Staying in another house and there is an ancient and dodgy central heating
system.

The valve is a Drayton Mid Position Actuator MA1.

It seems to have two functions; an open/close switch and a three position
switch for Heat Mid and Water. I assume that the logic is roughly;

If heating or water is called for the main valve opens and the 3 position
valve moves to Heat or Water. If both are called for then the Mid position
is selected which allows water to circulate to both.

Digging so far indicates that if the controller calls for heating (with
thermostat set above ambient temperature) nothing happens.

If water is called for the main valve sometimes opens and the pump runs.

There are manual overrides for both functions - valve and 3 way selector.

I can (just about) get the cheap plastic piece of shit manual override on
the main valve to stay open. The 3 way manual override plastic lever seems
to be sticking out of the back of the valve housing - I can see the other
end when I waggle it - so I can't move that valve around to see what
happens.

At the moment I am assuming that the valve is in the mid way position
(otherwise we wouldn't be getting hot water from the tank and some heat
from the radiators) and the strange behaviour of the heating is because it
only works when the programmer for the hot water is on.

Venting here to see if my conclusions seem reasonable.

One side of the house, the radiators do get hot, Some of the other
radiators don't, or at least take a long time (I've only recently put the
hot water on constant). Pump is on flat out setting. This suggests that
the radiators may not be balanced.

Now some heat is getting to the cold radiators. The new (compared to the
others) double radiator is doing something I haven't encountered before.
The rear part is heating up but the front part is staying cold. It doesn't
have air in because I have bled it (amazingly after a long search I found
a bleed screw) and it was full of water.

I assume if the 3 way valve was working properly and the heating side
wiring wasn't requesting heating then the 3 way valve would be set to Heat
and the central heating wouldn't work. However although I heard the main
valve move and watched the plastic lever move, I haven't heard anything
from the 3 way valve and the plastic lever seems to be floating.

Anyway having diagnosed this far I'm going to leave it with the central
heating and the water heating on full time to see if I can get the
temperature in the bungalow up to the expected level.

I'm now trying to remember if for frost protection the water heating was
turned off and the central heating thermostat was turned down to 5C. If so
that would explain why the house gets cold after a day or so. It also
suggest a lucky escape from some freezing if the weather turns bad.

Merry Christmas, everyone!



Dave R


--
Dell XPS laptop running W8.1

David

unread,
Dec 25, 2018, 4:40:09 AM12/25/18
to
Supplementary - I'm hoping that it is a faulty thermostat which is
clicking but not passing a current.
Now if only I'd brought my multi-meter with me.

Access to the wiring is interesting as well. I am used to airing cupboard
systems where all the wiring is nicely placed by the door for ease of
access. This is behind the clothes shelving half way up the wall behind
the boiler and not the easiest place to get to.

Guess what I will be looking for in the Boxing Day sales.

Oh, and that double radiator is still doing my head in. This morning the
front is warming up nicely but the rear panel is being slow.

I need to do something to improve the situation because the house will be
empty for a time in January and February with a consequent risk of frost
damage if the heating doesn't work properly using the thermostat.

Next step wiring diagrams.

Cheers

Roger Mills

unread,
Dec 25, 2018, 5:33:34 PM12/25/18
to
I'm not familiar with the Drayton 3-port mid-position valve but if it's
like most other makes, it will work like this - as shown in the Y-Plan
schematic at
http://wiki.diyfaq.org.uk/index.php?title=File:Y-Plan-Wiring.gif

When there is a HW demand but not a CH demand, the valve is un-powered
and sits in the HW position. The boiler and pump are powered directly
from the cylinder stat.

When HW and CH are calling for heat at the same time, the valve moves to
the mid position. The boiler and pump are still powered directly from
the cylinder stat.

When there is a CH demand but no HW demand (tank stat satisfied or HW
off at programmer) the valve moves to the CH position. A microswitch in
the valve actuator switches a live supply to the orange wire - which
then powers the boiler and pump.

