Its not a departure at all - its one of the standard circuits listed in
the On Site Guide:
http://wiki.diyfaq.org.uk/images/2/2b/Standard-Lighting-Circuits.jpg
(you will note there is also a standard 16A lighting circuit - although
that is very unlikely to be used in a domestic situation)
> All my knowledge comes from when, with the assistance of a retired
> electrician (a family relative), I totally rewired this 3 story 6 bed
> Victorian semi-detached house back around 1983.
>
> This is where I learned about the CU fusing regulations with regard
> to ring mains, lighting circuits, high power spur feeds to things like
> cooker points and power showers as well as to the requirement to
> provide a dedicated 15A fused feed to the immersion heater (classified
> as a fixed connected load requiringa high temp flex connection between
> the heater element terminals and the switched terminal box on the end
> of said dedicated feed).
Sounds like a very useful learning experience. Keep in mind though that
for subtle details that was several issues of BS7671 ago, and stuff has
(and will continue to) evolve.
> Plus I also learned about the earth bonding
> requirements of all exposed metalwork (pipework, stainless steel sinks
> etc).
Alas in those days many professional electricians had very little clue
about equipotential bonding (even the term "earth bonding" is a misnomer
when you think about it - earthing and bonding are two different systems
designed to add protection in two different ways). Not aided much by the
15th edition regs that also over egged the requirements somewhat.
You may find this useful:
http://wiki.diyfaq.org.uk/index.php?title=Earthing_and_Bonding
The key requirement in situations where EQ bonding is used is to
establish if the metalwork in question is capable of bringing a
potential into the equipotential zone. If its not, then there is no
point in bonding it. Hence why things like sinks and bath do not require
bonding in spite of so many electricians believing they do.
> It isn't exactly rocket science for someone experienced with
> electronics kit and a well founded knowledge of electrical theory.
> Once you understand that the fundamental protection provided by the
> fuse links (MCBs) in a CU is essentially to protect the permanent
> cabling and fittings it's easy to see why 5A was chosen for lighting
> and up to 30A for ring mains with 45A protecting 4mm FT&E cabling to a
> cooker point and other similar heavy duty loads.
Many of these things are chosen for backward compatibility as much as
fundamental theory.
> A small 3 bed semi can manage with just a single ring main circuit
> and a single lighting circuit plus cooker point and immersion heater
> feeds so could be nicely served by a 4 fuse CU with a set of fuses
> comprising of 5A for the lighting, 15A for the immersion, 30A for the
> ring main and a 45A for the cooker point.
Depends on how you define "manage". It an installation that does not
provide adequate discrimination[1] in the event of a fault
[1] i.e. the requirement that the effect of a fault be localised to it.
Plunging an entire house into darkness due to a lamp failing and
tripping a MCB is not acceptable today. (it never really was, but the
implications of it had not really been considered at the time)
> In a bigger property, you'd be well advised to fit a 6 way CU so you
> can split the lighting across two circuits, each with their own 5A
> fuse rather than the ill advised use of a 10A fuse on a single circuit
I sense an anti 10A fuse agenda here ;-)
> (even when 1.5mm cabling is used - the ratings on the fittings are all
> based on the protection of a 5A fused supply). Obviously, the second
> extra fuse position will allow two seperate ring mains to be provided.
I think you will find that modern lighting accessories are fine on 10A
circuits (note that even the limitation on the "small" version of the
normal lamp holders was removed).
(and TBH a 6 way CU is woefully inadequate for many places these days)
> When we first moved into the current property, it didn't have a
> cooker point so I was able to wire up three seperate ring mains
> (ground floor, first floor and second floor mains socket supplies).
If doing it now, it would be quite common to do that, and also add an
extra ring circuit for the kitchen / utility room - since the modern
compliment of kitchen appliances can rapidly use all 7.2kW capacity of a
ring circuit.
> The basement was catered for by fitting 3 single outlet 13A sockets
> onto the CU backboard each fed off the 3 ring main circuits so that
> the freezer we kept in the basement could be readily powered from any
> one of the ring main circuits as an insurance against any protracted
> outage that might arise due to faults or planned changes in the ring
> main wiring.
Would it not have been simpler to provide a dedicated circuit for this
purpose? Then you would *know* its not going to be tripped regardless of
what happens elsewhere.
> The freezer no longer resides in the basement but the 'diversity' of
> this setup is still very handy although I have installed an extra twin
> outlet wall socket away from the CU, connected most likely to the 1st
> floor ring main circuit (but I'd have to take a gander at the fuse
> cover labelling to confirm this - but it seems the most logical choice
> of ring main so I'd be surprised if it were otherwise since the same
> logic would have dictated my original choice).
>
> When it came to replacing all the VIR cabling in conduit lighting
> wiring, we knew it had to be split across two lighting circuits. As it
> happened I bought a couple of 100m reels of 1.5mm FT&E for this job
> and used nearly all of it.
