This is the oil burner safety control (model DKO 970) on my Wallstar
15/20 boiler, which once again is playing up.
I downloaded the 6-page manual
http://tinyurl.com/bz56n77 for the
DKO 970 and studied the flash codes.
In the manual on page 2 in the paragraph "1.2 Lock-out diagnoses" it
says the following:
In case of a failure the LED is permanently illuminated. Every
10 seconds the illumination is interrupted by a flash code,
which indicates the cause of the error. Therefore the following
sequence is performed which is repeated as long as the unit
is not reset.
Sequence:
illuminated phase dark phase Flash-Code dark phase
x z z z z
[where illuminated phase = 10 sec, dark phase = 0.6 sec, second dark
phase = 1.2 sec -- I can't fit all that on one line in FreeAgent
like in the actual PDF]
Error diagnosis
Error message: lockout
Flash-Code: x z z z z
Possible fault: within lock out safety time
no flame establishment
[where x = short pulse, z = long pulse]
This is the sequence I observe on my boiler when it won't start.
So my question is:
What does "within lock out safety time no flame establishment" mean in
layman's language?
Does this point to the burner, the igniter, the solenoid, or another
component?
NB: The boiler ALWAYS starts when I press the reset button on the DKO
970. I never have to press it more than once. The boiler then runs
perfectly, cycling through on/off phases exactly as it should.
But next morning it won't start and the above flash code sequence can
be observed. There's plenty of oil in the tank.
Thanks.
MM