Electrical socket from light switch for cctv.

931 views
Skip to first unread message

malcolmf

unread,
Nov 16, 2012, 7:56:53 PM11/16/12
to

Is it acceptable in the uk to put a socket for a cctv camera off of a
light switch? The socket would only be a single and would be at approx
7/8 feet high. I know its possible and that the draw is very low but
more asking if its against uk regulations. Cctv power is an ac to dc
converter with standard uk plug.

Thank you




--
malcolmf

Java Jive

unread,
Nov 16, 2012, 9:19:22 PM11/16/12
to
IANAE, but AIUI, you have to use a fused spur. Otherwise someone
could come along and plug an electric fire or kettle into it, and fry
the lighting circuit, possibly setting fire to the house as a result.

This means that if the CCTV PSU is of the wall-wart variety, it's a
no-no - you'll have to take a spur off a ring main - but if it's
an inline unit, as with say Dell laptop PSUs, then you can cut off the
three-pin plug and wire the power lead into the fused spur outlet. Of
course, the fuse in the spur unit needs to be 3A or less.
=========================================================
Please always reply to ng as the email in this post's
header does not exist. Or use a contact address at:
http://www.macfh.co.uk/JavaJive/JavaJive.html
http://www.macfh.co.uk/Macfarlane/Macfarlane.html

Bill Wright

unread,
Nov 16, 2012, 9:54:36 PM11/16/12
to
malcolmf wrote:
> Is it acceptable in the uk to put a socket for a cctv camera off of a
> light switch?
>
Where will you get the neutral from?

Bill

charles

unread,
Nov 17, 2012, 2:48:39 AM11/17/12
to
In article <malcolmf...@diybanter.com>,
you should use a 2 Amp socket.

--
From KT24

Using a RISC OS computer running v5.18

Archibald

unread,
Nov 17, 2012, 2:52:42 AM11/17/12
to
On Sat, 17 Nov 2012 02:19:22 +0000, Java Jive <ja...@evij.com.invalid>
wrote:

>IANAE, but AIUI, you have to use a fused spur. Otherwise someone
>could come along and plug an electric fire or kettle into it, and fry
>the lighting circuit, possibly setting fire to the house as a result.
>
Killing the cat, sparking off a nuclear event, accellerating global
warming and throwing the western world back into the dark ages.

Most houses have circuit breakers these days you know, before that
there were fuses.

Although it may be frowned on to dangle the heating system, shower and
grandmas iron lung off the lighting circuit, I still wouldn,t think
that the purchase of a fire extinguisher would be a worthwhile
enterprise.





>This means that if the CCTV PSU is of the wall-wart variety, it's a
>no-no - you'll have to take a spur off a ring main - but if it's
>an inline unit, as with say Dell laptop PSUs, then you can cut off the
>three-pin plug and wire the power lead into the fused spur outlet. Of
>course, the fuse in the spur unit needs to be 3A or less.
>
>On Sat, 17 Nov 2012 00:56:53 +0000, malcolmf
><malcolmf...@diybanter.com> wrote:
>
>>
>> Is it acceptable in the uk to put a socket for a cctv camera off of a
>> light switch? The socket would only be a single and would be at approx
>> 7/8 feet high. I know its possible and that the draw is very low but
>> more asking if its against uk regulations. Cctv power is an ac to dc
>> converter with standard uk plug.
>>
>> Thank you

I cannot recollect what the regulations say, but bathroom fans are fed
from the lighting circuit and the loads ust be similar.

Practically as a minimum I would use a dedicated connector that
couldn't be connected to accidentally, or better still wire directly
to a fused spur. Mounted outside, the camera should from a practical
point of view be on its own circuit with an RCBO protecting it, unless
of course you enjoy hunting around for ladders, tools etc in the dark
during a thundestorm.

HN

Tim+

unread,
Nov 17, 2012, 3:06:05 AM11/17/12
to
Well it's okay to have wall-switched sockets for table lamps etc. so I
don't see why not but you should use a round pin 5amp socket to avoid any
possibility of a normal appliance being plugged in.

Tim

Archibald

unread,
Nov 17, 2012, 3:18:27 AM11/17/12
to
He might have to use a a bit of force to get the standard UK plug in.

:-)


HN

harry

unread,
Nov 17, 2012, 4:09:07 AM11/17/12
to
You can use a 5amp socket. This precludes the possibilty of anyone
plugging anything else into it
http://www.screwfix.com/p/crabtree-5a-unswitched-socket/59778

You will have to find a neutral and earth.

Archibald

unread,
Nov 17, 2012, 5:07:49 AM11/17/12
to
Single wire system. Fully tried & tested, it was used by the Daleks
for eons and was only superceeded when the stairs encountered on Earth
forced them to adopt storage batteries and levitation.

HN

Gazz

unread,
Nov 17, 2012, 6:43:32 AM11/17/12
to


"malcolmf" <malcolmf...@diybanter.com> wrote in message
news:malcolmf...@diybanter.com...
Is the camera wireless or something then?

as if it's a standard wired one, you need to run the signal wire back to the
DVR, then get some 'shotgun' cable, which is 2 cables moulded side by side,
signal on one, and power on the other,

fit the wall wart next to the DVR, and connect it's output to the power
wires in the shotgun cable, pleg other end of cable into camera as normal.

I did similar to this on my cctv setup, but used an 18 way, 15 amp 12 volt
psu in a wall mounting box for the power to the camera's,

If the camera is a wireless jobbie, would it not be easier to extend the 12
volt wire from the wall wart and run it to the camera.

jgharston

unread,
Nov 17, 2012, 7:10:54 AM11/17/12
to
The OP asked about a CCTV socket off a light switch, not off
a lighting circuit. Admittedly, a bit of ambiguity there. If he
means "use a light switch to turn the power socket on and
off", then, yes, it's allowable as long as the circuit is /supplied/
from a power circuit and the circuit is protected by a 5A fuse/etc
upstream from the switch.

Eg: ring main-->5A Fused Spur---->5A "light" switch--->CCTV socket

I have exactly the same arrangement in my roofspace with "cctv"
replaced with "light".

If the OP means "can I take power from a lighting circuit", the
answer is a clear "no".

JGH

meow...@care2.com

unread,
Nov 17, 2012, 7:22:39 AM11/17/12
to
Its fine to connect it to a lighting circuit using a shuttered 2A or 5A round pin socket, or an FCU, but not a 13A socket.


NT

Tim+

unread,
Nov 17, 2012, 7:33:23 AM11/17/12
to
How do your light bulbs work if they don't consume power?

Tim

Dave Plowman (News)

unread,
Nov 17, 2012, 7:59:11 AM11/17/12
to
In article <lhsda8lj01arvhpdv...@4ax.com>,
Java Jive <ja...@evij.com.invalid> wrote:
> IANAE, but AIUI, you have to use a fused spur. Otherwise someone
> could come along and plug an electric fire or kettle into it, and fry
> the lighting circuit, possibly setting fire to the house as a result.

Then you need to have the house wiring seen to immediately. Lighting
circuits should be protected by a suitable device in the CU to prevent the
wiring frying even in event of a dead short.

--
*If tennis elbow is painful, imagine suffering with tennis balls *

Dave Plowman da...@davenoise.co.uk London SW
To e-mail, change noise into sound.

