On Sun, 01 Apr 2012 22:04:21 +0100, Andrew Gabriel <
and...@cucumber.demon.co.uk> wrote:
> In article <op.wb3tdtbuytk5n5@i7-940>,
> "Lieutenant Scott" <
n...@spam.com> writes:
>> On Sun, 01 Apr 2012 20:36:35 +0100, Andrew Gabriel <
and...@cucumber.demon.co.uk> wrote:
>>
>>> In article <op.wb3o4schytk5n5@i7-940>,
>>> "Lieutenant Scott" <
n...@spam.com> writes:
>>>> There's a gate valve on it with a red tap, which is switched off.
>>>>
>>>> What is this for?
>>>
>>> It's a crude bypass loop.
>>> It ensures there's still a flow path even if all the radiators
>>> shut off, and/or if the arrangement of valves for selecting
>>> heating/hot water have a mode where they're all closed.
>>>
>>> It probably shouldn't be shut off, unless the system has been
>>> modified since the original installation and no longer needs
>>> it. You can get special bypass loop valves to use instead of
>>> the gate valve which only open when the pump is trying to push
>>> against a closed circuit, so they don't bleed any flow into the
>>> return when there's a real demand for heat.
>>
>> Ah I see, thanks.
>>
>> It's possible I shut it off years ago and forgot.
>>
>> It used to be on a timer, and only limited by the thermostatic valves on the radiators, so it could block the pump without it.
>>
>> But I added a room stat and opened the radiator valves fully, so there will never be a blocked pump.
>
> Ideally, remove the TRV in the room with the stat, so it can't get
> turned off. You fit a stop valve instead (no knobs to turn).
I tend to leave all my doors open, so the whole house is at the same temperature.
I'd have to accidentally turn off six TRVs to cause a problem.
Mind you in the garage, only one (non thermostatic) valve. But its quite a number of turns, you couldn't knock it off by mistake.
>> I'll leave it shut for maximum power output.
>>
>> Would a pump actually break with no flow?
>
> No, but the boiler's heat exchanger would - it would overheat.
[ignore this line, I see you answered it below]
Surely the boiler would just cut out when it reached the desired water temperature and stay off, as it already does by cycling on and off to maintain the correct temperature in the flow pipe.
>> If so, what is the minimum flow required for the average pump? I could have the situation of only having one 10mm HEP pipe flowing (the garage circuit).
>
> You need to look at the boiler's instructions. The minimum is usually
> given as the minimum length of pipework around the bypass loop, so it's
> enough to absorb the heat still passing through the heat exchanger
> after the burner switches off, without causing the overheat stat to
> trip or the water in the exchanger to boil. Some modern boilers don't
> need an external bypass loop.
If it's just to remove that little bit of heat, I would imagine the flow through 10mm HEP would be sufficient.
Hang on a sec. If I switch off the heating at the point where the boiler is just about to stop burning, then no water is being pumped, and things don't break.
"You know that your landing gear is up and locked when it takes full power to taxi to the terminal."