If you have a 27kW boiler then about 300mm of 15mm pipe will drop the
permissible 1mb of pressure between the meter and the appliance! Your
boiler may be running "happily" but it will have seriously low pressure
at its inlet and will probably be running below its rated power.[1]
Since pressure drop as a function of flow rate is very non-linear
increasing the pipe diameter will allow much greater flow: you could run
almost 20m in 22mm pipe with an allowable drop[2], and with 28mm you
could run it down your street. And if the original boiler was rated at
around 12kW just for heating the house with a little extra for the HW
cylinder then it would probably have been fine on yards and yards of 15mm.
[1] you can measure it by timing the rate your gas meter runs with only
the boiler drawing gas. If you have a meter with a clock dial showing
cubic feet then time it for one revolution and divide 1100 by the time in
seconds to get kW. If it's digital take a couple of readings of the last
3 digits a minute or so apart, subtract the readings (to get litres of
gas) and multiply 38.6 by this volume and divide by the time (in seconds)
to get kW.
[2] counting every sharp 90 degree elbow or Tee as half a metre
--