JTM

unread,
Nov 17, 2012, 8:15:21 AM11/17/12
to
In article <raoea8lai3s32vo00...@4ax.com>,
someone wrote:
> >You will have to find a neutral and earth.
Would these do?
https://www.dropbox.com/s/pp6nm6gcpes9hi3/wires.jpg

John

John Rumm

unread,
Nov 17, 2012, 8:59:11 AM11/17/12
to
Powering a low current load from a lighting circuit is acceptable and
often done for things like extractor fans etc.

You can install sockets as well, although it is preferable to use one of
the small round pin shuttered 2 or 5A ones to prevent someone connecting
high current devices to the circuit and tripping it.

However connecting to a light switch as such may be a problem since you
usually only have two live wires (one switched) and no neutral.

Unless specified by the manufacturer, there is not usually any
requirement for a fused connection unit (aka spur unit) since they
circuit will typically be protected with a MCB that has a rating well
below the current carrying capacity of the cable.


--
Cheers,

John.

/=================================================================\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\=================================================================/

Jules Richardson

unread,
Nov 17, 2012, 12:30:09 PM11/17/12
to
String some bell wire across from a nearby lamp fitting?

ARW

unread,
Nov 17, 2012, 12:56:28 PM11/17/12
to
CT100 would be Bill's prefered cable:-)

--
Adam


ARW

unread,
Nov 17, 2012, 1:17:34 PM11/17/12
to
Gazz wrote:
> "malcolmf" <malcolmf...@diybanter.com> wrote in message
> news:malcolmf...@diybanter.com...
> >
> > Is it acceptable in the uk to put a socket for a cctv camera off of
> > a light switch? The socket would only be a single and would be at
> > approx 7/8 feet high. I know its possible and that the draw is very
> > low but more asking if its against uk regulations. Cctv power is an
> > ac to dc converter with standard uk plug.
>
> Is the camera wireless or something then?
>
> as if it's a standard wired one, you need to run the signal wire back
> to the DVR, then get some 'shotgun' cable, which is 2 cables moulded
> side by side, signal on one, and power on the other,

All the CCTV I fit uses CAT5 cable.

--
Adam


ARW

unread,
Nov 17, 2012, 1:18:33 PM11/17/12
to
Not even a 13A socket that is labelled CCTV ONLY?

--
Adam


John Rumm

unread,
Nov 17, 2012, 4:41:02 PM11/17/12
to
It would only be fair, he had seen the way electricians wire aerials ;-)

Gazz

unread,
Nov 17, 2012, 6:01:31 PM11/17/12
to

>> as if it's a standard wired one, you need to run the signal wire back
>> to the DVR, then get some 'shotgun' cable, which is 2 cables moulded
>> side by side, signal on one, and power on the other,
>
> All the CCTV I fit uses CAT5 cable.

Yeah but i don't imagine he's talking about a megapixel camera, or is going
to fanny about with baluns and all that.
it could be one of those 5 quid chingchong cameras off fleabay. a pair of
baluns would be 20 times what the camera is worth (worth not cost :)


Bill Wright

unread,
Nov 18, 2012, 12:13:59 AM11/18/12
to
ARW wrote:

> CT100 would be Bill's prefered cable:-)
>
The best way to use coax for mains is to use the inner for line and the
outer for neutral. Don't bother about an earth. No-one bothers
connecting the earth these days. It's just a hang-over from the early
days of radio when a good earth was needed for reception. Note that
when you power your electric fire through coax you actually save on your
electricity bill because the coax gets very hot and helps warm the room.
There is no cost for this because it's the same electricity as is going
through the fire, so you get the benefit of it twice. If the small of
burning plastic bothers you just push the coax under the rug.

Bill

Bill Wright

unread,
Nov 18, 2012, 12:17:07 AM11/18/12
to
John Rumm wrote:

>> CT100 would be Bill's prefered cable:-)
>
> It would only be fair, he had seen the way electricians wire aerials ;-)

Don't get me started.

http://www.wrightsaerials.tv/roguesgallery/035.shtml

Bill

charles

unread,
Nov 18, 2012, 12:35:53 AM11/18/12
to
In article <k89qqm$s6v$1...@speranza.aioe.org>,
Bill Wright <bi...@invalid.com> wrote:
> ARW wrote:

> > CT100 would be Bill's prefered cable:-)
> >
> The best way to use coax for mains is to use the inner for line and the
> outer for neutral. Don't bother about an earth.

[Snip]

Bill's not wrong. When a student and working with SSEB, I came across a
small area in Edinburgh which was wired with "concentric" mains cable.

Bill Wright

unread,
Nov 18, 2012, 12:47:28 AM11/18/12
to
charles wrote:
> In article <k89qqm$s6v$1...@speranza.aioe.org>,
> Bill Wright <bi...@invalid.com> wrote:
>> ARW wrote:
>
>>> CT100 would be Bill's prefered cable:-)
>>>
>> The best way to use coax for mains is to use the inner for line and the
>> outer for neutral. Don't bother about an earth.
>
> [Snip]
>
> Bill's not wrong. When a student and working with SSEB, I came across a
> small area in Edinburgh which was wired with "concentric" mains cable.
>
Well there you are then. What's good enough for Auld Reekie is good
enough for me. What was the csa of the inner, by the way? A tad more
than 1mm2 I would guess?

Of course nowadays they use coax with two inners for mains supplies...

Bill

harry

unread,
Nov 18, 2012, 2:15:02 AM11/18/12
to
On Nov 18, 5:47 am, Bill Wright <b...@invalid.com> wrote:
> charles wrote:
> > In article <k89qqm$s6...@speranza.aioe.org>,
> >    Bill Wright <b...@invalid.com> wrote:
> >> ARW wrote:
>
> >>> CT100 would be Bill's prefered cable:-)
>
> >> The best way to use coax for mains is to use the inner for line and the
> >> outer for neutral. Don't bother about an earth.
>
> > [Snip]
>
> > Bill's not wrong. When a student and working with SSEB, I came across a
> > small area in Edinburgh which was wired with "concentric" mains cable.
>
> Well there you are then. What's good enough for Auld Reekie is good
> enough for me. What was the csa of the inner, by the way? A tad more
> than 1mm2 I would guess?
>
> Of course nowadays they use coax with two inners for mains supplies...
>
> Bill

There was indeed coax for mains. The core was live. Of the outer
conductor, half the strands were individually insulated, which were
neutrals and the the other were not, which were the earth.
Haven't seen any for forty years.
It was supposed to be safer as the live conductor was inside the
others.

The Natural Philosopher

unread,
Nov 18, 2012, 3:33:51 AM11/18/12
to
You sure? when I laid mine it just had an outer and an inner.

> Bill


--
Ineptocracy

(in-ep-toc’-ra-cy) – a system of government where the least capable to
lead are elected by the least capable of producing, and where the
members of society least likely to sustain themselves or succeed, are
rewarded with goods and services paid for by the confiscated wealth of a
diminishing number of producers.

John Rumm

unread,
Nov 18, 2012, 5:00:57 AM11/18/12
to
Its called "split concentric"...

> Haven't seen any for forty years.

