Google Groups no longer supports new Usenet posts or subscriptions. Historical content remains viewable.
Dismiss

rendering an external wall - different mix for each coat?

697 views
Skip to first unread message

swimmydeepo

unread,
Apr 26, 2010, 5:30:12 AM4/26/10
to
I've just done the first layer (scratch coat)...the mix was 2 parts
cement + 3.5 sharp sand + 3.5 builder sand + waterproofer (Celtec).
I've ran out of Celtec and wondering if I can use a different mix for
the next coat - I have some LIME and some liquid waterproofer - what
would you recommend?
Shall I go buy some more Celtec or can I use a different mix with Lime
and/or liquid waterproofer for the next layers?

Andrew Gabriel

unread,
Apr 26, 2010, 11:23:27 AM4/26/10
to
In article <22216077-a288-477c...@c21g2000yqk.googlegroups.com>,

On the plastering and rendering course I did some years ago, we were
told you only include waterproofing in one of the two coats, assuming
you are applying the finish coat to the scratch coat whilst it's still
wet, as you should be (24-48h later). Otherwise the double waterproofing
can interfere with the drying out after it's set. IIRC, convention is
waterproof scratch coat when rendering in the summer, or waterproof the
finish coat when rendering in the winter (because wall dries out in a
different way in summer and winter). I'm not familiar with Celtec, so
check its instructions to see if they say something specific for it.

BTW, lime is not a waterproofer. In cement renders, its a plasticiser.
I could well imagine lime might interfere with the waterproofer (it
might use up proportionally more of the waterproofer because it's
more porous, making the waterproofer less effective, but see if the
waterproofer says anything about that). You can buy plasticiser, or
combined waterproofer/plasticiser, and many cements include plasticiser
admixtures anyway nowadays (it will say so on the bag if it does).

--
Andrew Gabriel
[email address is not usable -- followup in the newsgroup]

andrew

unread,
Apr 26, 2010, 5:43:14 PM4/26/10
to
Andrew Gabriel wrote:

> You can buy plasticiser, or
> combined waterproofer/plasticiser, and many cements include plasticiser
> admixtures anyway nowadays (it will say so on the bag if it does).

Our brickie seems to favour platiciser over lime plus it is a winteriser too
and allows work in cold temperatures. I think the waterproofer is added
separately.

I'm interested in adding external insulation (say 75mm celotex attached with
direct screw fittings, multi monti generic, and some wire mesh) and then
rendering over that with screed fibres to add more strength.

The reason being dense concrete blocks make for really fast construction
with no cavity and are cheaper than bricks but would this meet modern
building regs?

AJH

dennis@home

unread,
Apr 27, 2010, 3:10:20 AM4/27/10
to

"andrew" <ne...@sylva.icuklive.co.uk> wrote in message
news:83mfng...@mid.individual.net...

>
> I'm interested in adding external insulation (say 75mm celotex attached
> with
> direct screw fittings, multi monti generic, and some wire mesh) and then
> rendering over that with screed fibres to add more strength.
>
> The reason being dense concrete blocks make for really fast construction
> with no cavity and are cheaper than bricks but would this meet modern
> building regs?
>

They recently insulated a nine story(ish) block of flats by fixing
insulation slabs to the outside and rendering it.
AFAICS they were mineral wool slabs and I never drove past when there was
anything to support the render attached but I would think some sort of mesh
would be required. It appeared to be a well tried system as there were big
plastic disks tied through to the wall holding the slabs on and they
probably support the render too.

Remind me to look in 25 years and I will let you know how durable it is.
> AJH

swimmydeepo

unread,
Apr 27, 2010, 8:01:07 AM4/27/10
to
On Apr 26, 4:23 pm, and...@cucumber.demon.co.uk (Andrew Gabriel)
wrote:
> In article <22216077-a288-477c-837c-b6067673b...@c21g2000yqk.googlegroups.com>,

Thanks for your reply...
The message is clearer now: no plasticiser on second coat - this is
also recommended in other sites I've just visited.
I think I'm still going to use lime as an additive for the next coat.

Tim Lamb

unread,
Apr 27, 2010, 4:05:07 PM4/27/10
to
In message <83mfng...@mid.individual.net>, andrew
<ne...@sylva.icuklive.co.uk> writes

>Andrew Gabriel wrote:
>
>> You can buy plasticiser, or
>> combined waterproofer/plasticiser, and many cements include plasticiser
>> admixtures anyway nowadays (it will say so on the bag if it does).
>
>Our brickie seems to favour platiciser over lime plus it is a winteriser too
>and allows work in cold temperatures. I think the waterproofer is added
>separately.
>
>I'm interested in adding external insulation (say 75mm celotex attached with
>direct screw fittings, multi monti generic, and some wire mesh) and then
>rendering over that with screed fibres to add more strength.