If the boiler doesn't run when there is *only* a CH demand, it indicates
either that the valve hasn't moved all the way to the CH position or
that the microswitch isn't working.

The manual lever only moves the valve to the mid position, and is useful
when filling or bleeding the system to make sure that all water paths
are open. It will flop around when the valve is powered to the mid
position or beyond - this is normal.

With regard to the double radiator - unless the two sections communicate
at the top, it will have *two* bleed screws - one for each section. You
said the first one was hard to find - sounds like the second one is even
harder - but it will be there, somewhere! [These
are sometimes just over the top on the rear face of each section - often
under little circular covers which have to be prized off].
--
Cheers,
Roger
____________
Please reply to Newsgroup. Whilst email address is valid, it is seldom
checked.

John Rumm

unread,
Dec 25, 2018, 9:26:09 PM12/25/18
to
On 25/12/2018 09:40, David wrote:
Now there is a trick those guys at Victorinox are missing ;-)


--
Cheers,

John.

/=================================================================\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\=================================================================/

tabb...@gmail.com

unread,
Dec 26, 2018, 6:27:06 AM12/26/18
to
If you've not got a meter yet, you could use a tablelamp. Or better an extension lead that contains a neon.


NT

David

unread,
Dec 26, 2018, 8:14:01 AM12/26/18
to
Thanks.

Life gets ever more complicated.

First thing in the morning with hot water off the thermostat (tested via
twiddling and listening for the click) will turn the boiler and the pump
on and off, but not open the shared (flow) valve.

That is, there is a shared (flow) valve which has to open to allow any
water to flow, then a second 3 way valve which decides which way the water
will flow.

Given that, if the flow valve is permanently open and the 3 way switch is
in the middle then water should always flow around the central heating.

However......


For some reason later in the day, with the hot water off and the heating
on, twiddling the thermostat does not cause the boiler to fire and the
pump to run; I assume causing the pump to run is the critical test because
the boiler usually fires a bit after the pump runs.

Nothing like consistent test results.

I still think this Drayton valve is a piece of cheap plastic shit. I am
used to the Honeywell valves with metal casings and a nice metal lever arm
to lock the valve open which moves firmly and fits firmly into a notch.
The Drayton valve has a plastic casing which seems very flimsy, a plastic
lever which also feels flimsy and which doesn't locate firmly when locked
open, and seems to shake around on the valve body when the pump is running.

Oh, and the 3 position plastic arm is more than just "floppy" - I can see
the bottom of it sticking out of the back of the plastic housing so I
assume it isn't connected to anything internally.

So I'm still not 100% certain which conditions will make the CH run
reliably.

tabb...@gmail.com

unread,
Dec 26, 2018, 8:27:48 AM12/26/18
to
sounds like a dodgy switch somewhere. Monitor the output of the thermostat to see if it's reliable or not, then ditto the 3 way etc. You'll track it down that way. Intermitten faults just take more time.


NT

Roger Mills

unread,
Dec 26, 2018, 12:17:44 PM12/26/18
to
I don't understand what this "shared" valve is for. Where is it in the
circuit? Any chance you could draw a schematic for the water circuits,
and upload it somewhere with a link here to its location? It it's a
conventional Y-Plan system, I'd expect to find the pump installed in the
flow pipe from the boiler, followed by the 3-port valve - whose 2
outlets go the cylinder coil and radiators respectively. I would then
expect to see the outputs from the radiators and coil combine into the
boiler return pipe. There shouldn't be any other motorised valves.

David

unread,
Dec 27, 2018, 2:45:17 PM12/27/18
to
Yes - me getting the flow the wrong way round. So please ignore much of
the above. The lever appears to be probably the manual override for the
mid port valve and the other strange thing should be used when removing
the motorised head.

It looks as though the following thread more or less describes my problem
(second post).

<https://www.diydoctor.org.uk/forums/drayton-ma1-mid-postion-valve-not-
resetting-to-hot-water-t43772.html>

or

<https://bit.ly/2VdXb0f>

This suggests that there is probably a dodgy micro switch.