Still in common use, you can see it here:

http://wiki.diyfaq.org.uk/index.php?title=File:TNSUsingPMECutout3.jpg

> It was supposed to be safer as the live conductor was inside the
> others.

I suspect its real benefit is its much harder to stick nails through and
steal electricity.

meow...@care2.com

unread,
Nov 18, 2012, 6:39:44 AM11/18/12
to
I didn't think that was regs compliant. Plugging normal loads in would result in circuit overload.


NT

A.Lee

unread,
Nov 18, 2012, 7:02:59 AM11/18/12
to
<meow...@care2.com> wrote:

> On Saturday, November 17, 2012 6:18 adamwa...@blueyonder.co.uk wrote:
> > meow...@care2.com wrote:

> > > Its fine to connect it to a lighting circuit using a shuttered 2A or
> > > 5A round pin socket, or an FCU, but not a 13A socket.
>
> > Not even a 13A socket that is labelled CCTV ONLY?
>
> I didn't think that was regs compliant. Plugging normal loads in would
> result in circuit overload.

Considering most lighting circuits are in 1.5mm T+E, the cable can run
13 amps continuous if it is on a plasterboard ceiling, covered by
thermal insulation.
A change from 6A to 10A CB would suffice if the 6A was likely to be
exceeded, and still gives a big margin for safety of the cable.

Apart from some heaters and other large current eaters, lighting
circuits would be quite capable of carrying a number of socket outlets
if they were marked for low wattage appliances.
It is common for extractor fans and TV boosters/Sky boxes to run from
the lighting circuit in an attic.



--
To reply by e-mail, change the ' + ' to 'plus'.

Dave Liquorice

unread,
Nov 18, 2012, 7:04:10 AM11/18/12
to
On Sun, 18 Nov 2012 03:39:44 -0800 (PST), meow...@care2.com wrote:

>> Not even a 13A socket that is labelled CCTV ONLY?
>
> I didn't think that was regs compliant. Plugging normal loads in would
> result in circuit overload.

The lighting fuse/MCB would then operate...

Donno what the regs say but I can't see what is wrong with a 13A socket
connected to the lighting circuit via a FCU and 3A (or smaller) fuse.
Everything suitably labled as well.

I think there still needs to be clarification from the OP of what he
means By "Is it acceptable in the uk to put a socket for a cctv camera
off of a light switch?"

Is he looking to derive a power feed from the back of a light switch
direct to a socket or use a light switch as a switch to a remote socket
fed from a ring main or lighting power?

--
Cheers
Dave.



meow...@care2.com

unread,
Nov 18, 2012, 8:55:04 AM11/18/12
to
On Sunday, November 18, 2012 12:02:59 PM UTC, A.Lee wrote:
> <meow2222> wrote:
> > On Saturday, November 17, 2012 6:18 adamwa... wrote:
> > > meow2222 wrote:

> > > > Its fine to connect it to a lighting circuit using a shuttered 2A or
> > > > 5A round pin socket, or an FCU, but not a 13A socket.

> > > Not even a 13A socket that is labelled CCTV ONLY?

> > I didn't think that was regs compliant. Plugging normal loads in would
> > result in circuit overload.

> Considering most lighting circuits are in 1.5mm T+E, the cable can run
> 13 amps continuous if it is on a plasterboard ceiling, covered by
> thermal insulation.
> A change from 6A to 10A CB would suffice if the 6A was likely to be
> exceeded, and still gives a big margin for safety of the cable.
> Apart from some heaters and other large current eaters, lighting
> circuits would be quite capable of carrying a number of socket outlets
> if they were marked for low wattage appliances.
> It is common for extractor fans and TV boosters/Sky boxes to run from
> the lighting circuit in an attic.

'apart from.'

Many electrical items are capable of more than the regs permit. Bell wire is a classic example.


NT

John Rumm

unread,
Nov 18, 2012, 9:20:03 AM11/18/12
to
I am not aware of any specific regulation that says you can't use a 13A
socket on a circuit with a lower rating.

The main concern would be that a high load connected to it would cause
tripping of the circuit, and that in turn may pose a risk due to loss of
lighting. Hence it is required that the designer make sensible
decisions. So rigging an extra socket on your landing that is fed from
the lighting circuit would not be sensible - since someone is very
likely to plug a vacuum cleaner into it etc. However one in the loft
space intended to feed an aerial amp really poses no risk. Likewise,
socket designed for powering table lamps etc would be fine on a lighting
circuit - although in that circumstance using a physically incompatible
socket would make sense since it will be in proximity to general purpose
power sockets.

Cables on lighting circuits are usually fairly generously oversized, and
the cable rating is significantly in excess of the circuit breaker. So
you can't create a situation where you can overload the cable.

(a similar situation exists with a typical cooker on a 6mm^2 radial with
a 32A MCB)

Dave Plowman (News)

unread,
Nov 18, 2012, 9:34:34 AM11/18/12
to
In article <c576f5aa-82fb-4e4d...@googlegroups.com>,
<meow...@care2.com> wrote:
> Many electrical items are capable of more than the regs permit. Bell
> wire is a classic example.

You could probably get fencing wire to 'work' too. ;-)

--
*The sooner you fall behind, the more time you'll have to catch up *

Lieutenant Scott

unread,
Nov 18, 2012, 9:50:23 AM11/18/12
to
On Sat, 17 Nov 2012 02:54:36 -0000, Bill Wright <bi...@invalid.com> wrote:

> malcolmf wrote:
>> Is it acceptable in the uk to put a socket for a cctv camera off of a
>> light switch?
>>
> Where will you get the neutral from?

My light switches have a neutral. The mains is under the floor, comes up through the lightswitch, to the lighting in the ceiling.

Just as well, as I fitted automatic lightswitch (with a PIR) which need power.

Mind you one of my light switches for some reason doesn't have a neutral present. But earth suffices as a neutral.

--
http://petersparrots.com
http://petersphotos.com

I want to die peacefully, in my sleep, like my Uncle Bob. Not screaming in terror like his passengers...

Lieutenant Scott

unread,
Nov 18, 2012, 9:54:55 AM11/18/12
to
How do you know those wires are even live?
People are more violently opposed to fur than leather because it's safer to harass rich women than motorcycle gangs.

Lieutenant Scott

unread,
Nov 18, 2012, 9:56:54 AM11/18/12
to
It would result in the breaker tripping, not the end of the world.
Saying that she is promiscuous is an understatement.
She'll go zero to sixty-nine in under fifteen seconds."

Dave Plowman (News)

unread,
Nov 18, 2012, 10:03:26 AM11/18/12
to
In article <3vydna5Npu8hczXN...@brightview.co.uk>,
John Rumm <see.my.s...@nowhere.null> wrote:
> Likewise,
> socket designed for powering table lamps etc would be fine on a lighting
> circuit - although in that circumstance using a physically incompatible
> socket would make sense since it will be in proximity to general purpose
> power sockets.

More likely scenario is someone plugs in a vacuum cleaner or whatever into
a lighting circuit on a dimmer, and fooks the dimmer.

