On 30/03/2013 15:03, Owain wrote:
> On Mar 30, 2:07 pm, The Medway Handyman wrote:
>> Swapping a Sunvic SD 2701 mid position valve for a Honeywell V4073A.
>>
>> Sunvic has 4 wires; blue, grey, orange & white.
>>
>> Honeywell has 5 wires; blue, grey, orange, white & earth.
>>
>> Wires from wiring centre, via junction box are brown, blue, black &
>> earth. I'm guessing it's not the correct cable & the earth is being
>> used for something else.
>>
>> Connections are (wiring centre to valve); earth to white, blue to blue,
>> brown to orange, black to grey.
>>
>> What do I do with the spare earth wire?
>
> The earth wire is not spare. It MUST be connected to the circuit
> protective conductor.
When I say spare earth I mean spare green/yellow. The green/yellow is
connected to the white on the actuator. In the wiring centre its
connected to a green/yellow from the RF room stat. Neither are
connected to the earth from the mains input.
I suspect the Sunvice was double insulated & the Honeywell isn't?
And that 'any old' cable has been used in the past.
Point taken re the earth, that can be easily done.
>
>> Or do I need to investigate the wiring centre?
>
> If the cpc in the existing cable is being used for another purpose it
> MUST be disconnected from whatever it's being used for, and connected
> to earth. An additional/new cable (with cpc) MUST be run in if the
> number of cores in existing is inadequate.
>
> The cpc must be tested for continuity back to the main earth terminal
> (MET).
>
> Owain
>