SWMBO has decreed that she would like it to work 365 days a year, so she
has a nice warm towel to come out out of the shower to, which I believe
is fairly common practice to arrange when towel rails are installed?
However, if I am to accede to the request I need to get my head round
where the pipework needs changing.
System is as follows. Pipework to the gas-fired system boiler
downstairs is two 2 22mm pipes flow and return, along with gas in and
condensate out. The two 22mm pipes head upstairs and under the upstairs
floor, and through the house to the unvented HW cylinder lives in the
airing cupboard. Bathroom + towel rail is upstairs too, in the other
direction. HW and CH are controlled independently.
So - am I right in thinking that I can simply run a pair of new pipes
from my towel rail to intercept the two 22 mm pipes, in between boiler
and HW tank; and then the towel rail would simply go on and off with the
HW instead of with the CH?
Supplementary questions:
1. OK to run the new pipes in 10mm microbore (ie soldered direct to the
22mm pipes via T-adaptors) or would that screw things up? Whatever
happens, it's not an easy route to run the new pipework, microbore or
otherwise.
2. Would it be better or worse (from a long-term economy viewpoint) to
fit an electric element to the towel rail in parallel with the wet
system, and run that (off a time-switch) in the summer only?
Thanks
David
Probably slightly worse from economy to run it off electric, but does
your hot water system run whenever the shower does (which it woudln't
if the shower was electric, f'r instance)
Why not use a push-button timer set to about an hour, so that Mrs
Lobster can press the button before she slips into her bathrobe and
goes in, the towel will warm up while Mrs Lobster is slathering her
claws with whatever unguents Mrs Lobsters use in the shower, and the
rail will stay warm for a while afterwards to dry the towel.
About £30 from Elkay Energy Sense range www.elkay.co.uk/
If Mrs L spends longer than an hour in the shower she'll come out to a
cold towel, so an encouragement to her to use less hot water too.
Owain
You don't say where the HW and CH pipes split, or what controls/valves etc.
you've got.
I'm guessing that there's either a 3-port valve or 2 x 2-port valves in the
airing cupboard - controlling the CH and HW circuits? Is the pump also
there, or is it integral with the boiler? Either way, you need to take a
feed for the bathroom rad from the flow pipe *after* the pump but *before*
the valves. That way, the rad will be hot whenever either or both HW and CH
circuits are active. You *may* be able to leave the bathroom rad's return
pipe as it is - but check that this doesn't result in any reverse flow
problems (for example, causing some other rads to get hot when only the HW
is on).
--
Cheers,
Roger
______
Email address maintained for newsgroup use only, and not regularly
monitored.. Messages sent to it may not be read for several weeks.
PLEASE REPLY TO NEWSGROUP!
> You don't say where the HW and CH pipes split, or what controls/valves etc.
> you've got.
>
> I'm guessing that there's either a 3-port valve or 2 x 2-port valves in the
> airing cupboard - controlling the CH and HW circuits? Is the pump also
> there, or is it integral with the boiler?
OK, the pump's downstairs, integral with the boiler, and yes there's a
3-port valve plumbed in upstairs, just above the HW cylinder.
Either way, you need to
take a
> feed for the bathroom rad from the flow pipe *after* the pump but *before*
> the valves. That way, the rad will be hot whenever either or both HW and CH
> circuits are active.
So that sounds as if my plan above ("So - am I right in thinking...") is
correct then!
You *may* be able to leave the
bathroom rad's return
> pipe as it is - but check that this doesn't result in any reverse flow
> problems (for example, causing some other rads to get hot when only the HW
> is on).
Doesn't sound as if it's worth risking that; if I have to find a way to
get one new pipe through, then apart from making a couple more joints
there's no more aggro in running the second pipe alongside it.
Anyone got any feedback on my 'supplementaries'? ;-)
Many thanks
David
>Supplementary questions:
>1. OK to run the new pipes in 10mm microbore (ie soldered direct to the
> 22mm pipes via T-adaptors)
Yes. You will probably find that you still need to have the
balancing valve on the towel rail almost shut, otherwise most of the
water will circulate through the towel rail rather than the
radiators.
>2. Would it be better or worse (from a long-term economy viewpoint) to
>fit an electric element to the towel rail in parallel with the wet
>system, and run that (off a time-switch) in the summer only?
Depends on running hours, but in most circumstances better to heat
from the boiler. In general electric elements are fitted for ease
rather than reduced running costs.
--
David Hansen, Edinburgh
I will *always* explain revoked encryption keys, unless RIP prevents me
http://www.opsi.gov.uk/acts/acts2000/ukpga_20000023_en_8#pt3-pb3-l1g54
> Roger Mills wrote:
>
> You *may* be able to leave the bathroom rad's return
>> pipe as it is - but check that this doesn't result in any reverse
>> flow problems (for example, causing some other rads to get hot when
>> only the HW is on).
>
> Doesn't sound as if it's worth risking that; if I have to find a way
> to get one new pipe through, then apart from making a couple more
> joints there's no more aggro in running the second pipe alongside it.
>
If you want to achieve more or less the same effect without needing any
pipework changes, you might consider the following - which I used to do:
* Leave the bathroom rad(s) on the CH circuit
* In the winter, it/they will come on whenever the CH is on, which is
sufficient
* In the summer (when only the HW is on) remove the actuator from the 3-way
valve (but leave it connected electrically) and physically turn the wet bit
of the valve to the mid position
* Turn off all radiators except those in bathroom(s).