--
*If you don't like the news, go out and make some.

critcher

unread,
Nov 18, 2012, 11:07:20 AM11/18/12
to
On 18/11/2012 14:50, Lieutenant Scott wrote:
> On Sat, 17 Nov 2012 02:54:36 -0000, Bill Wright <bi...@invalid.com> wrote:
>
>> malcolmf wrote:
>>> Is it acceptable in the uk to put a socket for a cctv camera off of a
>>> light switch?
>>>
>> Where will you get the neutral from?
>
> My light switches have a neutral. The mains is under the floor, comes
> up through the lightswitch, to the lighting in the ceiling.
>
> Just as well, as I fitted automatic lightswitch (with a PIR) which need
> power.
>
> Mind you one of my light switches for some reason doesn't have a neutral
> present. But earth suffices as a neutral.
>



critcher said...................
I remember my mum plugging her electric iron into the light socket, but
she couldn't see what she was ironing at night.

critcher

unread,
Nov 18, 2012, 11:10:59 AM11/18/12
to
hang on I remember now, she had a socket with a dual output on it.

Lieutenant Scott

unread,
Nov 18, 2012, 11:19:36 AM11/18/12
to
Didn't she have a http://www.ebay.co.uk/itm/300818581986 ?
The children were lined up in the cafeteria of a Catholic elementary school for lunch. At the head of the table was a large pile of apples. The nun made a note, and posted on the apple tray: "Take only ONE. god is watching."
Moving further along the lunch line, at the other end of the table was a large pile of chocolate chip cookies. A child had written a note, "Take all you want. god is watching the apples."

critcher

unread,
Nov 18, 2012, 11:44:33 AM11/18/12
to
On 18/11/2012 16:19, Lieutenant Scott wrote:
> On Sun, 18 Nov 2012 16:07:20 -0000, critcher <w.g...@sky.com> wrote:
>
>> On 18/11/2012 14:50, Lieutenant Scott wrote:
>>> On Sat, 17 Nov 2012 02:54:36 -0000, Bill Wright <bi...@invalid.com>
>>> wrote:
>>>
>>>> malcolmf wrote:
>>>>> Is it acceptable in the uk to put a socket for a cctv camera off of a
>>>>> light switch?
>>>>>
>>>> Where will you get the neutral from?
>>>
>>> My light switches have a neutral. The mains is under the floor, comes
>>> up through the lightswitch, to the lighting in the ceiling.
>>>
>>> Just as well, as I fitted automatic lightswitch (with a PIR) which need
>>> power.
>>>
>>> Mind you one of my light switches for some reason doesn't have a neutral
>>> present. But earth suffices as a neutral.
>>
>> critcher said...................
>> I remember my mum plugging her electric iron into the light socket, but
>> she couldn't see what she was ironing at night.
>
> Didn't she have a http://www.ebay.co.uk/itm/300818581986 ?
>


yes, that was in my second post.

Lieutenant Scott

unread,
Nov 18, 2012, 11:53:08 AM11/18/12
to
How did you accidentally remember it being dark? Maybe the iron used more than 5 amps.
An expert is someone who takes a subject you understand and makes it sound confusing.

ARW

unread,
Nov 18, 2012, 12:23:11 PM11/18/12
to
I can find a shot on streetview of an apprentice leaning out of a hotel
window and using strip connector to extend an aerial cable:-)



--
Adam


ARW

unread,
Nov 18, 2012, 12:30:55 PM11/18/12
to
meow...@care2.com wrote:
> On Saturday, November 17, 2012 6:18:34 PM UTC,
> adamwa...@blueyonder.co.uk wrote:
> > meow...@care2.com wrote:
> > > On Saturday, November 17, 2012 12:56:53 AM UTC, malcolmf wrote:
>
> > > > Is it acceptable in the uk to put a socket for a cctv camera
> > > > off of a light switch? The socket would only be a single and
> > > > would be at approx 7/8 feet high. I know its possible and that
> > > > the draw is very low but more asking if its against uk
> > > > regulations. Cctv power is an ac to dc converter with standard
> > > > uk plug.
> > > > Thank you
>
> > > Its fine to connect it to a lighting circuit using a shuttered 2A
> > > or 5A round pin socket, or an FCU, but not a 13A socket.
>
> > Not even a 13A socket that is labelled CCTV ONLY?
>
> I didn't think that was regs compliant. Plugging normal loads in
> would result in circuit overload.

I don't know of a reg that forbids it provided that the outlet is labelled
for a specific appliance.

And if someone did plug a 3kW heater in then the fuse or MCB will trip and
nothing bad happens.

--
Adam


meow...@care2.com

unread,
Nov 18, 2012, 1:37:46 PM11/18/12
to
On Sunday, November 18, 2012 2:36:26 PM UTC, Dave Plowman (News) wrote:
> In article <c576f5aa-82fb-4e4d...@googlegroups.com>,
> <meow2222> wrote:

> > Many electrical items are capable of more than the regs permit. Bell
> > wire is a classic example.
> You could probably get fencing wire to 'work' too. ;-)

That's about what they used when Victoria was still alive.


NT

Adam Funk

unread,
Nov 18, 2012, 3:46:43 PM11/18/12
to
On 2012-11-18, Dave Plowman (News) wrote:

> In article <c576f5aa-82fb-4e4d...@googlegroups.com>,
> <meow...@care2.com> wrote:
>> Many electrical items are capable of more than the regs permit. Bell
>> wire is a classic example.
>
> You could probably get fencing wire to 'work' too. ;-)

That's how the electric fence was discovered, right?

m...@privacy.net

unread,
Nov 18, 2012, 7:34:15 PM11/18/12
to
On 17 Nov,
John Rumm <see.my.s...@nowhere.null> wrote:

> Unless specified by the manufacturer, there is not usually any
> requirement for a fused connection unit (aka spur unit) since they
> circuit will typically be protected with a MCB that has a rating well
> below the current carrying capacity of the cable.
>
But an FCU with 3a fuse may be required (or at least desirable) for
discrimination, to protect from loss of lighting due to plugging in an
appliance of excessive rating. This is assuming that a 13a socket outlet is
used to connect teh camera supply.

--
B Thumbs
Change lycos to yahoo to reply

John Rumm

unread,
Nov 19, 2012, 8:49:33 AM11/19/12
to
Yes its a valid argument, although its debatable if you will actually
get much discrimination with the arrangement in that order. (i.e. MCB
upline of a fuse). Also if fitting a socket to a lighting circuit it
will normally be for a specific purpose rather than a general socket, so
the chances of accidental overload should be small.

The main argument for using a FCU etc would be for connecting a bit of
fixed equipment that specifies it must be protected at 3A.

bert

unread,
Nov 20, 2012, 9:12:03 AM11/20/12
to
In message <k89qqm$s6v$1...@speranza.aioe.org>, Bill Wright
<bi...@invalid.com> writes
>Note that when you power your electric fire through coax you actually
>save on your electricity bill because the coax gets very hot and helps
>warm the room. There is no cost for this because it's the same
>electricity as is going through the fire, so you get the benefit of it
>twice.
<Snip>

Err no. If you're getting heat out he cable it's because it has
resistance which reduces the total current through the cable/fire
combination.
Any heat gain in the cable has an equal reduction in the fire.
--
bert

bert

unread,
Nov 20, 2012, 9:21:58 AM11/20/12
to
In message <op.wny4t9naytk5n5@i7-940>, Lieutenant Scott <n...@spam.com>
writes
>On Sat, 17 Nov 2012 02:54:36 -0000, Bill Wright <bi...@invalid.com> wrote:
>
>> malcolmf wrote:
>>> Is it acceptable in the uk to put a socket for a cctv camera off of a
>>> light switch?
>>>
>> Where will you get the neutral from?
>
>My light switches have a neutral. The mains is under the floor, comes
>up through the lightswitch, to the lighting in the ceiling.
>
>Just as well, as I fitted automatic lightswitch (with a PIR) which need power.
>
>Mind you one of my light switches for some reason doesn't have a
>neutral present. But earth suffices as a neutral.
>
I had reason to look up the wring regs regarding using a surplus earth
as a neutral in my room thermostat. Definite no-no. Also wrapping the
visible end with blue tape also a no-no.

