On 20/09/2021 07:54, Kevin Holohan wrote:
> I was investigating a crackling light switch in the garage yesterday.
> The switch also provides power to an outside PIR security light which
> the previous owner of the house had provisioned. Removing the switch
> showed there was just live/switched live and earth for the garage
> light, so the individual (not me!) who connected the outside light
> used the earth as the neutral.
Have you checked at the other end of that cable to see what the earth
wire is connected to there?
Obviously using an actual earth as a neutral is unacceptable for many
reasons, however it might be that the earth wire was repurposed as an
actual neutral by connecting it as such at *both* ends.
(if you do that then it must be over marked at both ends - and you can
only do it on a wire that is part of a cable - not a single).
I am guessing from the RCD comment that was probably not what happened!
> I guess the logic was that neutral and
> earth are connected back together at some point (either in the meter
> cupboard or at the local substation) but I don't think this
> arrangement is entirely acceptable. I have disconnected the outside
> security light and I will run a cable from the garage ceiling light
> to allow a more suitable connection to the lighting circuit for the
> security light. A couple of years ago I did replace my old CU with
> one using RCBOs. One lighting circuit (this one!) would not allow the
> RCBO to latch so I replaced it with a regular MCB. I wonder if
> borrowing the neutral was the reason for the RCBO not wanting to
> latch on?
Yup that would do it if there was any load on the connected back to
earth circumventing the RCD.
--
Cheers,
John.
/=================================================================\