On Saturday, 1 October 2022 at 16:49:25 UTC+1, rick wrote:
> I am terminating some 3 core flex onto an mcb and busbar
> For a short final length connection.
>
> BS 7671 allows for using flexible cables, it does stipulate that:
> A flexible cable shall be used for fixed wiring only where the relevant
> provisions of the Regulations are met. Flexible cables used for fixed
> wiring shall be of the heavy duty type unless the risk of damage during
> installation and service, due to impact or other mechanical stresses, is
> low or has been minimized or protection against mechanical damage is
> provided.
>
>
> In this case risk of damage is low - The cable will be clipped direct to
> rafters, and at least 2m above floor level.
>
>
> I don't have a ferrule crimp tool, I could twist and solder the stranded
> ends,
bad idea, solder is too soft to form a long term gas-tight joint under compression.
> or I could spirally wind around a short piece of solid conductor
> to provide mechanical strength
I wouldn't, having played with that idea long ago. High failure rate
> ..... is there a better way ?
>
> Would I be better to ignore bus bar and use WAGO connectors
ferrules.
Screw connectors are usually able to work well with flex, but I'd not trust MCB connections to.