--
bert

polygonum

unread,
Nov 20, 2012, 9:56:31 AM11/20/12
to
On 20/11/2012 14:12, bert wrote:
> In message <k89qqm$s6v$1...@speranza.aioe.org>, Bill Wright
> <bi...@invalid.com> writes

<haha>

>> Note that when you power your electric fire through coax you actually
>> save on your electricity bill because the coax gets very hot and helps
>> warm the room. There is no cost for this because it's the same
>> electricity as is going through the fire, so you get the benefit of it
>> twice.

</haha>

> <Snip>
>
> Err no. If you're getting heat out he cable it's because it has
> resistance which reduces the total current through the cable/fire
> combination.
> Any heat gain in the cable has an equal reduction in the fire.

Is that better?

--
Rod

John Williamson

unread,
Nov 20, 2012, 10:46:03 AM11/20/12
to
Err...

You're right about the resistance in the cable causing it to heat up.
But... You save money per hour of running time due to the reduced power
drawn, but you also get less total heat per hour for the same reason.
The cost per kilowatt hour of heat is the same, ignoring losses outside
the room.

--
Tciao for Now!

John.

Owain

unread,
Nov 20, 2012, 11:15:22 AM11/20/12
to
On Nov 20, 3:46 pm, John Williamson wrote:
> You're right about the resistance in the cable causing it to heat up.
> But... You save money per hour of running time due to the reduced power
> drawn, but you also get less total heat per hour for the same reason.
> The cost per kilowatt hour of heat is the same, ignoring losses outside
> the room.

Unless you're on a two-tier tariff, or one with a standing charge, in
which case the average cost per kilowatt-hour will fall the more you
use.

Owain

John Rumm

unread,
Nov 20, 2012, 12:12:54 PM11/20/12
to
On 20/11/2012 14:12, bert wrote:
I think you may have missed Bill's tongue being firmly in his cheek there!

John Rumm

unread,
Nov 20, 2012, 12:15:31 PM11/20/12
to
Using an earth as a neutral is a way to ensure an instant RCD trip on a
recent installation.

bert

unread,
Nov 20, 2012, 1:06:55 PM11/20/12
to
In message <ah1mtv...@mid.individual.net>, John Williamson
<johnwil...@btinternet.com> writes
Yes I agree In fact I had overlooked the impact of higher total
resistance resulting in less power, but the original poster of the
comment implied or stated you were getting extra heat for nothing, which
is wrong.
--
bert

bert

unread,
Nov 20, 2012, 1:09:59 PM11/20/12
to
In message <7pudnUKteb_cJzbN...@brightview.co.uk>, John
Rumm <see.my.s...@nowhere.null> writes
>On 20/11/2012 14:12, bert wrote:
>> In message <k89qqm$s6v$1...@speranza.aioe.org>, Bill Wright
>> <bi...@invalid.com> writes
>>> Note that when you power your electric fire through coax you actually
>>> save on your electricity bill because the coax gets very hot and helps
>>> warm the room. There is no cost for this because it's the same
>>> electricity as is going through the fire, so you get the benefit of it
>>> twice.
>> <Snip>
>>
>> Err no. If you're getting heat out he cable it's because it has
>> resistance which reduces the total current through the cable/fire
>> combination.
>> Any heat gain in the cable has an equal reduction in the fire.
>
>I think you may have missed Bill's tongue being firmly in his cheek there!
>
Irony and T-I-C don't do well on t'internet
--
bert

bert

unread,
Nov 20, 2012, 1:11:26 PM11/20/12
to
In message <7pudnX2teb9CJzbN...@brightview.co.uk>, John
Rumm <see.my.s...@nowhere.null> writes
>On 20/11/2012 14:21, bert wrote:
>> In message <op.wny4t9naytk5n5@i7-940>, Lieutenant Scott <n...@spam.com>
>> writes
>>> On Sat, 17 Nov 2012 02:54:36 -0000, Bill Wright <bi...@invalid.com> wrote:
>>>
>>>> malcolmf wrote:
>>>>> Is it acceptable in the uk to put a socket for a cctv camera off of a
>>>>> light switch?
>>>>>
>>>> Where will you get the neutral from?
>>>
>>> My light switches have a neutral. The mains is under the floor, comes
>>> up through the lightswitch, to the lighting in the ceiling.
>>>
>>> Just as well, as I fitted automatic lightswitch (with a PIR) which
>>> need power.
>>>
>>> Mind you one of my light switches for some reason doesn't have a
>>> neutral present. But earth suffices as a neutral.
>>>
>
>> I had reason to look up the wring regs regarding using a surplus earth
>> as a neutral in my room thermostat. Definite no-no. Also wrapping the
>> visible end with blue tape also a no-no.
>
>Using an earth as a neutral is a way to ensure an instant RCD trip on a
>recent installation.
>
If you want to use it as a neutral then you disconnect both ends from
earth.
--
bert

John Rumm

unread,
Nov 20, 2012, 2:49:33 PM11/20/12
to
If you read much of Bill's output you would realise they are both alive
and well ;-)

John Rumm

unread,
Nov 20, 2012, 2:52:00 PM11/20/12
to
I suspect that scotty (being a class A plonker) was suggesting that one
can use it directly while still connected to earth at the far end.
(still its safe for him, because mains shocks are not dangerous he tells
us!)

Lieutenant Scott

unread,
Nov 20, 2012, 4:01:20 PM11/20/12
to
WTF has this to do with a shock? I never said use the earth as a live.
Why do they call it a TV set when you only get one?

Lieutenant Scott

unread,
Nov 20, 2012, 4:01:36 PM11/20/12
to
Earth and neutral are both zero volts, it works just fine.
Yorkshire man takes his cat to the vet.
Yorkshireman: "Ayup, lad, I need to talk to thee about me cat."
Vet: "Is it a tom?"
Yorkshireman: "Nay, I've browt it wi' us."

