I've just moved house and notice that the Siemans electricity meter
has a red light wich is flashing slowly. Plus the LCD display is
flashing between 8888 and the current reading. Does anyone know what
this signifies?

Colin Wilson

unread,
Jun 17, 2007, 2:52:24 PM6/17/07
to

The flashing red light indicates usage, and somewhere on the meter
will probably be a reference to xxxx flashes per kWh

The 8888 is simply a test pattern to prove the meter has all the
display segments working correctly.

Dave Liquorice

unread,
Jun 17, 2007, 6:04:23 PM6/17/07
to
On Sun, 17 Jun 2007 08:41:12 -0700, lemmy wrote:

> I've just moved house and notice that the Siemans electricity meter
> has a red light wich is flashing slowly.

The light flashes once for each 1W/hr consumed (ie 1000 flashes per kW/hr)

> Plus the LCD display is flashing between 8888 and the current reading.

Shows that all the segments of the display are working and thus the
numbers shown are correct. No confusion between say 8 and 0, or 7 and 1
etc.

--
Cheers new...@howhill.com
Dave. pam is missing e-mail

Message has been deleted

Mike Harrison

unread,
Jun 17, 2007, 6:45:46 PM6/17/07
to
On Sun, 17 Jun 2007 15:37:36 -0700, Part timer <hhmn...@googlemail.com> wrote:

>On one of those Sky Three "law-and-order" type programmes 2 cops were
>hunting down a dodgy white van (permanantly borrowed from a rental
>fleet). Terraced houses, lots of cars parked, they had a look into the
>van and a cutain twitched in a nearby house. "Ello ello ello!" - they
>knock on the door. No answer. Looked through letterbox - smell of hash
>plantation! The two young lads leg it out of the back and are caught.
>One cop noticed the electricity meter was giving it all the 8s,
>flashing between the current reading - and he said it had been
>tampered with (obvious as the tails were linked to the incomers in a
>very dodgy way).

Hmmm which is the most likely :
a) Test pattern to show that the display is correct.
b) Copper that knows anything about electronic electricity meters.

The Wanderer

unread,
Jun 18, 2007, 2:43:47 AM6/18/07
to
On Sun, 17 Jun 2007 23:04:23 +0100 (BST), Dave Liquorice wrote:

> On Sun, 17 Jun 2007 08:41:12 -0700, lemmy wrote:
>
>> I've just moved house and notice that the Siemans electricity meter
>> has a red light wich is flashing slowly.
>
> The light flashes once for each 1W/hr consumed (ie 1000 flashes per kW/hr)

No, I don't think so. See the reply from Colin Wilson.

--
the dot wanderer at tesco dot net

David Hansen

unread,
Jun 18, 2007, 3:46:25 AM6/18/07
to
On Mon, 18 Jun 2007 07:43:47 +0100 someone who may be The Wanderer
<m...@privacy.net> wrote this:-

>> The light flashes once for each 1W/hr consumed (ie 1000 flashes per kW/hr)
>
>No, I don't think so. See the reply from Colin Wilson.

You mean the one where he typed, "The flashing red light indicates


usage, and somewhere on the meter will probably be a reference to

xxxx flashes per kWh"?

While it may or may not be 1000 flashes per unit, the light flashing
certainly does indicate usage.


--
David Hansen, Edinburgh
I will *always* explain revoked encryption keys, unless RIP prevents me
http://www.opsi.gov.uk/acts/acts2000/00023--e.htm#54

The Wanderer

unread,
Jun 18, 2007, 5:49:22 AM6/18/07
to
On Mon, 18 Jun 2007 08:46:25 +0100, David Hansen wrote:

> On Mon, 18 Jun 2007 07:43:47 +0100 someone who may be The Wanderer
> <m...@privacy.net> wrote this:-
>
>>> The light flashes once for each 1W/hr consumed (ie 1000 flashes per kW/hr)
>>
>>No, I don't think so. See the reply from Colin Wilson.
>
> You mean the one where he typed, "The flashing red light indicates
> usage, and somewhere on the meter will probably be a reference to
> xxxx flashes per kWh"?
>
> While it may or may not be 1000 flashes per unit, the light flashing
> certainly does indicate usage.