I will test the wiring when my multi meter turns up tomorrow, but it is
looking like a new motorised head for the valve.

Regards

David

unread,
Dec 27, 2018, 2:59:15 PM12/27/18
to
<snip>

If you look at this PDF
<https://www.draytoncontrols.co.uk/sites/default/files/Motorised%20Valve%
20Installer%20Guide.pdf>
right at the top there is a diagram of how to fit and remove the head.

For removal it is lock lever (1) and press button (2) then remove the head.

I was assuming that the plastic thing at the mid point of the valve was a
valve lock of some kind and got well confused.

It looks easy to replace (for some values of easy) but I have been caught
that way before.

<https://www.amazon.co.uk/Drayton-22mm-Position-Motorised-Valve/dp/
B01HR3E98G/>
gives a good picture which shows the lever on the LHS and the button with
the strange black dangly plastic thing by the thumb of the hand.

I hope it is just a replacement of the head because there aren't isolation
valves to allow me to remove the complete valve without draining down.

Anyway, how much do you think it might cost to fix this?

I'm noting that I can get the complete unit for around £90 on Amazon, but
also for about twice that price. Still looking for the head unit only.

£200 labour £100 parts or am I being optimistic?

Cheers

tabb...@gmail.com

unread,
Dec 27, 2018, 3:26:39 PM12/27/18
to
To replace a few microswitches?

DJC

unread,
Dec 27, 2018, 3:53:10 PM12/27/18
to
In October I bought
Products
1x Drayton MA1 Actuator (23D03) £40.39

from
heatingcontrolsonline.co.uk


>
> £200 labour £100 parts or am I being optimistic?
>
> Cheers
>
>
>
> Dave R
>


--
djc

(▀̿Ĺ̯▀̿ ̿)
No low-hanging fruit, just a lot of small berries up a tall tree.

The Natural Philosopher

unread,
Dec 28, 2018, 4:08:02 AM12/28/18
to
On 27/12/2018 19:45, David wrote:
> Yes - me getting the flow the wrong way round. So please ignore much of
> the above. The lever appears to be probably the manual override for the
> mid port valve and the other strange thing should be used when removing
> the motorised head.
>
> It looks as though the following thread more or less describes my problem
> (second post).
>
> <https://www.diydoctor.org.uk/forums/drayton-ma1-mid-postion-valve-not-
> resetting-to-hot-water-t43772.html>
>
> or
>
> <https://bit.ly/2VdXb0f>
>
> This suggests that there is probably a dodgy micro switch.

Be aware that the lever will open the valve but NOT actuate the microswitch

DAMHIKT


--
"The most difficult subjects can be explained to the most slow witted
man if he has not formed any idea of them already; but the simplest
thing cannot be made clear to the most intelligent man if he is firmly
persuaded that he knows already, without a shadow of doubt, what is laid
before him."

- Leo Tolstoy

David

unread,
Dec 28, 2018, 5:00:48 AM12/28/18
to
To confirm diagnosis, replace head and wire in.

My backstop for being too busy with pressing matters, and also someone who
can diagnose further.

I also don't have my DIY tools with me if it needs more than a click off/
click on new with wiring like for like.

John Rumm

unread,
Dec 29, 2018, 10:47:50 AM12/29/18
to
Many plumbers won't replace the switches... often the best you can
expect is swapping the whole valve head assembly.

David

unread,
Dec 30, 2018, 4:50:53 AM12/30/18
to
Thanks - makes me wonder if an electrician is a better option.

tabb...@gmail.com

unread,
Dec 30, 2018, 7:20:40 AM12/30/18
to
On Saturday, 29 December 2018 15:47:50 UTC, John Rumm wrote:
> On 27/12/2018 20:26, tabbypurr wrote:
> > On Thursday, 27 December 2018 19:59:15 UTC, David WE Roberts (Google)

> >> Anyway, how much do you think it might cost to fix this?
> >>
> >> I'm noting that I can get the complete unit for around £90 on Amazon, but
> >> also for about twice that price. Still looking for the head unit only.
> >>
> >> £200 labour £100 parts or am I being optimistic?
> >
> > To replace a few microswitches?
>
> Many plumbers won't replace the switches... often the best you can
> expect is swapping the whole valve head assembly.