* Then, whenever the HW is being heated (as determined by the timer and
cylinder stat) the bathroom radiator(s) will also get hot.
If you chose a mechanical timer with continuous 15min segments on it
then you can have it on full around the time you shower most often to
dry wet towels then have it on at one segment in 3 or 4 to maintain a
base heat during the day.
The bathroom heat is provided by separate rads so the rail is always on
electric. Very effective and absolutely no hassle to install.
--
fred
BBC3, ITV2/3/4, channels going to the DOGs
> Why not use a push-button timer set to about an hour, so that Mrs
> Lobster can press the button before she slips into her bathrobe and
> goes in, the towel will warm up while Mrs Lobster is slathering her
> claws with whatever unguents Mrs Lobsters use in the shower, and the
> rail will stay warm for a while afterwards to dry the towel.
That's actually a rather good thought, provided it would warm up enough
during the time-course of the shower in order to do its stuff - what do
you reckon? If not, I can see me being forced into changing the switch
for a rocker, so the bloody thing would end up being switched on 24/7!
> About �30 from Elkay Energy Sense range www.elkay.co.uk/
Hmm, some quite interesting stuff there!
Thanks
David
> If not, I can see me being forced into changing the switch
> for a rocker, so the bloody thing would end up being switched on 24/7!
How about a flow-switch on the shower water supply? They come in both
15mm and 22mm sizes, ready-fixed to a short length of copper pipe. Great
for turning on things that need to come on with the shower, when the
occupant is likely to forget. I use one for my anti-condensation
extractor fan, since I share my house with two lodgers and would prefer
not to worry about other people forgetting to turn it on.
Pete
Depends how hot the towel rail gets and how long Mrs L spends in the
shower, but it should certainly take the chill off. If necessary just
switch it on a little earlier - or even an hour earlier, and plunge it
again when finished showering to dry, it will still only be on 2 hours
not 24.
Owain
Ah, but prime lobster-showering time is first thing in the morning; ie
she crawls directly from bed to shower (and trust me - 'just taking the
edge off' really wouldn't cut the mustard!). The alternative would be a
preset 7-day timer I suppose; our weekday and weekday getting-up times
being pretty fixed.
David
Interesting idea...
> * In the summer (when only the HW is on) remove the actuator from the 3-way
> valve (but leave it connected electrically) and physically turn the wet bit
> of the valve to the mid position
What does the above step achieve - preventing all the CH pipes getting
hot or something? If so why does the towel rail still get hot?
> * Turn off all radiators except those in bathroom(s).
> * Then, whenever the HW is being heated (as determined by the timer and
> cylinder stat) the bathroom radiator(s) will also get hot.
Thanks
David
In the summer, with the CH off, the actuator will keep the valve permanently
in the HW-only position. Removing the actuator (and leaving it off) enables
you to manually move the valve to the mid (HW+CH) position without any
danger of the actuator moving it back again.
In this position, water will circulate round the radiators whenever the HW
is being heated. That is why you need to turn off all radiators *except*
those in bathroom(s) which you *want* to get hot.
That would work then. Or you could have a concealed 7-day timer for
waking-up and a visible hour-timer for occasional occasions and
visitors.
Owain
Ah, OK. I think I'm missing something though: what's the difference
between doing that, and turning off all the rads except the towel rail,
and then controlling the CH (which in summer would then comprise just
the towel rail) separately as normal (ie, just having it come on for a
quick burst at shower time)?
Thanks
David
> Roger Mills wrote:
>>
>> In this position, water will circulate round the radiators whenever
>> the HW is being heated. That is why you need to turn off all
>> radiators *except* those in bathroom(s) which you *want* to get hot.
>
> Ah, OK. I think I'm missing something though: what's the difference
> between doing that, and turning off all the rads except the towel
> rail, and then controlling the CH (which in summer would then
> comprise just the towel rail) separately as normal (ie, just having
> it come on for a quick burst at shower time)?
>
The difference is that it will then be controlled by the room stat - which
may decide that it doesn't need to come on. OK, you can turn the stat up to
max, so that it comes on for the whole timer period. But, with the HW demand
satisfied, and the boiler firing just for the towel rail, there may not be
enough flow to prevent the boiler from overheating.
With my method, the towel rail is controlled by the *cylinder* stat, and
only comes on while the HW is actually being heated.
What about re-plumbing the shower's hot water feed through it?
Probably not long enough to heat towels through unless it's a long shower.
--
Andrew Gabriel
[email address is not usable -- followup in the newsgroup]
>
> What about re-plumbing the shower's hot water feed through it?
> Probably not long enough to heat towels through unless it's a long
> shower.
Also, the *only* time it would get hot would be when the shower is running -
which isn't particularly useful!
I think Mr Lobster has a problem here of his own making - it would
seem quite clearly that Mrs Lobster expects him to pander to her every
whim and wish, and in the past he has done so. I suspect there has
been a bit of carelessness here in that the OP has in fact lead his
better half to understand it *can* be done.
More fool, Mr Lobster - the first rule of anything that SWMBO requests
is the much sucking in of air, ( viz. the local builder),and an
indication of how difficult, how expensive and how long such a
requirement will be to the detriment of all other tasks that have been
set.
Will you youngsters never learn !!