On 17/04/2017 19:43, Tricky Dicky wrote:
> I have just installed Hive and after some messing around managed to get everything talking to each other. The only problem is the boiler will not fire, the receiver is showing all green lights showing it is working but the boiler refuses to fire except when there is DHW demand.
>
> On the boiler - a Worcester a Junior 28i Combi - there are only three terminals Ls - live supply, Ns - Neutral supply and Lr - or switched live from the thermostat. On the Hive receiver I have L& N connected to terminals N& L respectively and the switched live connected to terminal 3 - Heating On (NO). Terminals 1&2 must be right as the status lights would not be on so that leaves the switched live which could be wrong. The remaining terminals in the receiver are 1 - common and 2 - Heating off (NC)
>
> Have I got the wiring wrong? Will I do any damage swapping connections round, the guys on the Hive live chat have not been any use referring me back to the wiring diagrams.
>
> Richard
From your description, I'm assume that you've got the single channel
(heating only) rather than dual channel (heating + hot water) receiver.
The single channel receiver works in a different way from the dual
channel jobbie.
The L&N are purely to power the receiver. The switch is what is usually
called "voltage free" and can be used to switch anything you like -
including low voltage stuff. It's a changeover switch, in which COM is
connected to NC in the off position and to NO when on. So the boiler
won't see anything from NO unless you supply power to COM.
So all you need to do is provide a link from L to COM, and all will be well.
--
Cheers,
Roger