On 22/04/2012 13:51, BartC wrote:
> Is there a problem with the electrical isolator switch for a
> wall-mounted combi boiler, being placed on the wall beneath the boiler,
> rather than to one side? It's been in the same place for decades.
Its not ideal (e.g. if the boiler leaks), but not explicitly forbidden.
> I've got a guy coming around who suggested it was against regulations
> and needs to be moved.
>
> He also said the lead pipe coming out of the gas meter was now illegal,
From BS6891 - 2005:
"8.3.3 Connecting lead composition pipes
When lead composition pipes are encountered and any connection joint has
to be made, then only a soldered cup joint onto copper pipe or a
suitable brass union fitting shall be made. Compression fittings
designed for jointing water weight lead pipework shall not be used.
COMMENTARY AND RECOMMENDATIONS ON 8.3.3
It is essential that care be taken when soldering a joint onto lead
composition pipework as blow lamps might provide too much heat at the
joint. Lead solder should be used for this purpose. It is essential that
joints be mechanically strong and gas tight."
So no mention of lead being removed...
The GSIR, prevents installation of new lead pipework however. See 5 (2)(a)
http://www.legislation.gov.uk/uksi/1998/2451/regulation/5/made
> and wanted to redo all the pipework, instead of just upgrading part of
> it. In fact, the pipe was copper when I cleaned off some of the tarnish.
> But would that lead pipe have needed to be upgraded? I got the feeling
> he was just making some of this stuff up.
Can you smell that? not gas, not horse, not donkey, must be bull!
--
Cheers,
John.
/=================================================================\