Hi,

My WallStar oil boiler (through-the-wall but otherwise conventional, non-condensing, not "system") has developed a fault which I feel is probably easy to fix if someone can help me understand how it's meant to work...

It locks out at some point but then is quite happy to start again if I press the lockout button (inside the outer cover on the burner itself). I've been "playing" and I get the feeling that it behaves itself better if the temperature control is set lower, although at the moment that's just my impression.
I wondered if the flow rate might be compromised somehow (maybe pump going faulty) but I can't hear any kettling.

Any ideas or pointers anyone? Please.

Michael Chare

unread,
Nov 19, 2013, 5:57:30 PM11/19/13
to
Dirty photcell? The jet should be changed regularly to avoid this (i.e.
every 1 or 2 years)

Blocked filter in the oil supply. The filters also need to be changed
regularly. Say ever 2 years.

Burner lockouts which you cancel by pressing a button on the burner
itself are generally caused by the flame going out. This is not a water
side problem.

Normally the boiler will stop when it gets to a specific temperature.
If that thermostat does not work there is generally a 2nd thermostat
which may have to be reset if it is tripped.

Do you have installation and maintenance manuals for the boiler and the
burner? You may be able to download them if you don't


--
Michael Chare

Dave Liquorice

unread,
Nov 19, 2013, 5:59:21 PM11/19/13
to
On Tue, 19 Nov 2013 13:49:36 -0800 (PST), Calvin wrote:

> It locks out at some point but then is quite happy to start again if I
> press the lockout button (inside the outer cover on the burner itself).
> I've been "playing" and I get the feeling that it behaves itself better
> if the temperature control is set lower, although at the moment that's
> just my impression.

I don't know that particular boiler but oil burners are generally bog
simple. I doubt very much that temperature control is directly
related to the lockout.

Lockouts occur when the control system in the burner thinks the flame
has gone out and after trying to reingnite it for a few seconds
thinks it hasn't succeeded. The flame detection uses a photocell and
these can get sooted up, hence the use of the word "thinks" above.
When was the burner last cleaned and serviced?

Of course you have checked that there is oil in the tank, that all
valves are properly open (don't forget the fire valve), that
filters/valves aren't blocked and that you have oil not oil/water at
the burner.

Remember oil floats on water. So water sinks in oil, to collect at
low points in the pipework. Has there been a frost? The water can
freeze in the pipes blocking or at least obstructing it. Spent half a
day getting the ice/slush out of our feed pipe a few winters back.
not nice with a foot of snow on the ground. Then another half a day
clearing all the gunge that had been dislodged out of the fire valve
and filter ... Have now dewatered the tank and have a glass bowl
filter to trap, and make visible, any water that does leave the tank
before it enters the pipework.

--
Cheers
Dave.



Calvin

unread,
Nov 19, 2013, 6:53:35 PM11/19/13
to
Thanks Michael and Dave,

From some reading around and standing outside listening to it I've pretty much convinced myself that it's not a waterside or thermostat problem.

I have to admit that it's some time (ahem!) since it was serviced so dirt/soot on the photocell would be quite a possibility. It was installed about 17 years ago (doesn't time fly!) and I'm sensing that fuel starvation due to the oil pump wearing out is quite a popular fault on these boilers after a much shorter time than that. That might fit with the runs-for-a-bit-then-stops nature of the problem.

Having seen the dates on my old paperwork I think I owe it a service so I guess I'll get someone in to repair and service it at the same time - and brace myself for the inevitable list of other worn out bits to be taken into consideration!

Michael Chare

unread,
Nov 19, 2013, 7:02:05 PM11/19/13
to
Alas, oil boilers do need regular servicing as you get a build up of
dirt inside also the parts I have mentioned do need to be changed
regularly - as I have found out!

--
Michael Chare

Dave Liquorice

unread,
Nov 19, 2013, 7:23:11 PM11/19/13
to
On Tue, 19 Nov 2013 15:53:35 -0800 (PST), Calvin wrote:

> I have to admit that it's some time (ahem!) since it was serviced so
> dirt/soot on the photocell would be quite a possibility. It was
> installed about 17 years ago (doesn't time fly!) and I'm sensing that
> fuel starvation due to the oil pump wearing out is quite a popular fault
> on these boilers after a much shorter time than that. That might fit
> with the runs-for-a-bit-then-stops nature of the problem.

Could be but I wouldn't like to say that. Our burner (Rielo I think,
there is less than a handful of burner makers) is of a similar
vintage and seems fine.

As yours has not been serviced for "a while" it could just be a worn
jet not atomising the oil well enough for a weak spark due to eroded
electrodes not igniting it reliably and soot on the photocell not
helping.

--
Cheers
Dave.



MM

unread,
Nov 20, 2013, 3:44:18 AM11/20/13
to
On Tue, 19 Nov 2013 13:49:36 -0800 (PST), Calvin
Be prepared for some heavy reading, Calvin! I was exactly where you
are a year ago. I'm digging our the Usenet links right now. It was a
veritable litany of problems that persisted off and on for six weeks
until the boiler was fixed. By the way, you don't state what model of
Wallstar yours is. Mine is a Wallstar 55 and approximately 10 years
old.

