1. Turn off cold water feed.
2. Open hot tap and let as much water drain out as the air pressure thingy
inside the Megaflo expels.
3. Connect hose to drain and drain it.
Question: The Megaflo will need to fill with air when the water drains out.
Where does the air come from? Is there an automatic valve somewhere, or do I
need to open something? Or does it get sucked in through the open hot water
tap?
Filling:
1. Close drain valve, and open cold water feed.
2. Anything else???
Do these things come with an instruction book? If so, I have no idea where
ours is, assuming that the builders ever left it.
Thanks for your help.
Open hot tap and leave open until all air is expelled.
Ah, many thanks! I eventually tracked down the installation manual, which
says this (just in case somebody else needs to know at some time in the
future):
8.4 DRAINING THE MEGAFLO UNIT
Switch off the electrical supply to the immersion heater(s) and shut down
the boiler on
indirect units. Turn off the mains water supply to the Megaflo unit. Attach
a hosepipe to the drain
cock having sufficient length to take water to a suitable discharge point
below the level of the unit, at
least one metre below the unit is recommended. Open hot water tap nearest to
the Megaflo to relieve
the system pressure. Open drain cock. If water fails to drain from the
Megaflo vent the unit by
manually opening the Temperature/Pressure Relief Valve.
8.5 DESCALING IMMERSION HEATER(S)
Open the cover(s) to the immersion heater housing(s) and disconnect wiring
from immersion heater(s).
Remove the thermostat by carefully pulling outwards from the immersion
heater. Unscrew immersion
heater backnut(s) and remove immersion heater from the unit. A key spanner
is supplied with the
Megaflo unit for easy removal/tightening of the immersion heater(s). Over
time the immersion heater
gasket may become stuck to the mating surface. To break the seal insert a
round bladed screwdriver into
one of the pockets on the immersion heater and gently lever up and down.
Carefully remove any scale from the surface of the element(s). DO NOT use a
sharp implement as
damage to the element surface could be caused. Ensure sealing surfaces are
clean and seals are
undamaged, if in doubt fit a new gasket.
Replace immersion heater(s) ensuring the lower (right angled) element hangs
vertically downwards
towards the base of the unit. It may be helpful to support the immersion
heater using a round bladed
screwdriver inserted into one of the thermostat pockets whilst the backnut
is tightened. Replace the
thermostat(s) by carefully plugging the two male spade terminations on the
underside of the thermostat
head into the corresponding terminations on the element.
Rewire the immersion heater(s) in accordance with Diagram 8. Close and
secure terminal cover(s).
8.6 REFILLING SYSTEM
DO NOT switch on the immersion heater(s) or boiler until the system has been
completely refilled.
Close the drain tap. With hot tap open, turn on mains water supply. When
water flows from the hot
tap allow to flow for a short while to purge air and to flush through any
disturbed particles. Close hot
tap and then open successive hot taps in system to purge any air. The
electrical supply can now be
switched on.
That's right. The cold feed shutoff and pressure reducing valve are
usually located close by. Shut it. Open a hot tap untill the expansion
volume has exhausted, and the water stops flowing. This can take a
surprisingly long time! Time it to co-incide with a bath, so as not to waste
the hot water! Then, there ought to be a drain cock plumbed in just at the
cold feed, at the bottom of the cylinder ( colour-coded blue ring ).
Attach a hose, and drain down. Leaving the hot tap open will speed this up,
as air can enter this way. Otherwise, hold open the Temp / Pressure relief
valve ( directly above the cold inlet, grey colour-coded ring, cleary marked
as Temp /Pressure relief ) untill the gurgling stops and the cylinder is
empty.
> Question: The Megaflo will need to fill with air when the water drains
> out. Where does the air come from? Is there an automatic valve somewhere,
> or do I need to open something? Or does it get sucked in through the open
> hot water tap?
It will naturally fill with air during draining-down, either via the hot
tap, the manually opened T/P relief, or by air bubbling back up the drain
hose. Don't worry about it.
> Filling:
> 1. Close drain valve, and open cold water feed.
> 2. Anything else???
No. This will re-generate the air volume too, which is something you need
to do occasionally ( anually here ) anyway, as per the instructions on the
front.
> Do these things come with an instruction book? If so, I have no idea where
> ours is, assuming that the builders ever left it.
Yes.
There's an installation manual in pdf format here:
http://www.heatraesadia.com/hs/heatraes.nsf
I don't thhink there's a user manual, other than the instructions for
re-generating the air volume which is on a label on the cylinder. They
should have left a Benchmark Log Book ( service history, basically ) with
the installation.
> Thanks for your help.
>
--
Ron
open cold tap elsewhere if the cylinder is high. That will drain it
pretty completely.
No, it won't.
The hot draw-off is at the top.
The draw-off pipe extends some short distance down into the cylinder, to
allow for the expansinon volume.
Regardless of how low the tap is, it will only drain as far as the end of
the draw-off pipe, or untill the pressure in the expansion volume is
exhausted. This is not low enough to replace the immersion elements, which
are mounted on the side of the megaflo cylinder.
--
Ron