My brother has been told by a plumber he cannot have a power flush on his
central heating system as it uses 8mm microbore.

Is that true?

Adam


Andy Hall

unread,
May 29, 2006, 12:38:59 PM5/29/06
to
On Mon, 29 May 2006 16:35:44 +0100, ARWadsworth wrote
(in article <kxEeg.77623$wl.2...@text.news.blueyonder.co.uk>):

Power flushing machines that I've seen connect in place of the pump and work
by circulating a chemical solution through the radiators one at a time - i.e.
the operator is supposed to go round and close all radiator valves and then
open at one radiator at a time. This is meant to flush through crud in the
radiators and it gets filtered at the power flushing machine or to the drain

One can figure out that if the radiators are badly silted up, that this could
be difficult through 8mm tube even though the lengths from the manifold are
typically only a few mm.

I suspect that the plumber is saving himself some grief in case the job is
unsuccessful or that it takes him longer than he'd like to do it.


I have an 8mm system which has been well looked after from the outset.

The approach that I took when exchanging boilers and switching to a sealed
system was to do the sealed system conversion first - this provided a means
to fill and flush the system from the mains rather than the roof tank.

I drained the system and then starting closest to the boiler, I visited each
radiator in turn and removed it. Care is needed because sludge is an
indellible dye. I covered the floor with plastic sheet and old towels and
used a cat litter tray under each valve. The radiator valve unions can be
undone. Fit a small plastic bag on each tail with a rubber band and take
radiator outside. Flush through with a pressure washer. At the radiator
turn off the valves and turn on the mains water at the filling loop.
You can then flush any crud in the pipes out. `Since the pipes are only
8mm, there is not going to be a lot to come out and it is not being pushed
around the pipes either.

I repeated this for each radiator and then refitted everything and added a
chemical flushing agent. The system was run hot for a few days and then
flushed to drain with fresh water. Finally, corrosion inhibitor was added.

The whole job can be done easily in a morning.


Ed Sirett

unread,
May 29, 2006, 2:10:39 PM5/29/06
to
On Mon, 29 May 2006 15:35:44 +0000, ARWadsworth wrote:

> My brother has been told by a plumber he cannot have a power flush on his
> central heating system as it uses 8mm microbore.
>

If a system with micro-bore pipe ever gets to be in need of a power flush
it is truly beyond any hope of redemption.

Frankly the idea of disturbing what little dirt there may be in such a
system out of the rads into the pipes looks like madness. besides which
the power flush flow rate in each radiator will be fairly small due to the
resistance of the 8mm pipe.

A flushing out of individual removed radiators (with a pressure washer if
you must) is all that should be done.

--
Ed Sirett - Property maintainer and registered gas fitter.
The FAQ for uk.diy is at http://www.diyfaq.org.uk
Gas fitting FAQ http://www.makewrite.demon.co.uk/GasFitting.html
Sealed CH FAQ http://www.makewrite.demon.co.uk/SealedCH.html
Choosing a Boiler FAQ http://www.makewrite.demon.co.uk/BoilerChoice.html
Gas Fitting Standards Docs here: http://www.makewrite.demon.co.uk/GasFittingStandards

John

unread,
May 29, 2006, 2:23:02 PM5/29/06
to

"Ed Sirett" <e...@makewrite.demon.co.uk> wrote in message
news:pan.2006.05.29....@makewrite.demon.co.uk...

I also have an 8mm system with the TwinFast Yorkshire valves (flow and
return coaxial at one end). I always remove radiators for decorating and
have never found much sludge. My main worry is sediment settling in
horizontal (or sagging) lengths of pipe. I am surprised that Ed feels that
flushing would not help. I wouldn't mind trying it - I imagine a pump that
sends shock waves through the water would be effective.
Incidentally - I have not found any faults with the twin valve arrangement
and can't understand why it became obsolete. It can be a very neat
installation and much easier to remove radiators. Mine have a nylon tube to
send the flow to the far end. I understand some people used metal and
suffered from corrosion. Was the problem a lack of understanding?
I think my house was the last in the road to use this system (1988) as an
identical house completed a few weeks later by the same plumber had
conventional valves on each end. Does anyone know when my type of valve fell
from favour?


