Ceiling light wiring - how to extend (hypothetical)

248 views
Skip to first unread message

Mentalguy2k8

unread,
Aug 7, 2013, 9:04:54 AM8/7/13
to
Just fixed a ceiling light that had stopped working because one of the
earths had come out of the terminal inside the ceiling fitting.

Started me thinking, what if one of the wires had snapped off? There's only
just enough cabling to (just) reach the terminals inside the ceiling rose,
so what would the (sensible) option be? A chocolate block small enough to
fit inside the rose, or would you have to replace the whole cabling from
there to where it comes from?

Why are some sparkies so obsessed with leaving so little cable that it's
almost under tension when fitted? I put up a ceiling fan in my last house
and whatever wire I connected first, it left me with about an inch of gap to
put all the other wires in the right holes and screw up the fittings, while
balancing a heavy motor on my head. Ridiculous.

Frank Erskine

unread,
Aug 7, 2013, 9:38:12 AM8/7/13
to
On Wed, 7 Aug 2013 14:04:54 +0100, "Mentalguy2k8"
<Mental...@gmail.com> wrote:

>Just fixed a ceiling light that had stopped working because one of the
>earths had come out of the terminal inside the ceiling fitting.

Hmm - does it rely on an earth to work?

--
Frank

Dave Plowman (News)

unread,
Aug 7, 2013, 9:38:21 AM8/7/13
to
In article <kttgln$8tk$1...@dont-email.me>,
Mentalguy2k8 <Mental...@gmail.com> wrote:
> Just fixed a ceiling light that had stopped working because one of the
> earths had come out of the terminal inside the ceiling fitting.

You really need to have it checked over professionally if an earth coming
adrift stopped it working. Could be a very dangerous fault.

--
*Isn't it a bit unnerving that doctors call what they do "practice?"

Dave Plowman da...@davenoise.co.uk London SW
To e-mail, change noise into sound.

Archibald

unread,
Aug 7, 2013, 9:48:24 AM8/7/13
to
On Wed, 7 Aug 2013 14:04:54 +0100, "Mentalguy2k8"
<Mental...@gmail.com> wrote:

If it stopped working because one of the earths came off, I would
humbly suggest you rethink your faultfinding approach, and maybe take
another look.

Personally I would stick another JB in the ceiling, although you can
get small boxes containing a bit of barrier strip now.

AB

Rob Morley

unread,
Aug 7, 2013, 11:29:53 AM8/7/13
to
On Wed, 7 Aug 2013 14:04:54 +0100
"Mentalguy2k8" <Mental...@gmail.com> wrote:

> Just fixed a ceiling light that had stopped working because one of
> the earths had come out of the terminal inside the ceiling fitting.
>
An earth coming adrift won't stop a light from working unless it's
wired incorrectly. Wonder why an unexposed cable would come loose.

bert

unread,
Aug 7, 2013, 11:58:17 AM8/7/13
to
In message <20130807162953.77166261@hyperion>, Rob Morley
<nos...@ntlworld.com> writes
Probably because it was installed by one of Adam's ace apprentices?
That's what happened with our extension - on 3 separate light fittings.
--
bert

Mentalguy2k8

unread,
Aug 7, 2013, 12:09:44 PM8/7/13
to

"Rob Morley" <nos...@ntlworld.com> wrote in message
news:20130807162953.77166261@hyperion...
I should have said that I tightened all of the wires up while I had it open
and the electricity off, I didn't think any of the others were noticably
loose but maybe one was, a couple of them (and the obviously misplaced earth
one) had been put into the fitting without (it looked to me) having had the
insulation stripped back properly first. I stripped them back a bit "just in
case" and refitted them nice and tightly.

If it makes any difference, it is a simple on/off switch that used to be a
metal dimmer switch and it controls 2 ceiling lights about 12 feet apart. No
idea why it stopped working when it did, it was OK one day and the next day
the lights were dead.

charles

unread,
Aug 7, 2013, 12:16:22 PM8/7/13
to
In article <acj409pmd42ntudgl...@4ax.com>,
some fluorescent needed the body earthed to get the tube to strike.

--
From KT24

Using a RISC OS computer running v5.18

Dave Plowman (News)

unread,
Aug 7, 2013, 12:46:01 PM8/7/13
to
In article <53778e45...@charleshope.demon.co.uk>,
charles <cha...@charleshope.demon.co.uk> wrote:
> In article <acj409pmd42ntudgl...@4ax.com>,
> Frank Erskine <frank....@btinternet.com> wrote:
> > On Wed, 7 Aug 2013 14:04:54 +0100, "Mentalguy2k8"
> > <Mental...@gmail.com> wrote:

> > >Just fixed a ceiling light that had stopped working because one of
> > >the earths had come out of the terminal inside the ceiling fitting.

> > Hmm - does it rely on an earth to work?

> some fluorescent needed the body earthed to get the tube to strike.

That's going back a bit. ;-)

--
*Why doesn't glue stick to the inside of the bottle?

