Could anyone help a complete novice out with a problem he's having with
the above boiler?
Bled the radiator in the bedroom and now the pressure gauge on the
boiler is reading 0 bar and doesn't want to fire up.
No central heating or hot water but when the water / heating is turned
on there is hum from the device which may or may not be the fan and when
the hot taps are turned on it sounds like it should fire but doesn't.

Any help would be appreciated

Simon




--
simonw91

The Natural Philosopher

unread,
Nov 12, 2012, 9:06:29 AM11/12/12
to
re pressurise the boiler, dear boy.

There should be a tap and a link pipe that you can turn on
somewhere..may need reconnecting.


--
Ineptocracy

(in-ep-toc’-ra-cy) – a system of government where the least capable to
lead are elected by the least capable of producing, and where the
members of society least likely to sustain themselves or succeed, are
rewarded with goods and services paid for by the confiscated wealth of a
diminishing number of producers.

John Williamson

unread,
Nov 12, 2012, 9:11:39 AM11/12/12
to
The system needs repressurising, as bleeding the air out of the
radiators has reduced the pressure below the safe limit set by the
maker. The problem may be that the air was in the expansion vessel and
has now migrated into the heating system through a ruptured diaphragm.
This means the expansion vessel has failed.

Someone will no doubt have all the details to hand. Or, if he's not
confident about identifying the various bits, it's about due for a
service by a qualified guy anyway...


--
Tciao for Now!

John.

newshound

unread,
Nov 12, 2012, 9:16:14 AM11/12/12
to
On 12/11/2012 14:06, The Natural Philosopher wrote:
> On 12/11/12 09:47, simonw91 wrote:
>> Morning all
>>
>> EDIT
>>
>> This problem has been resolved.
>>
>> Could anyone help a complete novice out with a problem he's having with
>> the above boiler?
>> Bled the radiator in the bedroom and now the pressure gauge on the
>> boiler is reading 0 bar and doesn't want to fire up.
>> No central heating or hot water but when the water / heating is turned
>> on there is hum from the device which may or may not be the fan and when
>> the hot taps are turned on it sounds like it should fire but doesn't.
>>
>> Any help would be appreciated
>>
>> Simon
>>
>>
>>
>>
> re pressurise the boiler, dear boy.
>
> There should be a tap and a link pipe that you can turn on
> somewhere..may need reconnecting.
>
>

And don't be tempted to leave it open; there should be a pressure gauge
or possibly a digital display on the boiler. Pressurise it to just over
the minimum (because the pressure will also rise as it heats up, and you
don't want to lift the relief valve).

--
For every complex problem, there is a solution which is simple, neat,
and wrong.
H L Menken