John

unread,
May 29, 2006, 2:26:02 PM5/29/06
to

>
> I also have an 8mm system with the TwinFast Yorkshire valves (flow and
> return coaxial at one end). I always remove radiators for decorating and
> have never found much sludge. My main worry is sediment settling in
> horizontal (or sagging) lengths of pipe. I am surprised that Ed feels that
> flushing would not help. I wouldn't mind trying it - I imagine a pump that
> sends shock waves through the water would be effective.
> Incidentally - I have not found any faults with the twin valve arrangement
> and can't understand why it became obsolete. It can be a very neat
> installation and much easier to remove radiators. Mine have a nylon tube
> to send the flow to the far end. I understand some people used metal and
> suffered from corrosion. Was the problem a lack of understanding?
> I think my house was the last in the road to use this system (1988) as an
> identical house completed a few weeks later by the same plumber had
> conventional valves on each end. Does anyone know when my type of valve
> fell from favour?
>
>
> Sorry - I meant MAXITWIN valve:
http://tinyurl.com/asr5x


Cicero

unread,
May 29, 2006, 4:29:21 PM5/29/06
to

"John" <john.p...@ntlworld.com> wrote in message
news:a_Geg.3958$002....@newsfe2-gui.ntli.net...
======================
Twin entry valves had a reputation for being difficult to get the
circulation going. I don't think it was a serious problem but it certainly
could be difficult at times. There was some debate about long the internal
pipe should be and whether it should be plastic or copper. I used copper
about 2/3rds the length of the radiator (as recommended) and always got a
good circulation going eventually.

As far as flushing is concerned I can only guess that it's less necessary
with 8mm because the normal pumped flow has a more powerful scouring action
than is the case with 15mm or greater. I've never had any blocked pipes,
possibly because I don't have a Summer shutdown. I think our weather is too
unpredictable to have a fixed Summer period when heating isn't necessary.

Cic.


Ed Sirett

unread,
May 29, 2006, 5:15:04 PM5/29/06
to

Mainly because the older units had copper internals which corroded and
broke as they were in contact with the iron. This caused only the corner
to get hot.

They are not as widely available and whilst a thermostatic version is
probably available the requirement to add TRVs to most radiators make
their replacement nigh on inevitable.

John

unread,
May 29, 2006, 5:54:39 PM5/29/06
to
>
> They are not as widely available and whilst a thermostatic version is
> probably available the requirement to add TRVs to most radiators make
> their replacement nigh on inevitable.
>
>
> --
> Ed Sirett - Property maintainer and registered gas fitter.
> The FAQ for uk.diy is at http://www.diyfaq.org.uk
> Gas fitting FAQ http://www.makewrite.demon.co.uk/GasFitting.html
> Sealed CH FAQ http://www.makewrite.demon.co.uk/SealedCH.html
> Choosing a Boiler FAQ http://www.makewrite.demon.co.uk/BoilerChoice.html
> Gas Fitting Standards Docs here:
> http://www.makewrite.demon.co.uk/GasFittingStandards
>

Good point - hadn't thought about the infernal requirement to fit
thermostatic valves - but how a sensor only inches from the heat source can
work properly is beyond me.


ARWadsworth

unread,
May 30, 2006, 1:28:13 PM5/30/06
to

"Andy Hall" <an...@hall.nospam> wrote in message
news:0001HW.C0A0E233...@10.0.0.1...

> On Mon, 29 May 2006 16:35:44 +0100, ARWadsworth wrote
> (in article <kxEeg.77623$wl.2...@text.news.blueyonder.co.uk>):
>
>> My brother has been told by a plumber he cannot have a power flush on his
>> central heating system as it uses 8mm microbore.
>>
>> Is that true?
>>
>> Adam
>>
>>
>
> Power flushing machines that I've seen connect in place of the pump and
> work
> by circulating a chemical solution through the radiators one at a time -
> i.e.
> the operator is supposed to go round and close all radiator valves and
> then
> open at one radiator at a time. This is meant to flush through crud in
> the
> radiators and it gets filtered at the power flushing machine or to the
> drain
>
> One can figure out that if the radiators are badly silted up, that this
> could
> be difficult through 8mm tube even though the lengths from the manifold
> are
> typically only a few mm.
>
> I suspect that the plumber is saving himself some grief in case the job is
> unsuccessful or that it takes him longer than he'd like to do it.

I hope not, he wants me to rewire his house!

> I have an 8mm system which has been well looked after from the outset.

Unfortunatley, this system is 15 years old and has been neglected before my
brother bought the house

> The approach that I took when exchanging boilers and switching to a sealed
> system was to do the sealed system conversion first

Can I do that without changing the hot water cylinder?