Err, yes, and my reference to CW's answer made it quite clear that I wasn't
disputing that the light flashes to indicate usage.

What I was disputing was the statement that the light flashes once for
every watthour. It is an erroneous statement that might mislead others. Or
are you suggesting that we should collectively turn a blind eye to
misinformation?

Message has been deleted

Alex

unread,
Jun 18, 2007, 6:57:16 AM6/18/07
to
AJH wrote:
> Has anybody made a counter that sees the flashes and data logs them
> off a usb port? Must be better than the clamp on things that are being
> shown on the news.

http://offog.org/code/electricity.html

Alex

David Hansen

unread,
Jun 18, 2007, 6:59:04 AM6/18/07
to
On Mon, 18 Jun 2007 10:49:22 +0100 someone who may be The Wanderer
<m...@privacy.net> wrote this:-

>What I was disputing was the statement that the light flashes once for
>every watthour.

The meter in the office is labelled "1000 imp/kWh". I assume that
"imp" stands for impulses, AKA flashes.

lemmy

unread,
Jun 18, 2007, 8:23:47 AM6/18/07
to
So everything's ok. Thanks very much for all the info.


The Wanderer

unread,
Jun 18, 2007, 9:44:00 AM6/18/07
to
On Mon, 18 Jun 2007 11:59:04 +0100, David Hansen wrote:

> On Mon, 18 Jun 2007 10:49:22 +0100 someone who may be The Wanderer
> <m...@privacy.net> wrote this:-
>
>>What I was disputing was the statement that the light flashes once for
>>every watthour.
>
> The meter in the office is labelled "1000 imp/kWh". I assume that
> "imp" stands for impulses, AKA flashes.

And the one here at home is labelled 800 imp/kwh. Which proves my point
that the earlier statement that the meter flashes once for every watthour
consumed is misleading. It *may* do, but other calibrations exist.

Message has been deleted

nickt

unread,
Jul 21, 2007, 6:46:39 AM7/21/07
to

www.calc-electric.com (£5, uses a webcam)

Lurch

unread,
Jul 21, 2007, 6:51:10 AM7/21/07
to
On Sat, 21 Jul 2007 03:46:39 -0700, nickt <nick...@yahoo.co.uk>
mused:

Spamming cunt.
--
Regards,
Stuart.

Keith

unread,
Jul 21, 2007, 9:23:30 AM7/21/07
to
In message <1185014799.7...@r34g2000hsd.googlegroups.com>,
nickt <nick...@yahoo.co.uk> writes

Which requires a computer on 24/7 to tell you how much you're wasting by
leaving things switched on 24/7.


--
Keith

Bob Eager

unread,
Jul 21, 2007, 10:23:17 AM7/21/07
to
On Sat, 21 Jul 2007 13:23:30 UTC, Keith <roadru...@blueyonder.co.uk>
wrote:

> In message <1185014799.7...@r34g2000hsd.googlegroups.com>,
> nickt <nick...@yahoo.co.uk> writes
> >On 18 Jun, 11:57, Alex <a...@kent.ac.uk> wrote:
> >> AJH wrote:
> >> > Has anybody made a counter that sees the flashes and data logs them
> >> > off a usb port? Must be better than the clamp on things that are being
> >> > shown on the news.
> >>
> >> http://offog.org/code/electricity.html
> >

> >www.calc-electric.com (ú5, uses a webcam)


>
> Which requires a computer on 24/7 to tell you how much you're wasting by
> leaving things switched on 24/7.

Not a problem..I have several computers on 24/7...!