Watch this space!

MM

MM

unread,
Nov 20, 2013, 3:55:16 AM11/20/13
to
Correction: My boiler is Wallstar 15/20.

MM

MM

unread,
Nov 20, 2013, 4:00:10 AM11/20/13
to
On Tue, 19 Nov 2013 13:49:36 -0800 (PST), Calvin
<csam...@bigfoot.com> wrote:

Read the posts at the links below to uk.d-i-y.

In short, the problem turned out to be the pump. But read 'em anyway,
because it should give you great insight into the boiler's various key
components, any of which, if failed, will cause a major problem.

My boiler, once fixed with the new pump and fire valve, has been
running now for a year (touch wood!) without any problem whatsoever.

Curious behaviour of my Wallstar boiler
https://groups.google.com/forum/#!searchin/uk.d-i-y/wallstar$2055|sort:relevance/uk.d-i-y/afYgAiKfriE/Z2kMomaBMe0J


My ongoing, intermittent Wallstar oil boiler problem AGAIN!
https://groups.google.com/forum/#!searchin/uk.d-i-y/wallstar$2055|sort:relevance/uk.d-i-y/1xhGMjcNRvE/tnbgdQZyMw0J


Fxed at last! My Wallstar 15/20 oil boiler is now working properly
https://groups.google.com/forum/#!searchin/uk.d-i-y/wallstar$2055|sort:relevance/uk.d-i-y/dUtvuK75JhA/jjmZxMoWh7QJ

MM

Michael Chare

unread,
Nov 20, 2013, 12:27:08 PM11/20/13
to
On 20/11/2013 09:00, MM wrote:

I have struggled to get google group searches to work.

What web page did you go to for the google groups search?

--
Michael Chare

Judith

unread,
Nov 20, 2013, 12:57:24 PM11/20/13
to


"MM" wrote in message news:9auo89ppam6oovrie...@4ax.com...

On Tue, 19 Nov 2013 13:49:36 -0800 (PST), Calvin
<csam...@bigfoot.com> wrote:

>
how many children do you have

when are you moving to germany

MM

unread,
Nov 21, 2013, 2:23:43 AM11/21/13
to
On Wed, 20 Nov 2013 17:27:08 +0000, Michael Chare
<mUNDERSCOREnews@chareDOTorgDOTuk> wrote:

>On 20/11/2013 09:00, MM wrote:
>
>I have struggled to get google group searches to work.
>
>What web page did you go to for the google groups search?

groups.google.com

MM

Michael Chare

unread,
Nov 21, 2013, 5:58:08 AM11/21/13
to
Thanks, for some reason it does not work properly with Mozilla Firefox.

--
Michael Chare

Bob Eager

unread,
Nov 21, 2013, 7:15:34 AM11/21/13
to
Works fine on Firefox for me.



--
Use the BIG mirror service in the UK: http://www.mirrorservice.org
My posts (including this one) are my copyright and if @diy_forums on
Twitter wish to tweet them they can pay me £30 a post
*lightning surge protection* - a w_tom conductor

Michael Chare

unread,
Nov 21, 2013, 12:41:44 PM11/21/13
to
On 21/11/2013 12:15, Bob Eager wrote:
> On Thu, 21 Nov 2013 10:58:08 +0000, Michael Chare wrote:
>
>> On 21/11/2013 07:23, MM wrote:
>>> On Wed, 20 Nov 2013 17:27:08 +0000, Michael Chare
>>> <mUNDERSCOREnews@chareDOTorgDOTuk> wrote:
>>>
>>>> On 20/11/2013 09:00, MM wrote:
>>>>
>>>> I have struggled to get google group searches to work.
>>>>
>>>> What web page did you go to for the google groups search?
>>>
>>> groups.google.com
>>>
>>> MM
>>>
>> Thanks, for some reason it does not work properly with Mozilla Firefox.
>
> Works fine on Firefox for me.
>
>
>
Thanks. It works on my laptop but not on my desktop. No obvious software
difference!

--
Michael Chare

Michael Chare

unread,
Nov 21, 2013, 3:27:59 PM11/21/13
to
Resetting Firefox solved the problem. Thank you google.

--
Michael Chare

Calvin

unread,
Nov 26, 2013, 5:27:32 PM11/26/13
to
Well it's all sorted now, thanks to my boiler man. He diagnosed a dodgy solenoid which was failing open circuit when it got hot, it sounded like a guess based on lots of experience and sure enough fitting a new one has fixed it.

The diagnosis was made on Friday but it wasn't until today that he was free to fix it and over the weekend I found that if the boiler temp was set to really low (like about 45 degrees) it just about kept going without locking out. That's probably not too good for a non-condensing boiler in the long term but I figured that it would be OK for a few days.

Thanks for your thoughts everyone.