On 22/11/2013 00:28, MJA wrote:
> Thanks for all the useful responses.
>
> On 2013-11-17, John Rumm <see.my.s...@nowhere.null> wrote:
>> On 17/11/2013 13:59, MJA wrote:
>>
>>> Anyone have any pointers to hot water cylinder heat exchanger
>>> efficiency data?
>>
>> Yup...
>
> I should have written heat exchanger effectiveness -- efficiency was a
> poor choice of word and I have been chastised. I am primarily
> interested in reheat time with a hot water priority system.
Yeah don't worry, we knew what you meant... don't mind harry.
> <useful and interesting response clipped>
>
>>> I cannot find any manufacturer documentation to calculate the effect
>>> of hot water cylinder heat exchanger efficiency on reheat time. Is it
>>> significant in the case of a part L compliant hot water cylinder? Is
>>
>> Many cylinders will state the transfer rate of the indirect coil - so
>> you can work out what you need from that.
>
> I find it difficult to find manufacturers information. For example,
> Range <
www.range-cylinders.co.uk/pdfs/sales/copper.pdf> quote reheat
> times of 25mins for Hercal cylinders, 20mins for Supercal cylinders
> and 15mins for Ultracal cylinders. I am suspicious about these
> figures because they are specified with 82C flow temperature at 15
> litres/min (18 for Ultracal).
>
> This is unrealistic -- a small (18Kw) boiler will produce a
> temperature rise of about 17C at 15 litres/min between return and
> flow. Hence the flow temperature will start low (10+17 = 27C) and
> slowly increase.
That assumes that the cylinder HE will extract all the heat per pass,
which it won't - especially at such a low differential. (in fact if the
cylinder is partly hot, you may even find the return temp to the boiler
is warmer than the flow for a short while as the cylinder gives up heat
to the primary water).
After a few trips through the boiler, you will be up to the expected
flow temp.
Some of the cylinder specs (its worth downloading the installation
manual with the technical stuff in it rather than just using the sales
brochures) will have proper graphs of power inputs vs reheat time for
one or more flow temps. Generally these are produced from test measurements.
> The brochure smacks too much of Hi-Fi amplifier makers giving peak
> music power output (PMPO) rather than continuous sine wave power into
> a resistive load at onset of clipping.
The normal element of salesmanship is that many of the figures will be
quoted for flow temps of 80 degrees - which are far less commonly used
for modern boilers.
> When it gets nearer to spring and time to do the work I will try
> contacting the technical departments of one or two copper cylinder
> manufacturers to see if they can help.
>
>>> Could I leave the old cylinder (which uses
>>> gravity circulation) unchanged except for conversion to fully pumped
>>> primary?
>>
>> You could obviously keep the old one, but it won't be well suited to a
>> DHW priority setup, and the boiler / weather compensation won't be
>> suited to any form of paralleled operation of the cylinder and the heating.
>>
>> Having said that, depending on your DHW demands (and the size of
>> cylinder you spec) you may find that a full reheat early in the morning
>> before the CH kicks in, then a couple of refreshes during the day are
>> adequate anyway, and they can be scheduled during heating setback periods.
>
> I will probably do the work in stages -- get a gas fitter in to change
> the boiler, then DIY the hot water cylinder change. I can see what
> the cylinder reheat time is like during the summer, and change it if
> necessary before the next heating season.
It its an older "normal" gravity cylinder, then obviously it will still
work, although the reheat times will probably be two or three times what
you would expect with a modern one with a high power HE.
I used to find my old setup (cast iron lump boiler running 80 degree
flow, through a normal 900 x 450 indirect copper cylinder (max coil
transfer rate about 5kW) would take over an hour for a full reheat.
There was not much point running just the cylinder on its own since it
could not consume the 20+ kW the boiler could produce. The new setup
with a cylinder of twice the capacity, is very much quicker, simply
because it can consume the full output of the boiler for most of the
reheat.
I did contemplate doing the boiler swap and cylinder etc separately, but
decided it was much easier to get all the changes (i.e. boiler, weather
comp / controls, conversion to unvented, new cylinder, radiator
juggling, extra TMVs etc) done at once to save going through all the
hassle more than once.