--
The information contained in this post is copyright the
poster, and specifically may not be published in, or used by
http://www.diybanter.com

Grend

unread,
Jul 9, 2017, 7:44:05 AM7/9/17
to
replying to The Wanderer, Grend wrote:
Hi there
It would seem to me that these meters are flashing their LED to indicate Watts
and not Watt/hours.
If my (1000imp) LED flashed 1000 times in an hour then that is indeed 1KW/hr
but what if it takes 2 hours to flash 1000 times? or only 30 minutes? Is it
just me or is everyone else wrong?
G

--
for full context, visit https://www.homeownershub.com/uk-diy/electricity-meter-flashing-light-402309-.htm


Tim Watts

unread,
Jul 9, 2017, 7:55:15 AM7/9/17
to
On 09/07/17 12:44, Grend wrote:
> replying to The Wanderer, Grend wrote:
> Hi there
> It would seem to me that these meters are flashing their LED to indicate
> Watts
> and not Watt/hours.
> If my (1000imp) LED flashed 1000 times in an hour then that is indeed
> 1KW/hr
> but what if it takes 2 hours to flash 1000 times? or only 30 minutes?
> Is it
> just me or is everyone else wrong?
> G
>

It's my understanding that the LED blinks for every "unit" of energy
passed, for some definition of "unit" (not necessarily 1kWh).

John Rumm

unread,
Jul 9, 2017, 8:01:26 AM7/9/17
to
On 09/07/2017 12:44, Grend wrote:
> replying to The Wanderer, Grend wrote:
> Hi there
> It would seem to me that these meters are flashing their LED to indicate
> Watts
> and not Watt/hours.
> If my (1000imp) LED flashed 1000 times in an hour then that is indeed
> 1KW/hr
> but what if it takes 2 hours to flash 1000 times? or only 30 minutes?

> Is it
> just me or is everyone else wrong?

Its just you.

Please when replying to a thread that is over ten years old, post a
snippet of the text you are replying to in your message so we know what
you are talking about. Most of us a reading this on usenet, not a web site.




--
Cheers,

John.

/=================================================================\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\=================================================================/

Andy Burns

unread,
Jul 9, 2017, 9:46:47 AM7/9/17
to
Grend wrote:

> It would seem to me that these meters are flashing their LED to indicate Watts
> and not Watt/hours.
> If my (1000imp) LED flashed 1000 times in an hour then that is indeed 1KW/hr
It is not 1 kilowatt per hour (Kw/h) but 1 kilowatt-hour (kWh)

> but what if it takes 2 hours to flash 1000 times? or only 30 minutes? Is it

If it flashes 1000 times in an ten minutes, or 1000 times in a
fortnight, that's still 1kWh

dennis@home

unread,
Jul 9, 2017, 12:25:54 PM7/9/17
to
On 09/07/2017 12:44, Grend wrote:
> replying to The Wanderer, Grend wrote:
> Hi there
> It would seem to me that these meters are flashing their LED to indicate
> Watts
> and not Watt/hours.
> If my (1000imp) LED flashed 1000 times in an hour then that is indeed
> 1KW/hr
> but what if it takes 2 hours to flash 1000 times? or only 30 minutes?
> Is it
> just me or is everyone else wrong?
> G
>

A kw hr is a unit of energy and has no actual time dependent part.

It the number of joules used by a 1kw load in an hour, or a 2kw load in
30 minutes, etc.

You will get 1000 flashes for each kw hr of energy used whatever time it
takes.

You can determine the actual watts by timing the flashes if you want or
count them to see how much energy you have used.

ARW

unread,
Jul 9, 2017, 1:10:15 PM7/9/17
to
On 09/07/2017 17:25, dennis@home wrote:
> On 09/07/2017 12:44, Grend wrote:
>> replying to The Wanderer, Grend wrote:
>> Hi there
>> It would seem to me that these meters are flashing their LED to
>> indicate Watts
>> and not Watt/hours.
>> If my (1000imp) LED flashed 1000 times in an hour then that is indeed
>> 1KW/hr
>> but what if it takes 2 hours to flash 1000 times? or only 30
>> minutes? Is it
>> just me or is everyone else wrong?
>> G
>>
>
> A kw hr is a unit of energy and has no actual time dependent part.

