in message
>> news:f8df15a2-a2d1-41d4...@s9g2000yqd.googlegroups.com...
>>> I need a water butt overflow that can cope with 12m^2 of shed roof
cistern overflows.
>
> You need something like this instead:
> http://www.diy.com/diy/jsp/bq/nav.jsp?action=detail&fh_secondid=9272087&ecamp=trf-005&CAWELAID=266881356
>
> You can get them in even bigger sizes (40 or 50mm) if you need them.
> --
> Cheers,
> Roger
> ____________
> Please reply to Newsgroup. Whilst email address is valid, it is seldom
> checked.
>

You are quite right! See Marley Polypropylene Tank Connector WUM43GX Grey
(Dia) 40mm EAN: 5011141007877

and the WUM33GX is the 32mm fitting.

That's what happens when you search quickly! ...and cheaper than I
remembered.


Peter


The Medway Handyman

unread,
Jun 13, 2010, 7:48:03 AM6/13/10
to

Water butt lids IME aren't watertight, so any excess water would overflow.
I have come across these rainwater diverters which feed water butts being
blocked - in which case the downpipe fills and overflows at the top.


--
Dave - The Medway Handyman
www.medwayhandyman.co.uk


Roger Mills

unread,
Jun 13, 2010, 8:01:21 AM6/13/10
to
On 13/06/2010 10:04, Peter Andrews wrote:

>
> ...and in my experience a downpipe diverter cannot extract water fast
> enough, i.e. if the butt is empty and we have a short heavy downpour the
> butt will get very little water from the diverter as it typically has a
> 15/20 mm pipe, if the main down pipe goes direct into the butt you catch all
> the available water, the surplus then runs out the 40mm overflow...
>
> Peter
>
>

Yes, the pipe size does limit the rate. However, I've been surprised at
how quickly my butt *does* fill up from one - and that's only capturing
the water from one half of a (double) garage roof.

harry

unread,
Jun 13, 2010, 12:26:38 PM6/13/10
to
On 13 June, 09:25, "John Whitworth"
<sexyjw@g_EEEEEEEEEEEEEEEE_mail.com> wrote:
> "Peter Andrews" <p.andr...@blueblueyonder.co.uk> wrote in message
>
> news:nj0Rn.42738$4w7.28753@hurricane...
>
>
>
>
>
> > "sm_jamieson" <sm_jamie...@hotmail.com> wrote in message

> >news:f8df15a2-a2d1-41d4...@s9g2000yqd.googlegroups.com...
> >>I need a water butt overflow that can cope with 12m^2 of shed roof
> >> when the butt is full. I think I'll need something like 32mm drainage
> >> pipe. Can you get a spigot for this size pipe that screws into the
> >> butt and seals with a washer ? I don't think solvent weld would work
> >> on the water butt plastic.
> >> Cheers,
> >> Simon.
>
> >http://www.marleyplumbinganddrainage.com/specifier/product/1515/1666/...

>
> > there is also a push fit version, but I can't immediately find it on their
> > website - however B&Q do/did stock it (grey only and about 6!) and I have
> > used them very successfully on my water butts.
>
> > Peter
>
> I want to install a water butt soon, to capture water from the summerhouse.
> Must admit, I'd not considered overflow - more whether I'd ever get it
> full...but I guess it needs thinking about. Not having bought the butt yet,
> is the reason for the overflow because the downpipe going into it is
> effectively watertight? And thus any overflow will go back up to the
> guttering it is supposed to be draining? I must admit, I'd thought the entry
> point was not so watertight, so any excess would have run off the top of the
> butt?
>
> JW- Hide quoted text -
>
> - Show quoted text -

You can buy a gadget that goes on the downpipe & fills your but & then
water goes down the downpipe.
http://articles.tipking.co.uk/Fitting_a_water_butt_and_rain_diverter.shtml

John Whitworth

unread,
Jun 13, 2010, 4:20:09 PM6/13/10
to

"Roger Mills" <watt....@gmail.com> wrote in message

news:87jvkg...@mid.individual.net...


> On 13/06/2010 10:04, Peter Andrews wrote:
>
>>
>> ...and in my experience a downpipe diverter cannot extract water fast
>> enough, i.e. if the butt is empty and we have a short heavy downpour the
>> butt will get very little water from the diverter as it typically has a
>> 15/20 mm pipe, if the main down pipe goes direct into the butt you catch
>> all
>> the available water, the surplus then runs out the 40mm overflow...
>>
>> Peter
>>
>>
> Yes, the pipe size does limit the rate. However, I've been surprised at
> how quickly my butt *does* fill up from one - and that's only capturing
> the water from one half of a (double) garage roof.
> --
> Cheers,
> Roger

Cheers guys. I'm going to have to come up with a cunning plan for my
overflow then, as it will be at the bottom of the garden, and due to the
ridiculous design of these houses, there is no drain around the back of the
house. Like Peter, I shall probably just have to work out a way to get it to
disperse over the garden.

There is no guttering on the summerhouse yet - and it really does need it -
so I shall be going with the 'full fat' pipe into the butt.

JW

John Whitworth

unread,
Jun 13, 2010, 5:05:19 PM6/13/10
to

"John Whitworth" <sexyjw@g_EEEEEEEEEEEEEEEE_mail.com> wrote in message
news:4c153d79$0$12154$fa0f...@news.zen.co.uk...

> so I shall be going with the 'full fat' pipe into the butt.

Oo-er...only just read that back. Wasn't meant to sound that way! :-D

Dave Liquorice

unread,
Jun 14, 2010, 5:17:00 AM6/14/10
to
On Sun, 13 Jun 2010 12:48:03 +0100, The Medway Handyman wrote:

> I have come across these rainwater diverters which feed water butts
> being blocked - in which case the downpipe fills and overflows at the
> top.

Not seen that but I've seen ours not able to cope with the volume of
water trying to get through it and being a round or square divertor
with round down pipe have four foot high fountains of water coming
out of the corners. It was seriously chucking it down though probably
around 50mm/hr but for only a few minutes.

As for capturing every last drop at normal rain fall rates I expect a
diverter will capture everything. Most rain rates in the UK are
measured at 1 or 2mm hour, or 40l/hr over 20m^2 for 2mm/hr. Yer
average 20mm divertor outlet pipe will carry that no problem.

--
Cheers
Dave.

0 new messages