On 20/06/2021 11:35, Max Demian wrote:
> On 20/06/2021 08:15, Tim+ wrote:
>>
>> EV “granny leads” plug into a standard 13 amp socket and draw about 10
>> amps
>> continuously. Because of the prolonged nature of the load, the plugs
>> usually have overheat protection built it.
Unless you put it under a duvet I can't see that there should really be
a problem. You can buy overheat thermal cutouts quite cheaply but I
don't know of any integral to a 13A plug.
>> This is fine and dandy unless you find yourself in a situation where you
>> have to use an extension lead. Now the thermal protection is in the
>> middle
>> of the chain so to speak (and probably outdoors where little harm can
>> result) but now the plug on the extension lead is unprotected.
>>
>> So, I was wondering if such a thing as either a plug with a built in
>> thermal cutout exists or whether it’s possible to add a self-resetting
>> thermal cutout into a conventional 13amp plug.
>>
>> Does this sound possible? What would be a “safe” temperature limit for
>> such a plug?
>
> You either need better quality connections or to reduce the load. 13A
> plugs, sockets and leads [1] certainly should take 13A continuously;
> people do/did it for 3KW electric heaters. If they don't they're not
> "fit for purpose".
Actually it has been found that 13A continuous load on a nominal 13A
socket is somewhat problematic and life shortening for both the plug and
the socket. That is one of the reasons why many portable heating
appliances have been derated to 2.4kW maximum (ie 10A). You can get away
with it for a kettle that only runs for a couple of minutes but not for
a room heater that might draw 3kW for many hours continuously.
>
> [1] Assuming the lead isn't wound onto a reel.
I'd have thought most decent plugs and sockets could stand 10A current
draw almost indefinitely. The plug *will* get warm to the touch though
due to thermal dissipation in the fuse. Fuses typically will blow in
just a few minutes at twice their nominal rated current.
--
Regards,
Martin Brown