On 18/06/2013 12:18, Ivan Dobsky wrote:
> I've always switched off the whole lot at the consumer unit, but the bloke
> next door but one says he's happy to just pull out one of the fuses. I know
> what he's saying, and I understand why he's not killed himself yet, but I'm
> too much of a coward to do this myself. My feeling is, with the fuse pulled,
> the neutral is still connected, and if you're unlucky, something could
> happen outside of the property which might make it suddenly become live. Or
> am I being too cautious?
Its appropriate to be cautious, and you rightly recognise that there are
still risks working on a circuit with the neutral connected. One of the
most common problems with modern installations is that its very easy to
trip the RCD protecting a circuit with a neutral to earth short while
working on it.
> It is sometimes a pain having to switch everything
> off, and if pulling the relevant fuse was sufficient, I'd rather do that.
If you are going to do extensive work[1] on a circuit, then its safest
to turn it off, and then open the CU and disconnect its neutral from the
neutral bus bar. (if someone has wired it nicely, it may even be in the
numbered position to match that of the MCB!). Once its disconnected,
your only real risk is from a cross connection to another circuit.
Testing your tester on the working circuit first is sensible. Include
tests between each pole and earth as well. Disconnect and then repeat.
That will pick up most of the possible non conventional wiring issues.
For complete peace of mind, then test the tester on a working circuit
again.
[1] If I were just changing a lightswitch or similar, I would probably
just turn off the MCB at the CU and leave the neutral connected. (I also
have the advantage of having wired the CU in the first place and tested
all the circuits, so I know what is connected to what!)