If it's not time dependent then why is there the hr mark in there?

--
Adam

Brian Gaff

unread,
Jul 9, 2017, 1:13:19 PM7/9/17
to
If it flashes and nobody is there to see it, has it really flashed at all?
Brian

--
----- -
This newsgroup posting comes to you directly from...
The Sofa of Brian Gaff...
bri...@blueyonder.co.uk
Blind user, so no pictures please!
"Tim Watts" <tw_u...@dionic.net> wrote in message
news:t5i93e-...@squidward.local.dionic.net...

Steve Walker

unread,
Jul 9, 2017, 1:22:31 PM7/9/17
to
It is an amount of energy. It doesn't matter whether you use 0.5kW for 2
hours or 2kW for 0.5 hours, it is equivalent to taking 1kW for 1 hour.
Yes time is used in the calculation, but the final result is not time
dependent , it is simply an amount, which could be spread over any
length of time. To see this, simply convert kWh into Joules ... again a
simple amount of energy, but no mention of time.

SteveW

The Natural Philosopher

unread,
Jul 9, 2017, 1:24:41 PM7/9/17
to
On 09/07/17 18:22, Steve Walker wrote:
> On 09/07/2017 18:10, ARW wrote:
>> On 09/07/2017 17:25, dennis@home wrote:
>>> On 09/07/2017 12:44, Grend wrote:
>>>> replying to The Wanderer, Grend wrote:
>>>> Hi there
>>>> It would seem to me that these meters are flashing their LED to
>>>> indicate Watts
>>>> and not Watt/hours.
>>>> If my (1000imp) LED flashed 1000 times in an hour then that is indeed
>>>> 1KW/hr
>>>> but what if it takes 2 hours to flash 1000 times? or only 30
>>>> minutes? Is it
>>>> just me or is everyone else wrong?
>>>> G
>>>>
>>>
>>> A kw hr is a unit of energy and has no actual time dependent part.
>>
>> If it's not time dependent then why is there the hr mark in there?
>

to get rid of any time dependency.




--
Socialism is the philosophy of failure, the creed of ignorance and the
gospel of envy.

Its inherent virtue is the equal sharing of misery.

Winston Churchill

dennis@home

unread,
Jul 9, 2017, 2:37:36 PM7/9/17
to
On 09/07/2017 18:10, ARW wrote:
To confuse people?

Bob Minchin

unread,
Jul 9, 2017, 2:40:44 PM7/9/17
to
Because there is already time built into the watt and the two cancel out

ARW

unread,
Jul 9, 2017, 3:25:11 PM7/9/17
to
It does a good job of it.





--
Adam

bert

unread,
Jul 9, 2017, 5:47:57 PM7/9/17
to
In article <ojtt41$ho9$1...@dont-email.me>, Bob Minchin
<bob.minc...@YOURHATntlworld.com> writes
What time is it?
--
bert

Fredxxx

unread,
Jul 9, 2017, 6:00:40 PM7/9/17
to
On 09/07/2017 21:51, Huge wrote:
> A kW/hr is a unit of volume.

Is it?

I would say it was M . L^2 . T^-4 ?

Otherwise your post went over my head!

dennis@home

unread,
Jul 9, 2017, 6:04:25 PM7/9/17
to
On 09/07/2017 22:46, bert wrote:

> What time is it?

22:46 when you posted.
Its in the header.

dennis@home

unread,
Jul 9, 2017, 6:25:47 PM7/9/17
to
Its 3,600,000 joules of energy.

Fredxxx

unread,
Jul 9, 2017, 7:17:10 PM7/9/17
to
The poster said kW/hr which is a rate of change of power. However, I
doubt that is what he meant.