Lieutenant Scott

unread,
Nov 20, 2012, 4:03:23 PM11/20/12
to
On Tue, 20 Nov 2012 17:15:31 -0000, John Rumm <see.my.s...@nowhere.null> wrote:

> On 20/11/2012 14:21, bert wrote:
>> In message <op.wny4t9naytk5n5@i7-940>, Lieutenant Scott <n...@spam.com>
>> writes
>>> On Sat, 17 Nov 2012 02:54:36 -0000, Bill Wright <bi...@invalid.com> wrote:
>>>
>>>> malcolmf wrote:
>>>>> Is it acceptable in the uk to put a socket for a cctv camera off of a
>>>>> light switch?
>>>>>
>>>> Where will you get the neutral from?
>>>
>>> My light switches have a neutral. The mains is under the floor, comes
>>> up through the lightswitch, to the lighting in the ceiling.
>>>
>>> Just as well, as I fitted automatic lightswitch (with a PIR) which
>>> need power.
>>>
>>> Mind you one of my light switches for some reason doesn't have a
>>> neutral present. But earth suffices as a neutral.
>>>
>
>> I had reason to look up the wring regs regarding using a surplus earth
>> as a neutral in my room thermostat. Definite no-no. Also wrapping the
>> visible end with blue tape also a no-no.
>
> Using an earth as a neutral is a way to ensure an instant RCD trip on a
> recent installation.

I've got fuses for everything except lighting. Less nuisance trips.

I have circuit breakers on the lighting to protect the PIR lighting system I put in my house which is a bit fragile to shorting if a bulb fails the wrong way.

I have no RCD. They don't protect me against fire, so I don't need them.
What's the difference between a church and a cinema?
In a church they say "Pray in the name of Jesus!"
In a cinema they say "Shut up for christ's sake!"

Adam Funk

unread,
Nov 20, 2012, 4:04:31 PM11/20/12
to
On 2012-11-20, John Rumm wrote:

> On 20/11/2012 14:12, bert wrote:
>> In message <k89qqm$s6v$1...@speranza.aioe.org>, Bill Wright
>> <bi...@invalid.com> writes
>>> Note that when you power your electric fire through coax you actually
>>> save on your electricity bill because the coax gets very hot and helps
>>> warm the room. There is no cost for this because it's the same
>>> electricity as is going through the fire, so you get the benefit of it
>>> twice.
>> <Snip>
>>
>> Err no. If you're getting heat out he cable it's because it has
>> resistance which reduces the total current through the cable/fire
>> combination.
>> Any heat gain in the cable has an equal reduction in the fire.
>
> I think you may have missed Bill's tongue being firmly in his cheek there!

It's OK as long as people don't try it!

ARW

unread,
Nov 20, 2012, 4:39:59 PM11/20/12
to
And as you a sandwich short of a picnic then we can ignore anything that you
say.

--
Adam


ARW

unread,
Nov 20, 2012, 4:41:10 PM11/20/12
to
Lieutenant Scott wrote:
> On Tue, 20 Nov 2012 14:21:58 -0000, bert <bert@[127.0.0.1]> wrote:
>
> > In message <op.wny4t9naytk5n5@i7-940>, Lieutenant Scott
> > <n...@spam.com> writes
> > > On Sat, 17 Nov 2012 02:54:36 -0000, Bill Wright
> > > <bi...@invalid.com> wrote:
> > > > malcolmf wrote:
> > > > > Is it acceptable in the uk to put a socket for a cctv camera
> > > > > off of a light switch?
> > > > >
> > > > Where will you get the neutral from?
> > >
> > > My light switches have a neutral. The mains is under the floor,
> > > comes up through the lightswitch, to the lighting in the ceiling.
> > >
> > > Just as well, as I fitted automatic lightswitch (with a PIR)
> > > which need power. Mind you one of my light switches for some reason
> > > doesn't have a
> > > neutral present. But earth suffices as a neutral.
> > >
> > I had reason to look up the wring regs regarding using a surplus
> > earth as a neutral in my room thermostat. Definite no-no. Also
> > wrapping the visible end with blue tape also a no-no.
>
> Earth and neutral are both zero volts, it works just fine.

Are you sure that they are always both zero volts?

--
Adam


Lieutenant Scott

unread,
Nov 20, 2012, 4:52:06 PM11/20/12
to
Says the guy without a response.
A sign at the golf course detailing the dress code:
Guys: No Shirts, No Golf
Girls: No Shirts, No Green Fees

Lieutenant Scott

unread,
Nov 20, 2012, 4:52:53 PM11/20/12
to
Near enough. I've never seen the difference be higher than a volt.
Two fish are in a tank. One says to the other, "I'll man the guns, you drive".

ARW

unread,
Nov 20, 2012, 5:01:12 PM11/20/12
to
My response is that you are a steaming great twat.

--
Adam


ARW

unread,
Nov 20, 2012, 5:03:05 PM11/20/12
to
Well there you go then "near enough" is the same thing as "equal". You thick
daft twat.
--
Adam


Lieutenant Scott

unread,
Nov 20, 2012, 5:10:11 PM11/20/12
to
Stop the troll-like behaviour and reply to the discussion in hand.
Maybe the grass looks greener on the other side of the fence because that is where the leaky septic tank is buried.

Lieutenant Scott

unread,
Nov 20, 2012, 5:11:04 PM11/20/12
to
It's equal as far as what we're discussing is concerned.

bert

unread,
Nov 20, 2012, 5:13:00 PM11/20/12
to
In message <op.wn3bcyx0ytk5n5@i7-940>, Lieutenant Scott <n...@spam.com>
writes
>On Tue, 20 Nov 2012 14:21:58 -0000, bert <bert@[127.0.0.1]> wrote:
>
>> In message <op.wny4t9naytk5n5@i7-940>, Lieutenant Scott <n...@spam.com>
>> writes
>>> On Sat, 17 Nov 2012 02:54:36 -0000, Bill Wright <bi...@invalid.com> wrote:
>>>
>>>> malcolmf wrote:
>>>>> Is it acceptable in the uk to put a socket for a cctv camera off of a
>>>>> light switch?
>>>>>
>>>> Where will you get the neutral from?
>>>
>>> My light switches have a neutral. The mains is under the floor, comes
>>> up through the lightswitch, to the lighting in the ceiling.
>>>
>>> Just as well, as I fitted automatic lightswitch (with a PIR) which
>>>need power.
>>>
>>> Mind you one of my light switches for some reason doesn't have a
>>> neutral present. But earth suffices as a neutral.
>>>
>> I had reason to look up the wring regs regarding using a surplus earth
>> as a neutral in my room thermostat. Definite no-no. Also wrapping the
>> visible end with blue tape also a no-no.
>
>Earth and neutral are both zero volts, it works just fine.
>
Earth & neutral are normally zero volts.
--
bert

John Rumm

unread,
Nov 20, 2012, 6:06:22 PM11/20/12
to
Until you get a circuit with a disconnected earth somewhere, then
everything metal in scotty's house is live because some clueless retard
decided it was ok to use the earth as a neutral.

Dave Plowman (News)

unread,
Nov 20, 2012, 6:20:55 PM11/20/12
to
In article <V7zGU8As...@nospam.co.uk>,
bert <bert@[127.0.0.1]> wrote:
> >Earth and neutral are both zero volts, it works just fine.
> >
> Earth & neutral are normally zero volts

Never heard of voltage drop in a circuit?

--
*If I agreed with you, we'd both be wrong.