Much what was done here for out re-build. Mind you ISTR BR only called
for 2.3W/m2 then, so we only got 25mm of Celotex.

Mesh was galvanised expanded metal lath and, yes you can see the cracks
where they join.


>
>The reason being dense concrete blocks make for really fast construction
>with no cavity and are cheaper than bricks but would this meet modern
>building regs?

Put 75mm on the inside with the plaster board ready attached. Met the BR
for our extension with external feather edge cladding but I guess render
would have been OK.

regards

--
Tim Lamb

Andrew Gabriel

unread,
Apr 27, 2010, 6:47:51 PM4/27/10
to
In article <bb678f95-6c5d-4cd9...@g11g2000yqe.googlegroups.com>,

swimmydeepo <swimm...@yahoo.co.uk> writes:
> Thanks for your reply...
> The message is clearer now: no plasticiser on second coat - this is
> also recommended in other sites I've just visited.
> I think I'm still going to use lime as an additive for the next coat.

Er, lime is a plasticiser, or did you mean no waterproofer?

Also, if you've left it more than 48 hours since scratch coat, I
don't know how well the two coats will bond. Probably worth looking
that up, as you might need to use a bonding agent (and if so, it will
have to be a waterproof one if your finish coat doesn't have a
waterproofer).

John Rumm

unread,
Apr 27, 2010, 8:04:28 PM4/27/10
to
Andrew Gabriel wrote:
> In article <bb678f95-6c5d-4cd9...@g11g2000yqe.googlegroups.com>,
> swimmydeepo <swimm...@yahoo.co.uk> writes:
>> Thanks for your reply...
>> The message is clearer now: no plasticiser on second coat - this is
>> also recommended in other sites I've just visited.
>> I think I'm still going to use lime as an additive for the next coat.
>
> Er, lime is a plasticiser, or did you mean no waterproofer?
>
> Also, if you've left it more than 48 hours since scratch coat, I
> don't know how well the two coats will bond. Probably worth looking
> that up, as you might need to use a bonding agent (and if so, it will
> have to be a waterproof one if your finish coat doesn't have a
> waterproofer).

You can leave the scratch coat a good deal longer if you like. So long
as its reasonably well keyed you should have no difficulty with the
finish coat. IIRC they used to leave it a week or more before doing the
top coat.

--
Cheers,

John.

/=================================================================\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\=================================================================/

John Rumm

unread,
Apr 27, 2010, 8:08:27 PM4/27/10
to
andrew wrote:
> Andrew Gabriel wrote:
>
>> You can buy plasticiser, or
>> combined waterproofer/plasticiser, and many cements include plasticiser
>> admixtures anyway nowadays (it will say so on the bag if it does).
>
> Our brickie seems to favour platiciser over lime plus it is a winteriser too
> and allows work in cold temperatures. I think the waterproofer is added
> separately.
>
> I'm interested in adding external insulation (say 75mm celotex attached with
> direct screw fittings, multi monti generic, and some wire mesh) and then
> rendering over that with screed fibres to add more strength.

I am seriously considering something similar for our place. From what I
have seen so far there are some nylon hammer in fixings with big round
mesh type heads. The idea being I believe that you slap up the
insulation with expanded metal lath over it, drill through the lot and
into the wall, then hammer the fixing in. Being nylon it does not form a
cold bridge.

What I am not sure about, is what type of render you can put on the
outside of it - whether ordinary sand and cement is ok, or if you need
something special and light weight. I can see some fibre re-enforcing
could be good.

Andrew Gabriel

unread,
Apr 28, 2010, 3:55:27 AM4/28/10
to
In article <k-CdncNYSfIQ5krW...@brightview.co.uk>,

John Rumm <see.my.s...@nowhere.null> writes:
> Andrew Gabriel wrote:
>> In article <bb678f95-6c5d-4cd9...@g11g2000yqe.googlegroups.com>,
>> swimmydeepo <swimm...@yahoo.co.uk> writes:
>>> Thanks for your reply...
>>> The message is clearer now: no plasticiser on second coat - this is
>>> also recommended in other sites I've just visited.
>>> I think I'm still going to use lime as an additive for the next coat.
>>
>> Er, lime is a plasticiser, or did you mean no waterproofer?
>>
>> Also, if you've left it more than 48 hours since scratch coat, I
>> don't know how well the two coats will bond. Probably worth looking
>> that up, as you might need to use a bonding agent (and if so, it will
>> have to be a waterproof one if your finish coat doesn't have a
>> waterproofer).
>
> You can leave the scratch coat a good deal longer if you like. So long
> as its reasonably well keyed you should have no difficulty with the
> finish coat. IIRC they used to leave it a week or more before doing the
> top coat.

