Hello

I wonder if anyone can answer a plumbing question. I just changed the potable water expansion tank for my unvented water system. All seems to be working fine, but I am wondering if I have a missed a step.

I have a zilmet 24l tank pre-charged to 50 psi sitting at the highest point in the system. Obviously the tank was full of air when I first connect it up and I am wondering if  I need to bleed the air from the water side of the membrane to fill it up with water? There seems to be no way to do it, and no suggestion it should be done, so I will presumably just contract legionaire's shortly?

Any comments appreciated!

Thanks
Darren

Rick Hughes

unread,
May 25, 2014, 10:16:54 AM5/25/14
to
I have 4 Zilmet expansion systems on my install.

The Zilmet 24Litre on Boiler feed loop has just failed (water coming
out of air charge valve) ... so have to obtain replacement next week and
fit.

According to my install instructions - these units are charged with air
when 'not connected' to a pressurised water system ... you would (or at
least should) drain water if you want to check the air pre-charge.

In my case you then fill the pipework and charge up the system to 1 bar
static charge.


--
UK SelfBuild: http://uk.groups.yahoo.com/group/UK_Selfbuild/

dennis@home

unread,
May 25, 2014, 11:27:40 AM5/25/14
to
On 25/05/2014 11:47, dazlew...@googlemail.com wrote:
The cylinder should be filled with air on the otherside of the membrane.
It will partly fill with water once there is some pressure in the system.
It should never fill compltetly with water, its bust if it does.

Phil L

unread,
May 25, 2014, 12:38:26 PM5/25/14
to

Rick Hughes

unread,
May 25, 2014, 1:38:56 PM5/25/14
to
forgot to add if this is a closed loop ...which is sounds like, then
there will be an airvent on it somewhere (top of your tank ?) may be an
autovent type.
Or a bleed screw to let air out.

It won't be on the expansion vessel.

dazlew...@googlemail.com

unread,
May 25, 2014, 1:43:34 PM5/25/14
to
Hi, yes I realise the membrane separates the water side from the air side, but my question is how should I get rid of the air remaining on the water side from when it is first installed. As it stands there will be air on both sides of the membrane. This means there is an air space in contact with the hot water. I guess like an old style non-membrane expansion vessel. I just wondered if anyone thought this was an issue, and if so, what can I do as there is no means for bleedingg the water side of the membrane.

Cheers

RJS

unread,
May 26, 2014, 12:13:45 PM5/26/14
to
Sorry if this a stupid question Darren: is it essential that the expansion vessel is at the highest point of the system? In my pressurised system - admitedly only for CH - the pressure vessel is not at the highest point in the system and any air is bled from the towel rads and attic rad. So if you are using the PV to pressurise a water system, shouldn't there be an air bleed point higher than the PV?

Richard

dazlew...@googlemail.com

unread,
May 26, 2014, 1:52:46 PM5/26/14
to
I'm not sure if it needs to go at the highest point, that's just where mine was when I moved in - sitting on top of water tank on the upstairs level. I can't think of any technical reason why it needs to be there, but someone else might know otherwise. My question would apply wherever it is located (unless it was placed upside down lower in the system so the water would drain into the vessel (or at least the part where there is meant to be water!).

Darren

dennis@home

unread,
May 26, 2014, 5:28:51 PM5/26/14
to
The membrane will stop that.
There isn't any air in the vessel on the water side when its working.
The air pressure will keep the membrane filling the whole of the vessel
until the water gets to at least the precharge pressure.

Rick Hughes

unread,
May 26, 2014, 5:43:18 PM5/26/14
to
There has to be an air bleed somewhere ... as I mentioned on my install
the air bleed is an 'auto vent' on top of Thermal store ... not the
highest part of pipework but it works as air does end up there.

Follow the pipe run you will (or should) find either an auto air vent or
a manual bleed screw.

dazlew...@googlemail.com

unread,
May 26, 2014, 6:11:49 PM5/26/14
to
Hi

I cannot see any bleed at all on the hot potable circuit. There is an auto bleeder on the central heating circuit (I had to replace that too this weekend), but seemingly not one on the domestic water. Even of there were, my question is about bleeding air from the expansion vessel (the water side of the mebrane) because the expansion vessel is in effect on a spu at the highest point, I cannot see how bleeding from lower down can hel anyway.

I suspect over time the water will dissolve and come out that way.

Darrem

Onetap

unread,
May 27, 2014, 7:31:33 AM5/27/14
to
I understood the question.
I wouldn't bother.
The air (on the water side of the membrane) will just act as an additional expansion device, similar to the air trapped in a pressure gauge syphon tube.

The oxygen will dissolve and get carried out by the water.
The remaining nitrogen will gradually get entrained if/when the water speed exceeds 2 ft/s or so.
It doesn't do any harm and I can't see any need to remove it.
There's lots of dissolved oxygen in the mains water anyway. Some will come out of solution when the pressure drops, after the PRV set and refill the pipes anyway.

Mathew Newton

unread,
May 28, 2014, 8:21:14 AM5/28/14
to
Hi Darren,

On Sunday, 25 May 2014 11:47:41 UTC+1, dazlew...@googlemail.com wrote:

> Obviously the tank was full of air when I first connect it up and I am
> wondering if  I need to bleed the air from the water side of the membrane to
> fill it up with water? There seems to be no way to do it, and no suggestion
> it should be done, so I will presumably just contract legionaire's shortly?

Your premise regarding the initial state is incorrect. If pre-charged, which is the state that all expansion vessels are usually supplied in, there is very little air on the water side of the membrane hence they don't need to be bled.

Take a look at the following cut-away:

http://diy.blogoverflow.com/files/2013/02/Inside-Expansion-Tank.jpg

Of course, there can be no pressures involved in such a situation however it might help visualise how the diaphragm sits when pre-charged i.e. it doesn't sit midway down the vessel as you might otherwise think (if it did it'd have to stretch to accommodate the necessary movement which would do nothing for longevity).

The following diagram shows the subsequent accommodation of expansion:

http://docs.engineeringtoolbox.com/documents/1272/diaphragm-expansion-tank.png

Mathew

smac...@gmail.com

unread,
Aug 17, 2019, 11:56:47 AM8/17/19
to
Hi Mathew, I know that this is from an old post but I was just wondering the same question about possible air trapped on the water side of an expansion vessel. Your answer is brilliant and the addition of the pictures makes it all make sense so thanks for your time. Steve

harry

unread,
Aug 17, 2019, 1:19:08 PM8/17/19
to
On Sunday, 25 May 2014 11:47:41 UTC+1, dazlew...@googlemail.com wrote:
There is no air on the water side. When you buy the tank the diaphragm is fully deformed against the connection. It only moves away when the water pressure exceeds the air pressure.