On 16/11/2022 10:29, AnthonyL wrote:
> Baxi 105 HE Combi. Recently installed a Drayton Wiser thermostat
> which is set to come on at 0630 to 0830 and call for a temperature of
> 19.5C in the lounge.
>
> It started off at the right time with a room temperature of just below
> 17C and nearly reached 18C by 0830.
>
> What I don't understand is the the burner would cycle on and off. Why
> isn't it on all the time till the temperature is reached?
It sounds as if there is insufficient load at that flow temperature.
The load will be a function of the total radiator area, and the
difference between the flow temp and the average house room temp.
If the boiler is operating at minimum power, and the flow temp exceeds
the flow temp you have set, then it will be forced to cycle since that
is the only way it can reduce its output to less than its minimum output
when firing.
This probably indicates that your radiators are undersized for that
combination of flow temp, and room temp, and/or the boiler is oversized.
If you increase the flow temp limit a bit, then the rads will be hotter
and also able to dissipate heat faster.
> The boiler output temperature is set for 50C. It is low as I
> understand from here that boiler efficiency increases with lower
> return temperatures.
It does - but also lower flow temperatures will result in lower rates of
heat movement (i.e. power) into the house. So if the total rad load is
on 5.5kW at 50 deg into a house at 17 deg, and the boiler output at
maximum "turn down" rate (i.e. modulated as low as it can go [1]) is
11kW, then it will need to cycle at a 50% duty rate to achieve an
average power output of 5.5kW.
> It may be too low to achieve the desired room temperature but then I
> would expect the burners to be on all the time.
Only *if* it can dump all the heat it is producing.
[1] The Baxi 105HE is very powerful boiler, with a heat output to the CH
of between ~11 to 31 kW. That *minimum* output power is very high (many
houses would be ok with a maximum output of that much!)
How many rads / rooms is it heating?
If it is less than 30, then I would suggest doing some heat loss calcs:
http://wiki.diyfaq.org.uk/index.php/Heat_loss
(and/or you could measure all the rads and go and lookup the typical
output power based on the size and delta T - ideally the total output of
all of them added together needs to be near the upper end of the
boiler's max power)
Minor rant: heating installers used to do proper heat loss calcs to work
out the required boiler size - since going too large meant lots of
cycling and inefficiency, less comfort for the owners since you got
larger temperature fluctuations, and not to mention the excess wear and
tear on the system resulting in lower reliability and shorter life
expectancy of the kit.
Then boilers got all clever and gained the ability to modulate their
output - at which point it seems that many installers decided - there
was no need to bother sizing it "correctly" any more, just leave it to
the modulation to match the demand. Alas that only works if the typical
heat demand falls into the output range that the boiler can actually
manage.
--