Ideal is 24 hours, as the cement in the scratch coat still has enough
setting to do to actually bond with the finish coat, and at 24-48h,
the scratch coat should be ideally damp enough so you don't need to kill
the suction (which also kills the bond strength) although the waterproofer
may reduce the need for this.

After 48 hours, you may need to rely on something else to do the
bonding, such as keying and/or a bonding agent, as the cement bond
between the two coats rapidly becomes much weaker the longer the
time between the two coats.

swimmydeepo

unread,
Apr 29, 2010, 8:40:55 AM4/29/10
to
On Apr 28, 8:55 am, and...@cucumber.demon.co.uk (Andrew Gabriel)
wrote:
> In article <k-CdncNYSfIQ5krWnZ2dnUVZ7tdi4...@brightview.co.uk>,

>         John Rumm <see.my.signat...@nowhere.null> writes:
>
>
>
>
>
> > Andrew Gabriel wrote:
> >> In article <bb678f95-6c5d-4cd9-9ad2-dc5bf81c4...@g11g2000yqe.googlegroups.com>,

bonding agent like PVA or SBR?
Anyhow, it's been now about a week since I've done my first
coat...would it be feasible to use an angle grinder to improve the
keying? I've done the scratching but maybe I'll get a better and
deeper key...

stuart noble

unread,
Apr 29, 2010, 9:13:33 AM4/29/10
to

In my (somewhat limited) experience, keying is much overrated. On a
gable end wall I did, where some was properly keyed and, for reasons I
can't remember, some wasn't, it made no difference to how well the next
coat went on.

swimmydeepo

unread,
Apr 29, 2010, 4:09:09 PM4/29/10
to

"It made no difference"...do you mean the lot fell down in the same
way?
No disrespect here, but in my limited knowledge the main point of
keying (or scratching) is to improve adhesion between 2 coats - in
simpler words: to keep the second coat hanging in place as long as
possible (correct me if I'm wrong).

andrew

unread,
Apr 29, 2010, 5:17:31 PM4/29/10
to
Tim Lamb wrote:

AJH>>I'm interested in adding external insulation (say 75mm celotex attached
AJH>>with direct screw fittings, multi monti generic, and some wire mesh)
and
AJH>>then rendering over that with screed fibres to add more strength.


>
> Much what was done here for out re-build. Mind you ISTR BR only called
> for 2.3W/m2 then, so we only got 25mm of Celotex.

What sort of U value does one of these zero energy houses aim for in the
wall? I work on a block of flats that has 10" of glass fibre filled cavity
and 100mm of celotex should be near that. From the way the boiler runs in
cold weather each flat seems to require 2.5kW. and I guess a small flat is
around 250m^3 so with 2 air changes an hour you could lose 3.5kW without
heat recovery for a delta T 20C.


>
> Mesh was galvanised expanded metal lath and, yes you can see the cracks
> where they join.

All the more reason to add screed fibres?


>>
>>The reason being dense concrete blocks make for really fast construction
>>with no cavity and are cheaper than bricks but would this meet modern
>>building regs?
>
> Put 75mm on the inside with the plaster board ready attached. Met the BR
> for our extension with external feather edge cladding but I guess render
> would have been OK.
>

I've already done this on a store room that has been converted to an office
but I used extraliner 12mm plasterboard with 50mm celotex, quite expensive
at GBP30/sheet. I raised the floor with 75mm celotex and 75mm of screed
with 150' of polyplumb spiral embedded in it.

stuart noble

unread,
Apr 30, 2010, 4:39:29 AM4/30/10
to

>> In my (somewhat limited) experience, keying is much overrated. On a
>> gable end wall I did, where some was properly keyed and, for reasons I
>> can't remember, some wasn't, it made no difference to how well the next
>> coat went on.
>
> "It made no difference"...do you mean the lot fell down in the same
> way?
> No disrespect here, but in my limited knowledge the main point of
> keying (or scratching) is to improve adhesion between 2 coats - in
> simpler words: to keep the second coat hanging in place as long as
> possible (correct me if I'm wrong).

AFAIK...AIUI...IME...etc etc...
The bond between coats operates at a microscopic level, so that mortar
sticks to the face of a brick even though it has no visible grooves or
scratches.
Keying helps reduce the initial slump when the mortar is trowelled on to
a large, flat area, but doesn't affect the long term adhesion. IOW it's
less arm work for the plasterer.
When I was young and inexperienced, I built a breeze block garden wall
and got a plasterer in to render it. He told me to pva the blocks, so I
did 3 or 4 coats on to be on the safe side, with the result that the
wall had a nice satin sheen :-). When he arrived to do the render, he
raised his eyes to the heavens and said he couldn't do the job because
the render would slide down the wall. However, once suction took over,
the stuff went on well, and stayed on for at least 2 decades until the
house was sold.
On this basis I have every confidence that you could successfully render
a sheet of glass. You can certainly render flimsy plastic pots

