>a) Is a laundry chute legal in the UK for residential houses?
>b) Is my plan above sufficient to satisfy all the building and fire
>regs?
>c) Do I have to inform the council that I'm putting one in?
In my twenty-mumble years in Building Control, I've never been asked
about a laundry chute in a house. But thinking about it;
As it will involve a material alteration to the internal fire spread
of the building, and may involve a structural opening in a floor
(unless it fits between a pair of joists), then it would require a
Building Regulations application.
It can be done, and if it's in a dwellinghouse rather than a building
containing flats, then it shouldn't require more than enclosing the
chute in fire resisting construction to the same level as the
remainder of the building. So if the house's top floor is no more than
7.5m above ground level, then 30 minutes fire resistance would be
enough. If the chute opened onto a stair enclosure at any level, then
the doors or hatches may need to be fire resisting to 20 minutes.
--