>
> The Mortgage company had held back £1000 of the loan on account of
> the state of the lighting circuit wiring but when I delved a little
> deeper into the state of the rest of the wiring, I discovered the
> house had two ring circuits and a mix of spur fed outlets randomly
> distributed about the property (one ring main fed half the ground
> floor sockets and half the first floor sockets and the other ring main
> fed all the 2nd floor sockets but with a length of heavy duty rubber
> sheathed appliance cord being used instead of the regulation FT&E.
Its not uncommon to find all sorts of strange stuff in existing
installations - especially if they are ageing and have been hacked about
a bit in the following years.
(I recall digging a 5A circular junction box out of the plaster above
the sink in the kitchen of a neighbour's property. (yes it was the screw
terminal type that is intended to remain accessible for maintenance))
> What had started out as just a lighting circuit 'rewire' developed
> into a complete rewiring of the whole house. The job was essentially
> an exercise in re-organising the randomly fed sockets into 3 distinct
> ring mains.
>
> Since the top floor was the only proper ring main in the whole house,
> I replaced the rubber sheathed flex with 2.5mm FT&E to bring it up to
> standard then dropped a very long mains extension down to the kitchen
> with another extension lead into the basement to power the freezer
> whilst I stripped out most of the 'ring main' wiring to the ground and
> first floor sockets, sorting out the recovered lengths of FT&E so I
> could rebuild the ring main circuits using shortest lengths first.
>
> This minimised the need to add extra cable to the point where I was
> able to beg the extra 20 or so metres from my dad thus reducing the
> cable costs to nil with only the new dual gang 13A sockets as the main
> parts cost.
>
> It was a lot of work to sort it out but I felt it just had to be done
> in the interest of safety (it's not good having sockets in the same
> room powered from different fuses in the CU). needless to say (after
> sorting out the earth bonding) I had no trouble getting the job
> certified and the extra grand released by the Mortgage company.
I would expect that as long as you fill in the test results correctly
they will be happy (they probably don't even look at the name of the
contractor on top of the page!)
> I suspect anyone trying to get their house wiring certified whilst
> they have a 10A fused lighting circuit in the mix will have a hard
> time trying to convince an inspector that it is within regs and
> standard wiring practice.
Your suspicion is this case is unfounded - or at least not for this
reason. Needless to say Part P has complicated the "certification"
process somewhat in subsequent years.
> With many house owners now using CFLs and LED lamps in place of most
> of the originally fitted 60 and 100 watt incandescent lamps, I think
> any such 10A lighting circuits could now be 'downgraded' to 5A fuse or
> 6A mcb protected circuits without any problems.
Quite possibly, although you would need to consider what you are
attempting to achieve, and also the unintended consequences of the change.
Keep in mind that when providing over current protection for any
circuit, there are two discrete issues that need to be addressed:
overload, and fault handling. (i.e. long term over current resulting
from applying more load than the circuit design current, and the very
short term effects from massive over current caused by someone nailing
through the cable etc). Traditionally these two functions are provided
by the same protective device at the origin of the circuit[2]. If you
are using one of the standard circuits, then both of these are allowed
for in the design; The protective device nominal rating is lower than
that of the "as installed" cable current carrying capacity[3], and
someone has already done the sums to make sure the cable won't melt
while carrying 1000A for the few ms necessary to open the MCB on its
magnetic trip).
So for example changing a "whole house" 10A lighting circuit to a
"normal" type B 6A MCB on the grounds that modern lamps no longer
require the current may be fine. But you are starting with a circuit
that was already adequately protected. As consequence of changing the
protective device, you have also reduced the fault current tolerance of
the MCB from 50A to 30A (type B MCBs need 5x nominal current to trip on
the "instant" part of their response curve)[4]. A result you may now
find is that when one of the few remaining incandescent lamps does fail,
its far more likely to trip the whole circuit. (and trips and falls in
the house kill orders of magnitude more people each year than are
electrocuted!) (note that this is easy enough to mitigate in this
particular example since you could use a type C MCBs instead)
[2] this does not always have to be the case - fault current protection
must be provided at the origin, while overload protection may be
delegated elsewhere or in some cases may not be required at all.
[3] Remember that the "clipped direct" current carrying capacity of even
1.0mm T&E is 16A
http://wiki.diyfaq.org.uk/index.php?title=Cables#Cable_Sizes
[4]
http://wiki.diyfaq.org.uk/index.php?title=File:Curve-MCBTypeB.png
> Other than 'special cases' I think anyone with a 10A fuse protected
> lighting circuit should downgrade to a 5A fuse for their own peace of
> mind just on safety grounds alone.
While that all sounds nice and warm and fuzzy, can you actually justify
it on technical merit?
> Using a 10A fuse, even in a larger
> domestic property is probably unnecessary with modern lamps these
> days.
Agreed in most cases... although keep in mind the increasing use of
ancillary loads on lighting circuits - e.g. extractor fans for forced
ventilation in kitchens, loos, bath/shower rooms etc, localised space
heating with "heater" lamps etc.