We however can. The choice is the OP replacing a few switches or paying someone else to replace the head.


NT

John Rumm

unread,
Dec 30, 2018, 1:40:47 PM12/30/18
to
If you can get the right switch, and don#'t mind lack of heating etc til
then. I expect as a DIY exercise, replace the head, but then set about
fixing the removed one ready for next time.

Tim Lamb

unread,
Dec 31, 2018, 4:50:53 AM12/31/18
to
In message <xtSdncGOxKyxjLTB...@brightview.co.uk>, John
Rumm <see.my.s...@nowhere.null> writes
>On 30/12/2018 12:20, tabb...@gmail.com wrote:
>> On Saturday, 29 December 2018 15:47:50 UTC, John Rumm wrote:
>>> On 27/12/2018 20:26, tabbypurr wrote:
>>>> On Thursday, 27 December 2018 19:59:15 UTC, David WE Roberts (Google)
>>
>>>>> Anyway, how much do you think it might cost to fix this?
>>>>>
>>>>> I'm noting that I can get the complete unit for around £90 on Amazon, but
>>>>> also for about twice that price. Still looking for the head unit only.
>>>>>
>>>>> £200 labour £100 parts or am I being optimistic?
>>>>
>>>> To replace a few microswitches?
>>>
>>> Many plumbers won't replace the switches... often the best you can
>>> expect is swapping the whole valve head assembly.
>> We however can. The choice is the OP replacing a few switches or
>>paying someone else to replace the head.
>
>If you can get the right switch, and don#'t mind lack of heating etc
>til then. I expect as a DIY exercise, replace the head, but then set
>about fixing the removed one ready for next time.

Have we covered *valve not travelling far enough* to operate the
microswitch?

--
Tim Lamb

The Natural Philosopher

unread,
Dec 31, 2018, 5:32:09 AM12/31/18
to
On 30/12/2018 18:40, John Rumm wrote:
> On 30/12/2018 12:20, tabb...@gmail.com wrote:
>> On Saturday, 29 December 2018 15:47:50 UTC, John Rumm  wrote:
>>> On 27/12/2018 20:26, tabbypurr wrote:
>>>> On Thursday, 27 December 2018 19:59:15 UTC, David WE Roberts (Google)
>>
>>>>> Anyway, how much do you think it might cost to fix this?
>>>>>
>>>>> I'm noting that I can get the complete unit for around £90 on
>>>>> Amazon, but
>>>>> also for about twice that price. Still looking for the head unit only.
>>>>>
>>>>> £200 labour £100 parts or am I being optimistic?
>>>>
>>>> To replace a few microswitches?
>>>
>>> Many plumbers won't replace the switches... often the best you can
>>> expect is swapping the whole valve head assembly.
>>
>> We however can. The choice is the OP replacing a few switches or
>> paying someone else to replace the head.
>
> If you can get the right switch, and don#'t mind lack of heating etc til
> then. I expect as a DIY exercise, replace the head, but then set about
> fixing the removed one ready for next time.
>
>
I giot a complete valve for less than the cost of the head and simply
swapped heads one time.


--
It’s easier to fool people than to convince them that they have been fooled.
Mark Twain


The Natural Philosopher

unread,
Dec 31, 2018, 5:33:26 AM12/31/18
to
In generally if the motor moves them at all it moives all the way.

The hand lever IME will NOT open the valve enough to move the microswitch.

John Rumm

unread,
Dec 31, 2018, 8:59:19 AM12/31/18
to
On 30/12/2018 20:08, Tim Lamb wrote:
I was referring to the specific case of dealing with failed microswitches.