In article <
uf6lQXEF...@0.0.0.0>, Percy <Pe...@no.chance> writes
>I'll try to keep this as short as possible. My heating system is 28
>years old and is 8mm microbore with standard steel panel radiators and
>an indirect hot water cylinder.
>
>It's the balancing that I'm having problems with. I've read all the info
>I can find and frankly none of it seems to have the desired effect on my
>system and there are other problems.
>
Is this the method you are following:
http://www.diyfaq.org.uk/plumbing/rad-balance.html
>My pump has 3 speed settings and the middle setting seems to work best.
>
That's a good start, yes.
>I started by turning all the main valves and TRVs fully open and the
>lock shield valves to a quarter turn from off and immediately noticed
>quite noticeable sounds of rushing water in a few of the radiators. If I
>open the lock shields the noise goes away but I now have no control over
>the flow through the radiators.
>
Classic noob mistake, what you have done is throttle the system and that
is not what you do at all. You start with all lockshields fully open and
only start to close ones that show low temperature drop. At the end of
the process (after many cycles) you will expect to see lockshields on
large rads on long pipe runs far from the boiler still fully open and
small rads close to the boiler perhaps on the quarter or half turn open
that you have attempted. Use a measurement table as described and
measure all rads within 5 or 10 mins, then work out how much each is to
be adjusted on that loop and make all the changes at once before waiting
20mins for the system to stabilise again. You can make gross changes at
the start eg. if a rad is dropping virtually nothing then go from fully
open (say 8/9 turns) to half shut (4T) in one loop, if it's still
dropping next to nothing then half the opening again on the next loop
(2T) and fine tune once you start getting meaningful drops. As Phil
suggests in his guide I note lockshield open-ness as number of quarter
turns from closed as this avoids the use of fractions.
>I am trying to use one of these
http://tinyurl.com/8uuqqvu to measure
>the temperatures but I can't get a reading from the pipes as they are
>only 8mm and trying it on the bottom corners of the rads gives wildly
>varying results. I have heard mention of putting a patch of black tape
>on the rads but, is this really necessary?
>
The reason for the tape has been well described here before and yes it
is necessary. Your tape is in the wrong place though, hottest place is
at the top of the panel closest to the inlet end, coldest place is at
the bottom of the panel closest to the outlet end, this is where the
patches should be. If you need help determining which is flow and return
then read the guide at the link again. A patch of tape about 30mm square
is fine (it doesn't need to be black, I use white) and to keep the
measurement target small you can just use the IR thermometer in contact
with the target (most have a window aperture about 20mm dia).
>I can't get near to the required drop across the rads and soon get back
>to the point where the rushing sound returns before any difference is
>noticeable.
>
There is no such thing as a 'required' drop (read the process and
philosophy described on the above link again), the system drop is a
function of boiler output and total rad loading and unless you have
designed it so the rads can sink all the heat that the boiler can
produce then the overall return temperature will be higher than the
ideal and you wont get the magic 20, 15 or 10 degree drop that you hope
for. Throttling the system to compensate for this and force a lower
return temperature is not the way to do it, you'll just have to put up
with the lower drop.
>What am I doing wrong and what should I be doing?
Have another go and post back if you still have probs.
--
fred
it's a ba-na-na . . . .