I have a 30(?) year old Glow-Worm Space Saver 38 boiler which, for the
last 10 months (when I moved in) has been totally fine. With all the
strong wind recently I've noticed that the pilot light has gone out a
lot but I've always been able to relight it and carry on as normal.
Last Thursday I got home from work to notice that it had gone out
again. I tried to relight it and it wouldn't. When I eventually did
and turned the gas flow upto full (On) the whole lot just went out
after about 10 seconds. I thought it was the wind again so I tried a
couple more times without success and left it for the evening.
Over the weekend the wind was a lot more settled so I tried it again
but still had issues. It doesn't seem to like a sudden burst of gas
(i.e. turning it upto full quickly) - turning it from pilot to full
will almost guarantee it going out. The only was I can get it to light
is the following:
1. Hold down the gas flow dial and light the pilot.
2. After about 30 seconds I SLOWLY release the gas flow dial and pilot
light seems to stay lit.
3. I turn the gas flow upto about a third, just to get the main burner
to kick in.
4. Leave it for five minutes (which seems to warm it up and make it
stable) and then turn it upto about two thirds.
5. Leave it for another five minutes and then turn it upto full (On).
This method seems to work but after I turn the heating off the boiler
obviously cools down and then the pilot light will eventually go out
(within 20-30 mins). This means I cannot set the heating to come on
with the timer.
It's almost like the boiler doesn't like being cool? When hot, the
flame seems stable even when cutting out between main burner bursts.
I do intend on getting a gas man out asap to take a look at it, but I
just wanted a "second opinion" from you guys just so I know what to
expect to be told. Could it be the thermocouple, or something more
drastic? (the thermocouple also seems to lead up behind the boiler
making it hard to change - is it a boiler off-the-wall jobby?)
Cheers guys,
Paul.
Might be the thermocouple or that the pilot jet is partially
blocked with dirt because the boiler needs servicing. When
was it last serviced?
--
Andrew Gabriel
[email address is not usable -- followup in the newsgroup]
I had a similar problem. I suspected that it might be a broken sight
glass, leading to a through draught through the boiler. Managed to
secure a replacement for the very old Ideal Standard boiler (later IS
boilers have similar sight glasses) and the boiler has not gone out
since.
Maris
For whatever reason, the gas valve is failing to respond to a signal from
the thermocouple that the pilot light is alive and well. This can be due to
any of 3 reasons:
* Duff gas valve
* Duff thermocouple
* Pilot not heating the thermocouple properly
This last one can be due to the pilot not being strong enough, or pointing
in the wrong direction - maybe because of a bit of crud across the jet. The
fact that it goes out with the slightest gust of wind suggests that you need
to turn the wick up a bit. Is there a separate little governor which
controls the pressure to the pilot - and hence the height of the flame? If
so, tweak it up a bit, and make sure that the flame is directed straight at
the thermocouple. If that doesn't work, replace the thermocouple. If *that*
doesn't work, it could be that the gas valve is duff - but that's less
likely than the other things.
--
Cheers,
Roger
______
Email address maintained for newsgroup use only, and not regularly
monitored.. Messages sent to it may not be read for several weeks.
PLEASE REPLY TO NEWSGROUP!
Cheers guys. After reading on the internet it did seem to be to be the
thermocouple as the most likely cause. I get the impression that they
are fairly straightforward to change/fit. When I look at my boiler
controls I have the thermostat on the left, the ignition next to it,
then the gas valve. Just to the right of the gas valve is what I think
is the thermocouple (piccie from internet->
http://www.boilerpart.gbr.cc/images/cust/boilerpart.gbr.cc/GLOK9049l.jpg
- just above the right contact in the blue plastic part) - something
that looks screwed into gas valve housing - with a copper pipe coming
out of it, going under the boiler and then goes into the back of the
boiler. Am I correct? If so, how do I disconnect/connect the back part
as there doesn't look to be enough room! (couple of centimetres).
Is it a DIY job - I am a competent DIYer but I won't mess with what
experts and professionals get trained to do!
Cheers,
Paul.
EEsh I remember having to go through that crap. And forever having to change
the thermocouples!