ARW

unread,
Aug 7, 2013, 12:57:17 PM8/7/13
to
Mentalguy2k8 wrote:
> "Rob Morley" <nos...@ntlworld.com> wrote in message
> news:20130807162953.77166261@hyperion...
>> On Wed, 7 Aug 2013 14:04:54 +0100
>> "Mentalguy2k8" <Mental...@gmail.com> wrote:
>>
>>> Just fixed a ceiling light that had stopped working because one of
>>> the earths had come out of the terminal inside the ceiling fitting.
>>>
>> An earth coming adrift won't stop a light from working unless it's
>> wired incorrectly. Wonder why an unexposed cable would come loose.
>
> I should have said that I tightened all of the wires up while I had
> it open and the electricity off, I didn't think any of the others
> were noticably loose but maybe one was, a couple of them (and the
> obviously misplaced earth one) had been put into the fitting without
> (it looked to me) having had the insulation stripped back properly
> first. I stripped them back a bit "just in case" and refitted them
> nice and tightly.

Is this "earth sleeving" or "proper insulation" covering the earth cable?

--
Adam


charles

unread,
Aug 7, 2013, 1:09:00 PM8/7/13
to
In article <537790f...@davenoise.co.uk>,
Dave Plowman (News) <da...@davenoise.co.uk> wrote:
> In article <53778e45...@charleshope.demon.co.uk>,
> charles <cha...@charleshope.demon.co.uk> wrote:
> > In article <acj409pmd42ntudgl...@4ax.com>,
> > Frank Erskine <frank....@btinternet.com> wrote:
> > > On Wed, 7 Aug 2013 14:04:54 +0100, "Mentalguy2k8"
> > > <Mental...@gmail.com> wrote:

> > > >Just fixed a ceiling light that had stopped working because one of
> > > >the earths had come out of the terminal inside the ceiling fitting.

> > > Hmm - does it rely on an earth to work?

> > some fluorescent needed the body earthed to get the tube to strike.

> That's going back a bit. ;-)

but some are still inservice ;-(

Mentalguy2k8

unread,
Aug 7, 2013, 1:24:25 PM8/7/13
to

"ARW" <adamwa...@blueyonder.co.uk> wrote in message
news:kttu9i$jsb$1...@dont-email.me...
On the earth cable was a loose-fitting green and yellow striped sleeve,
could be just pulled off with the fingers. It was this that was held by the
screw in the fitting, either the earth cable was never put in there or it
popped out at some point.

spuorg...@gowanhill.com

unread,
Aug 7, 2013, 1:55:30 PM8/7/13
to
Mentalguy2k8 wrote:
> Started me thinking, what if one of the wires had snapped off? There's only
> just enough cabling to (just) reach the terminals inside the ceiling rose,
> so what would the (sensible) option be? A chocolate block small enough to
> fit inside the rose, or would you have to replace the whole cabling from
> there to where it comes from?

I have a bathroom light where the choc block is already wedged up to the ceiling with the wire ends just about poking out of the ceiling far enough to be caught by the terminals.

Some form of crimp might do if I could find crimp tool that will do 'end on' crimp instead of requiring sideways access to the cable.

I shall require similar if I am to repuropse the obsolete underfloor heating thermostat wires into 2 amp sockets for the 'tannoy' system. The wires have all been cut short in the BESA boxes.

Owain

Graham.

unread,
Aug 7, 2013, 1:59:54 PM8/7/13
to
On Wed, 7 Aug 2013 10:55:30 -0700 (PDT), spuorg...@gowanhill.com
wrote:
Well a man needs something to summon SWMBO with pipe & slippers.


--
Graham.

%Profound_observation%

The Natural Philosopher

unread,
Aug 7, 2013, 4:30:37 PM8/7/13
to
this is where I break out the soldering iron and the heatshrink....


--
Ineptocracy

(in-ep-toc’-ra-cy) – a system of government where the least capable to lead are elected by the least capable of producing, and where the members of society least likely to sustain themselves or succeed, are rewarded with goods and services paid for by the confiscated wealth of a diminishing number of producers.

spuorg...@gowanhill.com

unread,
Aug 7, 2013, 5:53:10 PM8/7/13
to
Graham. wrote:
> >I shall require similar if I am to repuropse the obsolete underfloor
> >heating thermostat wires into 2 amp sockets for the 'tannoy' system.
> >The wires have all been cut short in the BESA boxes.
> Well a man needs something to summon SWMBO with pipe & slippers.

It's so I can have classic FM in the bathroom.

There are a variety of PBXen for telephonically summoning the domestics.

Owain

Brian Gaff

unread,
Aug 7, 2013, 5:54:25 PM8/7/13
to
Could have looked good on You bin framed though.
No idea as to why its done, but its nothing new. My house wired in the 70s
is just the same.

Brian

--
From the Sofa of Brian Gaff Reply address is active
"Mentalguy2k8" <Mental...@gmail.com> wrote in message
news:kttgln$8tk$1...@dont-email.me...

Mentalguy2k8

unread,
Aug 8, 2013, 6:24:29 AM8/8/13
to

"Brian Gaff" <Bri...@blueyonder.co.uk> wrote in message
news:ktufmc$pbt$1...@dont-email.me...
> Could have looked good on You bin framed though.
> No idea as to why its done, but its nothing new. My house wired in the 70s
> is just the same.

Maybe they're different now, but I remember wondering at the time why they
didn't make the terminal block removable so you could wire it all up and
*then* plug the main motor unit into it instead of having to hold the whole
thing up with one hand and try to push wires into terminals and screw them
up with the other.

John Rumm

unread,
Aug 8, 2013, 9:14:43 AM8/8/13
to
Like:

http://www.tlc-direct.co.uk/Products/TLCT101C.html



--
Cheers,

John.

/=================================================================\