In article <
7uSdnce1Ls048ALM...@brightview.co.uk>, John
Rumm <see.my.s...@nowhere.null> writes
>On 24/05/2013 08:23, Jon Connell wrote:
>> On 23/05/2013 18:42, John Rumm wrote:
>>> Have you considered simply fitting a prog stat for each boiler in an
>>> appropriate place in the respective zone?
>>>
>>> You could basically set the programmers to "always on" then, and let the
>>> programmable stats deal with the timing and variation of temperature.
>>
>> I was hoping for a single point of control to keep things simple, but
>> this does appear to be the consensus.
>
>The difficulty you will have is that you need one stat per zone, and
>they need to be located somewhere in the zone to be effective. Since
>most stats require local adjustment, you arrive at two prog stats as a
>simple solution.
>
The Honeywell CM907 wired stat has a remote sensor option, just a 10k
thermistor IIRC but you need to buy the Honeywell one to get the custom
terminal block that fits in the main unit to connect to the auxiliary
pushfit pins (although I was tight and didn't). I ran the sensor pair
over Cat5e twisted pair that was spare and I have the stat by the boiler
in the kitchen, away from impulsive fingers in the lounge. There's
programmable offset too in case the wiring upsets the set point.
I wouldn't expect wireless to work through too many thick walls but I
have run the CM927 (wireless) through 3 or so thinner solid walls.
I've also modded some non remote sense stats by simply clipping out the
thermistor and remoting it over twisted pair. An easy mod and working
well on my current install after the Honeywell croaked.
>There are some controls that will allow you to program both stats from
>one location. Vaillant control centres can act as a prog stat and also
>control a slave one for a second zone. However they are quite boiler
>specific, and they assume that both zones are being driven from the same
>boiler.
>
Useful info ta.