2.5mm swa current rating

1,097 views
Skip to first unread message

Andrew Mawson

unread,
May 14, 2013, 12:37:40 PM5/14/13
to
According to the TLC web site 2 core 2.5mm SWA is rated at 36 amps, and 3
core 2.5mm is rated at 31 amps. If I am using 3 core with the third core as
a cpc (connected to the wire armour ) can I reasonably use a 32 amp breaker
to feed it? The cable is buried.

(It is 30 meters long, fed off a 30mA rcd board, and feeds four 13a sockets
in the control cabinet for my front gate, with very minimal load (a wireless
hub, three cat5 cameras and the gate itself which is only 3 amps peak.
However it would be very convenient to use another socket on this circuit
for the occasional power tool, concrete mixer, 9" angle grinder etc to save
running extension leads, and I know my 9" grinder will trip a 20 amp breaker
on start up)

AWEM

Tim Watts

unread,
May 14, 2013, 1:09:34 PM5/14/13
to
I think for 30m you are going to get done by voltage drop requirements - I
suspect 6mm2 will be nearer the mark.

Also, be careful as XLPE cable is often quoted as "X-amps" on the assumption
of running at 90C. Most accessories it terminates in will only be rated for
70C - unless you are using metal boxes with appropriately rated connectors.

I assume you will have RCD protection at the supply end?

Would you like me to look up the numbers properly (or someone else might
have them in their head)?

Cheers

Tim

--
Tim Watts Personal Blog: http://squiddy.blog.dionic.net/

http://www.sensorly.com/ Crowd mapping of 2G/3G/4G mobile signal coverage

Reading this on the web? See:
http://wiki.diyfaq.org.uk/index.php?title=Usenet

Tim Watts

unread,
May 14, 2013, 1:11:38 PM5/14/13
to
Oh crap.

There are so many "30s" above I got blinded to the bit that said "20A
breaker".

You're probably OK with that then...

And yes, the CPC doesn't count - treat as 2 core.

Stewith

unread,
May 14, 2013, 1:30:32 PM5/14/13
to

"Andrew Mawson" <andrew@please_remove_me.mawson.org.uk> wrote in message
news:h6ednTG68vrT9Q_M...@bt.com...
According to the book, 90degree C SWA cable is rated at 36A when in free
air or on perforated cable tray, clipped direct it is 33A.
Buried is not listed in the table but the 70 degree SWA is rated at 1A
higher
buried than it is clipped direct, so it seems logical that your cable should
also
be OK at 1A higher (34A).


Fredxx

unread,
May 14, 2013, 2:15:08 PM5/14/13
to
I think doubly blinded!! Andrew mentioned using a 32A breaker because
his 9" grinder would trip a 20A breaker!

John Rumm

unread,
May 14, 2013, 2:15:47 PM5/14/13
to
On 14/05/2013 18:11, Tim Watts wrote:
He did say 32A MCB - I think the 20A bit was just an aside that the AG
trips one.

> And yes, the CPC doesn't count - treat as 2 core.

Indeed. And this is also one of those circumstances where one could
argue that the overload protection is enforced by the nature of the load
(i.e. they are not general purpose sockets, but designed to feed very
specific bits of kit), so all the head end MCB needs do is provide
adequate fault protection.


--
Cheers,

John.

/=================================================================\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\=================================================================/

Tim Lamb

unread,
May 14, 2013, 3:17:02 PM5/14/13
to
In message <h6ednTG68vrT9Q_M...@bt.com>, Andrew Mawson
<andrew@please_remove_me.mawson.org.uk> writes
Must be a Makita! Mine does that on a 20 amp ELCB. I rather wondered if
the build up of dust on the windings was causing 30mA of leakage?

Can you not use a 25 amp breaker or go to *C* rating?

BTW the trencher has reached my budget plus transport and is still a
long way off the last 10 seconds:-)
Must be lots of people planning GSHPs!



--
Tim Lamb

Tim Watts

unread,
May 14, 2013, 3:25:26 PM5/14/13
to
Gawd...

In which case, 6mm2 probably - maybe 4mm2 at a stretch - will have to check
the numbers properly.

No way will 2.5mm2 be adequate.

Andrew Mawson

unread,
May 15, 2013, 2:25:37 PM5/15/13
to
"Tim Lamb" wrote in message
news:PAyjlonu...@marfordfarm.demon.co.uk...
Well at the time of writing there are 94 people watching it and it's north
of �1300. The number of people who have rung me up asking me to stop the
auction must now exceed ten !

AWEM

Andrew Mawson

unread,
May 15, 2013, 2:35:22 PM5/15/13
to
"Tim Watts" wrote in message
news:6mfa6a-...@squidward.local.dionic.net...
Well rest assured that it's not getting 6mm - it's getting 2.5mm as it's in
the ground and has been for a year! Now I'm about to commission the gate
it's the fusing I was asking about NOT the cable. Standing load of the
electronic bits is less than an amp. Normal 'peak' load is something like 3
amps which happens when the gate opens - maybe 6 to 10 times a day for 25
seconds, then once every blue moon I >MAY< plug an angle grinder in which
>MAY<trip the 20 amp mcb I was planning to fit, so I was (and still am)
considering fitting a 32 amp breaker. My question was entirely based on the
current rating of three core (3 phase) swa in a single phase application.

AWEM

(Don't you just love threads that go off at tangents !!!!!!!!)

ARW

unread,
May 15, 2013, 3:53:15 PM5/15/13
to

ARW

unread,
May 15, 2013, 4:15:07 PM5/15/13
to
But it is not 3 phase is it? (rhetorical)

So Tim was right that you can ignore the 3rd core and treat it as 2 core.

Your CCC is 33A if the cable is buried.

If it was me I would try using a C type 20A MCB and see how things go.

--
Adam