3,600,000 joules is a kW.hr

Fredxxx

unread,
Jul 9, 2017, 7:26:33 PM7/9/17
to
On 09/07/2017 17:25, dennis@home wrote:
> On 09/07/2017 12:44, Grend wrote:
>> replying to The Wanderer, Grend wrote:
>> Hi there
>> It would seem to me that these meters are flashing their LED to
>> indicate Watts
>> and not Watt/hours.
>> If my (1000imp) LED flashed 1000 times in an hour then that is indeed
>> 1KW/hr
>> but what if it takes 2 hours to flash 1000 times? or only 30
>> minutes? Is it
>> just me or is everyone else wrong?
>> G
>>
>
> A kw hr is a unit of energy and has no actual time dependent part.

That depends on whether energy itself has a time dependent part.

My own feeling is that it does, as indeed this article and other
articles would have us believe:

http://www.efm.leeds.ac.uk/CIVE/CIVE1400/Section5/dimensional_analysis.htm

John Rumm

unread,
Jul 9, 2017, 9:41:35 PM7/9/17
to
On 09/07/2017 18:10, ARW wrote:
kw are a measure of power, and hours a measure of time, so you have in
effect power multiplied by time.

Power is the rate of flow of energy - i.e. energy divided by time, so
with kw h you are getting:

energy
------ x time
time

Two times cancel out, and leave you a measure of energy with no rate of
use component.

Bob Minchin

unread,
Jul 10, 2017, 5:12:47 AM7/10/17
to
It does not matter

dimensionally watts= energy/time

again dimensionally, watt.hrs = (energy/time).time = energy


David

unread,
Jul 10, 2017, 11:08:09 AM7/10/17
to
On Sun, 09 Jul 2017 18:13:15 +0100, Brian Gaff wrote:

> If it flashes and nobody is there to see it, has it really flashed at
> all?
> Brian

If I understand the current laws on indecent exposure, it still counts if
nobody is watching.

Bears are now nervous about shitting in the woods.

Cheers



Dave R


--
AMD FX-6300 in GA-990X-Gaming SLI-CF running Windows 7 Pro x64

---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus

Dave W

unread,
Jul 10, 2017, 4:08:32 PM7/10/17
to
On 09/07/2017 12:44, Grend wrote:
> replying to The Wanderer, Grend wrote:
> Hi there
> It would seem to me that these meters are flashing their LED to indicate
> Watts
> and not Watt/hours.
> If my (1000imp) LED flashed 1000 times in an hour then that is indeed
> 1KW/hr
> but what if it takes 2 hours to flash 1000 times? or only 30 minutes?
> Is it
> just me or is everyone else wrong?
> G
>
You say 1000 flashes in an hour = 1 kilowatt flowing every hour. 1000
flashes actually means 1000 watt-hours have been consumed. If it takes 2
hours or 30 minutes or any other period for 1000 flashes, 1000
watt-hours have still been consumed, but not at the same wattage.

The unit is watt-hours, not watts per hour which doesn't make sense.
--
Dave W

The Natural Philosopher

unread,
Jul 11, 2017, 3:48:33 AM7/11/17
to
On 10/07/17 21:07, Dave W wrote:
> The unit is watt-hours, not watts per hour which doesn't make sense.

It does. Its the ramp rate of a power source or sink.

I.e. in the UK when the sun rises on a sunny summers day the power
output of all thjose solar panels rises at a peak of about 3GW per hour..

--
"Socialist governments traditionally do make a financial mess. They
always run out of other people's money. It's quite a characteristic of them"

Margaret Thatcher

Andy Burns

unread,
Jul 11, 2017, 6:19:34 AM7/11/17
to
The Natural Philosopher wrote:

> Dave W wrote:
>
>> The unit is watt-hours, not watts per hour which doesn't make sense.
>
> It does. Its the ramp rate of a power source or sink.
> I.e. in the UK when the sun rises on a sunny summers day the power
> output of all thjose solar panels rises at a peak of about 3GW per hour..

Or Dinorwig starting from zero (actually a small negative power when
spinning in air) to full output = 0.4 TW/h

Shame it can't keep that up for more than 16 seconds ...