Dave Plowman da...@davenoise.co.uk London SW
To e-mail, change noise into sound.

geoff

unread,
Nov 20, 2012, 6:21:17 PM11/20/12
to
In message <V7zGU8As...@nospam.co.uk>, bert <bert@[127.0.0.1]>
writes
Earth and neutral are normally connected at the local substation

but

RULE No 1

You always measure live wrt neutral NOT to earth

RULE No 2

see rule No 1


--
geoff

Lieutenant Scott

unread,
Nov 20, 2012, 7:31:39 PM11/20/12
to
On Tue, 20 Nov 2012 23:06:22 -0000, John Rumm <see.my.s...@nowhere.null> wrote:

> On 20/11/2012 22:13, bert wrote:
>> In message <op.wn3bcyx0ytk5n5@i7-940>, Lieutenant Scott <n...@spam.com>
>> writes
>>> On Tue, 20 Nov 2012 14:21:58 -0000, bert <bert@[127.0.0.1]> wrote:
>>>
>>>> In message <op.wny4t9naytk5n5@i7-940>, Lieutenant Scott <n...@spam.com>
>>>> writes
>>>>> On Sat, 17 Nov 2012 02:54:36 -0000, Bill Wright <bi...@invalid.com>
>>>>> wrote:
>>>>>

>>>>>
>>>>> My light switches have a neutral. The mains is under the floor, comes
>>>>> up through the lightswitch, to the lighting in the ceiling.
>>>>>
>>>>> Just as well, as I fitted automatic lightswitch (with a PIR) which
>>>>> need power.
>>>>>
>>>>> Mind you one of my light switches for some reason doesn't have a
>>>>> neutral present. But earth suffices as a neutral.
>>>>>
>>>> I had reason to look up the wring regs regarding using a surplus earth
>>>> as a neutral in my room thermostat. Definite no-no. Also wrapping the
>>>> visible end with blue tape also a no-no.
>>>
>>> Earth and neutral are both zero volts, it works just fine.
>>>
>> Earth & neutral are normally zero volts.
>
> Until you get a circuit with a disconnected earth somewhere, then
> everything metal in scotty's house is live because some clueless retard
> decided it was ok to use the earth as a neutral.

Bullshit. I'm not connecting LIVE to the earth, I'm connecting NEUTRAL to it.
It is bad luck to be superstitious.

Lieutenant Scott

unread,
Nov 20, 2012, 7:32:15 PM11/20/12
to
Yes always subtract zero and not zero. [shakes head]
"Boy, will I give YOU a haircut!" said Tom barbarously.

The Other Mike

unread,
Nov 20, 2012, 7:38:06 PM11/20/12
to
On Sun, 18 Nov 2012 05:35:53 +0000 (GMT), charles
<cha...@charleshope.demon.co.uk> wrote:

>In article <k89qqm$s6v$1...@speranza.aioe.org>,
> Bill Wright <bi...@invalid.com> wrote:
>> ARW wrote:
>
>> > CT100 would be Bill's prefered cable:-)
>> >
>> The best way to use coax for mains is to use the inner for line and the
>> outer for neutral. Don't bother about an earth.
>
>[Snip]
>
>Bill's not wrong. When a student and working with SSEB, I came across a
>small area in Edinburgh which was wired with "concentric" mains cable.

I've seen it used in the past year for a new installation of street
lighting, Single red core, spiral armour for combined neutral /
earth, probably still got a short offcut somewhere that I picked up.

John Rumm

unread,
Nov 20, 2012, 8:29:10 PM11/20/12
to
no knobstick, if you are placing a load between live and earth then you
are connecting live to earth.

Think how much current flows through the circuit when you disconnect the
earth - its a nice round number. Now apply ohms law to work out the
voltage drop across the load with zero current flowing through it.
Finally take that away from your mains supply voltage and you have the
voltage on your (previously) earthed metalwork.

Dave Liquorice

unread,
Nov 21, 2012, 5:20:19 AM11/21/12
to
On Tue, 20 Nov 2012 21:03:23 -0000, Lieutenant Scott wrote:

> I've got fuses for everything except lighting. Less nuisance trips.
>
> I have circuit breakers on the lighting to protect the PIR lighting
> system I put in my house which is a bit fragile to shorting if a bulb
> fails the wrong way.

Curious, fuses are far more tolerant of bulb failure than MCBs.

> I have no RCD. They don't protect me against fire, so I don't need
> them.

And the reasoning behind that is?

--
Cheers
Dave.



Steve Firth

unread,
Nov 21, 2012, 12:34:29 PM11/21/12
to
"Dave Liquorice" <allsortsn...@howhill.com> wrote:
> On Tue, 20 Nov 2012 21:03:23 -0000, Lieutenant Scott wrote:
[snip]

>> I have no RCD. They don't protect me against fire, so I don't need
>> them.
>
> And the reasoning behind that is?

That he is a troll and an idiot.

--
<•DarWin><|
_/ _/

Lieutenant Scott

unread,
Nov 21, 2012, 1:06:28 PM11/21/12
to
On Wed, 21 Nov 2012 01:29:10 -0000, John Rumm <see.my.s...@nowhere.null> wrote:

> On 21/11/2012 00:31, Lieutenant Scott wrote:
>> On Tue, 20 Nov 2012 23:06:22 -0000, John Rumm
>> <see.my.s...@nowhere.null> wrote:
>>
>>> On 20/11/2012 22:13, bert wrote:
>>>> In message <op.wn3bcyx0ytk5n5@i7-940>, Lieutenant Scott <n...@spam.com>
>>>> writes
>>>>> On Tue, 20 Nov 2012 14:21:58 -0000, bert <bert@[127.0.0.1]> wrote:
>>>>>

>>

>>>>>
>>>>> Earth and neutral are both zero volts, it works just fine.
>>>>>
>>>> Earth & neutral are normally zero volts.
>>>
>>> Until you get a circuit with a disconnected earth somewhere, then
>>> everything metal in scotty's house is live because some clueless retard
>>> decided it was ok to use the earth as a neutral.
>>
>> Bullshit. I'm not connecting LIVE to the earth, I'm connecting NEUTRAL
>> to it.
>
> no knobstick, if you are placing a load between live and earth then you
> are connecting live to earth.
>
> Think how much current flows through the circuit when you disconnect the
> earth - its a nice round number. Now apply ohms law to work out the
> voltage drop across the load with zero current flowing through it.
> Finally take that away from your mains supply voltage and you have the
> voltage on your (previously) earthed metalwork.

With fuck all current capabilities. We were talking about small loads remember.

That CRT over there has got millions of volts of static on it but for some reason it doesn't kill me when I touch it....
Peter is now listening to "Guo Yi & Guo Yue - Mongolian Horse"

Lieutenant Scott

unread,
Nov 21, 2012, 1:08:14 PM11/21/12
to
On Wed, 21 Nov 2012 10:20:19 -0000, Dave Liquorice <allsortsn...@howhill.com> wrote:

> On Tue, 20 Nov 2012 21:03:23 -0000, Lieutenant Scott wrote:
>
>> I've got fuses for everything except lighting. Less nuisance trips.
>>
>> I have circuit breakers on the lighting to protect the PIR lighting
>> system I put in my house which is a bit fragile to shorting if a bulb
>> fails the wrong way.
>
> Curious, fuses are far more tolerant of bulb failure than MCBs.

Exactly. When an incandescent blows in a shorted state (GU10 spots like to do this), the MCB trips quicker than the fuse. With the fuse, it's the PIR device that breaks first. And they cost more than an MCB.