> [IMG]http://i39.tinypic.com/fxgnm.jpg[/IMG]

swimmydeepo

unread,
Apr 30, 2010, 4:54:21 AM4/30/10
to


Did you use PVA diluted? If so what percentage of water?

stuart noble

unread,
Apr 30, 2010, 5:44:58 AM4/30/10
to

For what? The wall, or the pot?

swimmydeepo

unread,
Apr 30, 2010, 8:25:08 AM4/30/10
to

the wall of course...
For the first coat I did use some PVA diluted initially but it dried
out too quickly and the rendering kept falling - I managed in the end
but I guess I've wasted 50% of the mixing on the floor...so I decided
to use just water and in my case it made the job much easier.

stuart noble

unread,
Apr 30, 2010, 8:31:47 AM4/30/10
to

>>> Did you use PVA diluted? If so what percentage of water?
>> For what? The wall, or the pot?
>
> the wall of course...

Dunno, it was over 30 years ago. Nowadays I find 1 pva to 4 water about
right for most jobs.


Andrew Gabriel

unread,
May 1, 2010, 7:49:12 AM5/1/10
to
In article <1c3e0a8b-34fd-4914...@i9g2000yqi.googlegroups.com>,

swimmydeepo <swimm...@yahoo.co.uk> writes:
> On Apr 28, 8:55�am, and...@cucumber.demon.co.uk (Andrew Gabriel)
> wrote:
>>
>> > You can leave the scratch coat a good deal longer if you like. So long
>> > as its reasonably well keyed you should have no difficulty with the
>> > finish coat. IIRC they used to leave it a week or more before doing the
>> > top coat.
>>
>> Ideal is 24 hours, as the cement in the scratch coat still has enough
>> setting to do to actually bond with the finish coat, and at 24-48h,
>> the scratch coat should be ideally damp enough so you don't need to kill
>> the suction (which also kills the bond strength) although the waterproofer
>> may reduce the need for this.
>>
>> After 48 hours, you may need to rely on something else to do the
>> bonding, such as keying and/or a bonding agent, as the cement bond
>> between the two coats rapidly becomes much weaker the longer the
>> time between the two coats.
>
> bonding agent like PVA or SBR?
> Anyhow, it's been now about a week since I've done my first
> coat...would it be feasible to use an angle grinder to improve the
> keying? I've done the scratching but maybe I'll get a better and
> deeper key...

Yes, but not PVA (as it's water soluable) unless you use waterproofer
in the finish coat too (which is probably OK now the scratch coat is
well dry).

To be honest, I think you need to consult a professional at this point
or you might end up with something which fails and is difficult to put
right.

stuart noble

unread,
May 1, 2010, 8:21:51 AM5/1/10
to
Andrew Gabriel wrote:
> In article <1c3e0a8b-34fd-4914...@i9g2000yqi.googlegroups.com>,
> swimmydeepo <swimm...@yahoo.co.uk> writes:
>> On Apr 28, 8:55 am, and...@cucumber.demon.co.uk (Andrew Gabriel)
>> wrote:
>>>> You can leave the scratch coat a good deal longer if you like. So long
>>>> as its reasonably well keyed you should have no difficulty with the
>>>> finish coat. IIRC they used to leave it a week or more before doing the
>>>> top coat.
>>> Ideal is 24 hours, as the cement in the scratch coat still has enough
>>> setting to do to actually bond with the finish coat, and at 24-48h,
>>> the scratch coat should be ideally damp enough so you don't need to kill
>>> the suction (which also kills the bond strength) although the waterproofer
>>> may reduce the need for this.
>>>
>>> After 48 hours, you may need to rely on something else to do the
>>> bonding, such as keying and/or a bonding agent, as the cement bond
>>> between the two coats rapidly becomes much weaker the longer the
>>> time between the two coats.
>> bonding agent like PVA or SBR?
>> Anyhow, it's been now about a week since I've done my first
>> coat...would it be feasible to use an angle grinder to improve the
>> keying? I've done the scratching but maybe I'll get a better and
>> deeper key...
>
> Yes, but not PVA (as it's water soluable)

Not actually soluble. "Sensitive to prolonged contact with water" is the
official terminology I think. Not really important here as you're only
stopping the base coat sucking the water out of your mortar, which it
probably wouldn't anyway.


unless you use waterproofer
> in the finish coat too (which is probably OK now the scratch coat is
> well dry).
>
> To be honest, I think you need to consult a professional at this point
> or you might end up with something which fails and is difficult to put
> right.
>

Nah, suck it and see. Do a patch and, if it still looks good next
morning, it's probably there for good.

0 new messages