On 20/01/2013 17:50, Gordy wrote:
I'm not sure that you *do* necessarily need a by-pass valve.
The usual reason for fitting one would be if the boiler requires pump
over-run but there is no guaranteed flow path. This is often the case
with S-Plan systems which, with all zone valves shut, leave nowhere for
the over-run flow to go unless there's a by-pass.
But if you have W-Plan system with a diverter valve (or is it a Y-Plan
system with a mid-position valve?) it can never close completely -
either the HW or CH ports (or possibly both) will be open. If just the
HW port is open, there will be a flow path through the HW cylinder's
indirect coil. If just the CH port is open, there *should* be a flow
path through one or more radiators.
When you say that all your rads have TRVs, do you mean *literally* all?
Is there no room stat? If there is, it is usual for the rad nearest to
that *not* to have a TRV.
The generic fitting instructions for by-pass valves are likely to cover
the general case (including S-Plan) where they *do* need to be fitted
after the pump and before any zone valves, but in your case - if you
decide that you *do* need one - I can see no reason why it can't be
where you suggest, just by-passing the CH circuit because, except in
CH-only mode, there will always be a flow path through the HW circuit.
--
Cheers,
Roger