Ben Blaukopf

unread,
Jan 18, 2013, 5:35:31 AM1/18/13
to
Woke up this morning to find a d1 error - condensate pipe/trap blocked
on my Vokera. Frozen, obviously - except it couldn't be, because it
routes to an internal waste stack. I extracted the pipe and trap from
inside the boiler and found the pipe blocked with a load of black
gritty gunk (which apparently is due to the condensate dissolving the
aluminium heat exchanger?). Cleaned that out, still didn't work.
Faffed around a bit, and it started working, presumably because some
condensate higher up had finally cleared the sensor. Put it back
together, working boiler :)

So ice isn't the only problem. Question is, is this level of blockage
normal? Or is my heat exchanger on its last legs?

Andrew Gabriel

unread,
Jan 18, 2013, 6:40:22 AM1/18/13
to
In article <c7e672fa-3e39-4951...@w3g2000yqj.googlegroups.com>,
My (Keston) runs at low temp - typically 45 flow, 32 return.
I have had a couple of cases of something slimy/jelly-like
growing in the bottom of the heat exchanger, and blocking
the drain hole. You will get a build up of burned insects
and the like there, which were sucked in the air intake.
If you run the boiler at very low temperature like I do,
this can form the basis for some organic growths, and even
if you don't, that debris itself can block things if it
builds up.

To clear out debris which collects in the bottom of the
heat exchanger before it builds up enough to block the outlet,
I now pour a couple of pints of water into the flue terminal a
couple of times a year, which with my Celcius 25 does result in
washing away any solids collecting on the bottom of the heat
exchanger, and it hasn't blocked for some years now. I don't
know if this is safe for all condensing boilers (but certainly
don't make a mistake and pour it in the air intake - that's
probably rather fatal in most cases). However, it's a lot
easier that taking the burner off the top of the heat exchanger
and flushing through with water, which is what the service
instructions expect you to do (and always requires a new
gasket, as a new gasket breaks into about 20 pieces the first
time you fire up the boiler).

--
Andrew Gabriel
[email address is not usable -- followup in the newsgroup]

Ben Blaukopf

unread,
Jan 18, 2013, 11:11:49 AM1/18/13
to
On Jan 18, 11:40 am, and...@cucumber.demon.co.uk (Andrew Gabriel)
wrote:
> In article <c7e672fa-3e39-4951-86ba-754ecadf0...@w3g2000yqj.googlegroups.com>,
Ta.

In the "faffed about" stage, I was reading the bit in the manual about
the heat exchanger and replacing seals, and deciding that was a step
too far.

I presume that if I simply identify which bit of the flue the plume is
coming out of, I'm unlikely to go far wrong, provided it doesn't run
downhill to the outside!

Andrew Gabriel

unread,
Jan 18, 2013, 11:33:31 AM1/18/13
to
In article <ec8bcf74-c453-44b0...@fw2g2000vbb.googlegroups.com>,
Ben Blaukopf <bbla...@airsource.co.uk> writes:
> Ta.
> In the "faffed about" stage, I was reading the bit in the manual about
> the heat exchanger and replacing seals, and deciding that was a step
> too far.
> I presume that if I simply identify which bit of the flue the plume is
> coming out of, I'm unlikely to go far wrong, provided it doesn't run
> downhill to the outside!

Someone familiar with the insides of your boiler would need
to comment on that - I'm not.

ISTM it shouldn't do any harm because condensation in the flue
needs to run back into the boiler anyway and be drained out,
but that path might not flush the base of the heat exchanger,
and might not be able to handle more than a tiny trickle in all
cases.

newshound

unread,
Jan 18, 2013, 1:25:48 PM1/18/13
to
Presumably with the "concentric" flues, the vent is always on the inside
with the intake as the annulus


David.WE.Roberts

unread,
Jan 18, 2013, 2:21:51 PM1/18/13
to
If I understand what is going on (which is questionable) when my Worcester
Bosch combi is first powered up it runs in a special low temperature mode
and also primes the condensate drain.

So perhaps all I would need to do was power off then on again every 6
months or so.

Cheers

Dave R


--
Pan in Vista on second Vista PC.

meatloaf

unread,
Jan 1, 2014, 4:24:09 PM1/1/14
to
Woke up this morning with water dripping from my sabre boiler, took it apart and found that water was somehow getting into the combustion chamber,checked condensate trap and it was empty ,stripped out condensate pipe back to the Condensing unit it was blocked solid with ash like grit, Condensing unit itself was blocked as well and full of water cleaned them all out and boiler returned to normal operation