- this provided a means
> to fill and flush the system from the mains rather than the roof tank.
>
> I drained the system and then starting closest to the boiler, I visited
> each
> radiator in turn and removed it. Care is needed because sludge is an
> indellible dye. I covered the floor with plastic sheet and old towels
> and
> used a cat litter tray under each valve. The radiator valve unions can
> be
> undone. Fit a small plastic bag on each tail with a rubber band and take
> radiator outside. Flush through with a pressure washer. At the
> radiator
> turn off the valves and turn on the mains water at the filling loop.
> You can then flush any crud in the pipes out. `Since the pipes are only
> 8mm, there is not going to be a lot to come out and it is not being pushed
> around the pipes either.

I removed all the rads and flushed them last year when he moved in. I also
changed the pump which was noisy and added inhibitor. The main problem is
now of overpumping which as I understand will reduce the effectiveness of
the inhibitior and the sound of water falling down the vent pipe when the
pump shuts off. I removed a rad over the weekend and although there was
plenty of black water there was not the sludge that was present a year ago.


> I repeated this for each radiator and then refitted everything and added a
> chemical flushing agent. The system was run hot for a few days and then
> flushed to drain with fresh water. Finally, corrosion inhibitor was
> added.
>


I think I may reflush the rads and this time use a cleanser.

Adam


ARWadsworth

unread,
May 30, 2006, 1:30:07 PM5/30/06
to

"Ed Sirett" <e...@makewrite.demon.co.uk> wrote in message
news:pan.2006.05.29....@makewrite.demon.co.uk...
> On Mon, 29 May 2006 15:35:44 +0000, ARWadsworth wrote:
>
>> My brother has been told by a plumber he cannot have a power flush on his
>> central heating system as it uses 8mm microbore.
>>
> If a system with micro-bore pipe ever gets to be in need of a power flush
> it is truly beyond any hope of redemption.

All of it or just the rads? I am prepared to swap them if needs be.


> Frankly the idea of disturbing what little dirt there may be in such a
> system out of the rads into the pipes looks like madness. besides which
> the power flush flow rate in each radiator will be fairly small due to the
> resistance of the 8mm pipe.
>
> A flushing out of individual removed radiators (with a pressure washer if
> you must) is all that should be done.
>

Cheers Ed, see my reply to Andy

Adam


Ed Sirett

unread,
May 30, 2006, 2:45:06 PM5/30/06
to
On Mon, 29 May 2006 21:54:39 +0000, John wrote:

>>
>> They are not as widely available and whilst a thermostatic version is
>> probably available the requirement to add TRVs to most radiators make
>> their replacement nigh on inevitable.
>>

>

> Good point - hadn't thought about the infernal requirement to fit
> thermostatic valves - but how a sensor only inches from the heat source can
> work properly is beyond me.

Little heat is trasnferred by radiation especially from the lower part of
the rad.
The convection draughts keep the TRV more in tune with the room that the
radiator.
The TRV does not have to be at the same temp as the room but merely has to
sense and react to changes in the room temp.

Ed Sirett

unread,
May 30, 2006, 2:47:06 PM5/30/06
to
On Tue, 30 May 2006 17:30:07 +0000, ARWadsworth wrote:

>
> "Ed Sirett" <e...@makewrite.demon.co.uk> wrote in message
> news:pan.2006.05.29....@makewrite.demon.co.uk...
>> On Mon, 29 May 2006 15:35:44 +0000, ARWadsworth wrote:
>>
>>> My brother has been told by a plumber he cannot have a power flush on his
>>> central heating system as it uses 8mm microbore.
>>>
>> If a system with micro-bore pipe ever gets to be in need of a power flush
>> it is truly beyond any hope of redemption.
>
> All of it or just the rads? I am prepared to swap them if needs be.

15mm can and do block on very badly sludged systems. It won't take so much
to block an 8mm pipe. I have no idea wether an 8mm pipe is unblockable by
pressure and chemicals alone - but I'd reckon against it.

ARWadsworth

unread,
May 30, 2006, 3:02:30 PM5/30/06
to

"Ed Sirett" <e...@makewrite.demon.co.uk> wrote in message
news:pan.2006.05.30....@makewrite.demon.co.uk...

