My (Keston) runs at low temp - typically 45 flow, 32 return.
I have had a couple of cases of something slimy/jelly-like
growing in the bottom of the heat exchanger, and blocking
the drain hole. You will get a build up of burned insects
and the like there, which were sucked in the air intake.
If you run the boiler at very low temperature like I do,
this can form the basis for some organic growths, and even
if you don't, that debris itself can block things if it
builds up.
To clear out debris which collects in the bottom of the
heat exchanger before it builds up enough to block the outlet,
I now pour a couple of pints of water into the flue terminal a
couple of times a year, which with my Celcius 25 does result in
washing away any solids collecting on the bottom of the heat
exchanger, and it hasn't blocked for some years now. I don't
know if this is safe for all condensing boilers (but certainly
don't make a mistake and pour it in the air intake - that's
probably rather fatal in most cases). However, it's a lot
easier that taking the burner off the top of the heat exchanger
and flushing through with water, which is what the service
instructions expect you to do (and always requires a new
gasket, as a new gasket breaks into about 20 pieces the first
time you fire up the boiler).
--