>> I have no RCD. They don't protect me against fire, so I don't need
>> them.
>
> And the reasoning behind that is?

Because I'm not a pansy afraid of a shock.
If Christians want us to believe in a Redeemer, let them act redeemed. -- Voltaire

ARW

unread,
Nov 21, 2012, 2:35:38 PM11/21/12
to
Owain wrote:
> On Nov 20, 3:46 pm, John Williamson wrote:
> > You're right about the resistance in the cable causing it to heat
> > up. But... You save money per hour of running time due to the
> > reduced power drawn, but you also get less total heat per hour for
> > the same reason. The cost per kilowatt hour of heat is the same,
> > ignoring losses outside the room.
>
> Unless you're on a two-tier tariff, or one with a standing charge, in
> which case the average cost per kilowatt-hour will fall the more you
> use.

Smart arse:-)

--
Adam


GMM

unread,
Nov 21, 2012, 3:55:44 PM11/21/12
to
On 18/11/2012 16:07, critcher wrote:
> On 18/11/2012 14:50, Lieutenant Scott wrote:
>> On Sat, 17 Nov 2012 02:54:36 -0000, Bill Wright <bi...@invalid.com> wrote:
>>
>>> malcolmf wrote:
>>>> Is it acceptable in the uk to put a socket for a cctv camera off of a
>>>> light switch?
>>>>
>>> Where will you get the neutral from?
>>
>> My light switches have a neutral. The mains is under the floor, comes
>> up through the lightswitch, to the lighting in the ceiling.
>>
>> Just as well, as I fitted automatic lightswitch (with a PIR) which need
>> power.
>>
>> Mind you one of my light switches for some reason doesn't have a neutral
>> present. But earth suffices as a neutral.
>>
>
>
>
> critcher said...................
> I remember my mum plugging her electric iron into the light socket, but
> she couldn't see what she was ironing at night.

My Dad used to have some bayonet plugs so he could do that. On his
drill in particular as I recall. Of course in those days electrickery
wasn't as complcated and dangerous as it is now......;)

Andy Champ

unread,
Nov 21, 2012, 4:07:55 PM11/21/12
to
On 20/11/2012 21:52, Lieutenant Scott wrote:
> Near enough. I've never seen the difference be higher than a volt.

Not when I've measured it.

It took me a while to work out why the voltage N-L and L-E was the same,
and yet there was a voltage between them. Since then I;ve been taught a
little about AC...

Andy

bert

unread,
Nov 21, 2012, 4:06:46 PM11/21/12
to
In message <D8OdndFAJuNNojDN...@bt.com>, GMM
<GlMiMa-AT-yahoo.co.uk@?.?.invalid> writes
And the Elfin Safety hadn't been born.
--
bert

Lieutenant Scott

unread,
Nov 21, 2012, 4:28:55 PM11/21/12
to
He will be slaughtered one day, you'll see.
An actor works all his life to gain recognition.
He makes guest appearances, spends a lot for publicity people and agents etc.
Then, when he finally becomes well known, he complains he cannot go out in public anymore.

Lieutenant Scott

unread,
Nov 21, 2012, 4:29:39 PM11/21/12
to
Maybe you oughta get better wires. A big voltage drop on neutral indicates you're using crap wiring.
I'd rather have a life than a living.

AlanD

unread,
Nov 21, 2012, 4:35:51 PM11/21/12
to
On 18/11/2012 05:17, Bill Wright wrote:
> John Rumm wrote:
>
>>> CT100 would be Bill's prefered cable:-)
>>
>> It would only be fair, he had seen the way electricians wire aerials ;-)
>
> Don't get me started.
>
> http://www.wrightsaerials.tv/roguesgallery/035.shtml
>
> Bill

I particularly like this one:
http://www.wrightsaerials.tv/roguesgallery/042.shtml


Adam Funk

unread,
Nov 21, 2012, 4:49:33 PM11/21/12
to
I like the way everything is clearly colour-coded, mostly red.

John Rumm

unread,
Nov 21, 2012, 5:36:53 PM11/21/12
to
A 25W load (assuming its the only bodge like this you have done) would
pass 100mA. Plenty enough to kill you, and since you have not got a RCD,
and the current is not enough to open a fuse or MCB, you can be sure the
power will stay on long enough to get you properly dead.

> That CRT over there has got millions of volts of static on it but for
> some reason it doesn't kill me when I touch it....

Poke your finger into its 35kV EHT supply - that is only a few mA as well...

Lieutenant Scott

unread,
Nov 21, 2012, 6:20:07 PM11/21/12
to
Do you take me for some kind of pansy? Directly touching the live wire has never killed me, so 100mA certainly won't.

Anyway, that's 100mA if the voltage across me is zero. If we say it's half each, I get 120 volts, and the current is 50mA.

>> That CRT over there has got millions of volts of static on it but for
>> some reason it doesn't kill me when I touch it....
>
> Poke your finger into its 35kV EHT supply - that is only a few mA as well...

Yes, and 150 times more voltage than the mains. Both are important.
"Have you been hunting bear lately?"
"No, the grass tickles."

Lieutenant Scott

unread,
Nov 21, 2012, 6:22:58 PM11/21/12
to
Anyway, going back a bit...... someone suggested the problem occurs if the earth gets disconnected. So you're trying to blame one thing for another thing happening later. That's like saying it's my fault for parking my car on a double yellow line because then the guy doing 150mph through the built up area wouldn't have hit it.
Aristotle believed wind direction determined whether a baby would be a boy or a girl.

Dave Liquorice

unread,
Nov 21, 2012, 6:36:50 PM11/21/12
to
On Wed, 21 Nov 2012 18:08:14 -0000, Lieutenant Scott wrote:

>>> I've got fuses for everything except lighting. Less nuisance trips.
>>
>> Curious, fuses are far more tolerant of bulb failure than MCBs.
>
> Exactly. When an incandescent blows in a shorted state (GU10 spots
> like to do this), the MCB trips quicker than the fuse.

Bzinga.


--
Cheers
Dave.



Lieutenant Scott

unread,
Nov 21, 2012, 7:02:39 PM11/21/12
to
Which is WHY I have put MCBs in on those circuits. Understand?
"Th on my k yboard has stopp d working"

Java Jive

unread,
Nov 21, 2012, 9:24:55 PM11/21/12
to
No, a closer analogy would be reversing out of your drive instead of
reversing into it - it's making some sort of accident more likely,
like the one that killed the son of the neighbours of the keyboard
player in my ex wife's band.

The history of mankind generally and such aspects as air and rail
travel particularly demonstrate that sooner or later the rare
conditions required to create an accident occur in combination to
cause one.

By abusing one of the safety features of the UK electrical standards
you are deliberately making an accident, possibly a fatal one, more
likely. You are being a pillock.

On Wed, 21 Nov 2012 23:22:58 -0000, "Lieutenant Scott" <n...@spam.com>
wrote:
>
> Anyway, going back a bit...... someone suggested the problem occurs if the earth gets disconnected. So you're trying to blame one thing for another thing happening later. That's like saying it's my fault for parking my car on a double yellow line because then the guy doing 150mph through the built up area wouldn't have hit it.
--
=========================================================