> On Tue, 30 May 2006 17:30:07 +0000, ARWadsworth wrote:
>
>>
>> "Ed Sirett" <e...@makewrite.demon.co.uk> wrote in message
>> news:pan.2006.05.29....@makewrite.demon.co.uk...
>>> On Mon, 29 May 2006 15:35:44 +0000, ARWadsworth wrote:
>>>
>>>> My brother has been told by a plumber he cannot have a power flush on
>>>> his
>>>> central heating system as it uses 8mm microbore.
>>>>
>>> If a system with micro-bore pipe ever gets to be in need of a power
>>> flush
>>> it is truly beyond any hope of redemption.
>>
>> All of it or just the rads? I am prepared to swap them if needs be.
>
> 15mm can and do block on very badly sludged systems. It won't take so much
> to block an 8mm pipe. I have no idea wether an 8mm pipe is unblockable by
> pressure and chemicals alone - but I'd reckon against it.

S**t. Any more chance of being successfull in a soft water area. I am now
only hoping for miracles.

Adam


Chris Bacon

unread,
May 30, 2006, 3:22:31 PM5/30/06
to
ARWadsworth wrote:
> "Ed Sirett" wrote in message
>>15mm can and do block on very badly sludged systems. It won't take so much
>>to block an 8mm pipe. I have no idea wether an 8mm pipe is unblockable by
>>pressure and chemicals alone - but I'd reckon against it.
>
> S**t. Any more chance of being successfull in a soft water area. I am now
> only hoping for miracles.

Soft or hard water probably won't affect scale in CH systems...
if you flush the radiators through, then I should think that the
reduction in total sludge in the system, combined with the fact
that small bore pipes have a high flow rate, and radiators are
nice "settlement tanks", might help.

Andy Hall

unread,
May 30, 2006, 5:49:19 PM5/30/06
to
On Tue, 30 May 2006 18:28:13 +0100, ARWadsworth wrote
(in article <Ng%eg.78173$wl.1...@text.news.blueyonder.co.uk>):

It should be possible in principle. However, if it's a hard water area the
coil might be scaled up. You would need to take out the immersion heater
and look inside to check that. If it is, then you could descale with
chemicals and replace the immersion heater. However, this may not be the
best way to invest in the system. It might be better to write off the
cylinder and start with a new one,...


That's reasonably easy to do and would give an idea of the general state of
the system as well.

>
> Adam
>
>


Stuart

unread,
Jun 3, 2006, 10:06:03 AM6/3/06
to
On Mon, 29 May 2006 17:38:59 +0100, Andy Hall <an...@hall.nospam> wrote:

>On Mon, 29 May 2006 16:35:44 +0100, ARWadsworth wrote
>(in article <kxEeg.77623$wl.2...@text.news.blueyonder.co.uk>):
>
>> My brother has been told by a plumber he cannot have a power flush on his
>> central heating system as it uses 8mm microbore.
>>
>> Is that true?
>>
>> Adam
>>
>>
>
>Power flushing machines that I've seen connect in place of the pump and work
>by circulating a chemical solution through the radiators one at a time - i.e.
>the operator is supposed to go round and close all radiator valves and then
>open at one radiator at a time. This is meant to flush through crud in the
>radiators and it gets filtered at the power flushing machine or to the drain
>
>One can figure out that if the radiators are badly silted up, that this could
>be difficult through 8mm tube even though the lengths from the manifold are
>typically
>only a few mm.


" a few mm" ?????


Andy Hall

unread,
Jun 3, 2006, 11:03:37 AM6/3/06
to
On Sat, 3 Jun 2006 15:06:03 +0100, Stuart wrote
(in article <dp53825tmnb3ja292...@4ax.com>):

Well, yes. Maybe a couple of thousand for example.....

What's that between friends.?


powerflu...@gmail.com

unread,
Jul 8, 2012, 9:02:37 AM7/8/12
to
--------------------------

Power flushing is not very effective on microbore because the drop in flow is big with small pipes. Try a powder flush as it has been developed especially for microbore systems and use much stronger machines.

ARWadsworth

unread,
Jul 8, 2012, 9:11:33 AM7/8/12
to
Well I will bear that advice with a pinch of salt. After all you are
replying to a post I made in 2006. We swapped the pipework to 15mm a few
years later.

Any ideas of how to clear a turd from the uk.d-i-y newsgroup in the year
2012?


--
Adam


Gazz

unread,
Jul 8, 2012, 12:52:29 PM7/8/12
to
>>
>> Power flushing is not very effective on microbore because the drop in
>> flow is big with small pipes. Try a powder flush as it has been
>> developed especially for microbore systems and use much stronger
>> machines.
>
> Well I will bear that advice with a pinch of salt. After all you are
> replying to a post I made in 2006. We swapped the pipework to 15mm a few
> years later.
>
> Any ideas of how to clear a turd from the uk.d-i-y newsgroup in the year
> 2012?

fit an enema fitting to the end of the power flush hose...