I'm building a small two-bedroomed end-terrace house, approx 7 x 5M in
size. Latest building regs, including Part L, so insulation is pretty
good.
I'm going to use a Worcester 25 Si, which is more than sufficient for
this house.I want to use the smallest radiators I can, but obviously
big enough to do the job.
I've used a couple of different calculators, and I'm getting very
different results. The "advanced" calculator on
http://www.radiatorsizingcalculator.co.uk/ is giving me a power
requirement of more than twice what the Barlo heatloss calculator
does.
I'm tending to believe the Barlo heatloss calculator, because although
it's very old, the laws of physics don't change. And the Barlo
calculator allows me to enter the U-Values, whereas I don't know what
assumptions the radiatorsizingcalculator site uses.
For example, with one 2.48m x 2.37m room, the Barlo calculator says I
need 308 watts, which seems incredibly low. The
radiatorsizingcalculator site reckons I need 686 w.
My U-values are:
External wall: 0.16 (2 x 100mm thermalite + 100mm filled cavity)
Windows: 1.5 (Energy Class B uPVC double glazing)
Floor: 0.16 (solid floor with 100mm kooltherm K3)
1st floor ceiling: 0.13
I'm assuming:
Room temp 21 degrees
Outside air temp -1 degrees
Ground temp 10 degrees (guess)
1.5 air changes per hour (guess)
Can anyone see anything obviously wrong with my assumptions,
especially the number of air changes and the ground temp?
It looks like the total heating requirement will be under 3KW, which
seems crazy low for 70 square metres of living space.