I find that with the vent in the open position it leaks water from
around the little red cap at the top of the canister.
Should this happen? I was under the assumption it would allow
air out but not water.
Could anyone offer advice on this using one of these.
Should the canister be left in the open or closed position?
My only need for using it is that there is a high point in my plumbing
system which will trap a pocket of air.
Thanks
You should be able to leave it turned to the open position and with
the red cap loose and not have leaks.
If you do and can't fix it by cleaning the canister and float then it
is faulty and you need a replacement.
Andy Hall
Email by removing the word after the two letter,
top level Nordic country domain.
Cheers
Rob
Also had a problem with the same device. Mine started leaking after about 5
years. Even after the valve seat was cleaned it still leaked. I think the
valve mechanism had somehow lost its "spring". Fortunately the valve was
superfluous as there is another in the boiler and it was replaced with a
stop-end. If you need air release in that position consider a manual air
release valve.
Alan
Chris
"Alan James" <alanREMOVE...@hotmail.com> wrote in message
news:3dfe...@212.67.96.135...
>Personally, I have yet to find an auto-air release valve that does what it
>says on the tin. I think they all leak water, so I use mine manually - it's
>safer.
>
>Chris
Do you have hard water by any chance?
I'm wondering whether this could be a scale deposit issue.
I've had no problems at all with either the Honeywell AAV (made by
Brauckmann) or with an all brass type from Reliance, or with an air
separator also from Reliance, which works on the same principle but
with a taller chamber.
http://www.rwc.co.uk/rwc/hoprofs.htm
According to the instructions I have, the little red cap is meant to be
screwed tight after
initial venting. Is your little red cap loose?
>
> Could anyone offer advice on this using one of these.
> Should the canister be left in the open or closed position?
>
The main body of the device should be in the open position.
Also in the manual:
NOTE. Automatic air vents should only
be fitted to the positive pressure side
of the system.