On 31/12/2011 17:50, Lieutenant Scott wrote:
> On Wed, 30 Nov 2011 20:13:10 -0000, Roger Mills <
watt....@gmail.com>
> wrote:
>
>> On 30/11/2011 18:47, Lieutenant Scott wrote:
>>> On Wed, 30 Nov 2011 17:57:01 -0000, ARWadsworth
>>> <
adamwa...@blueyonder.co.uk> wrote:
>>>
>>
>>>>
>>>>
>>>> A C Plan is independant HW and CH and does use a motorised valve. See
>>>>
>>>>
http://wiki.diyfaq.org.uk/index.php?title=Central_Heating_Controls_and_Zoning#Gravity_DHW:_C-Plan
>>>>
>>>>
>>>>
>>>> When HW is not called for via the cylinder stat or programmer then the
>>>> valve
>>>> for the HW is closed.
>>>
>>> Can you therefore have:
>>>
>>> HW only
>>> heating only
>>> Both?
>>>
>>
>> YES! That's precisely the point of it. With a 'conventional' gravity HW
>> and pumped CH system (which was what you initially described), you can't
>> - you have to run the boiler to make the CH work, and that heats the HW
>> whether you want it or not.
>
> Mine does this very simply, one valve for the hot water, one for the
> heating. You can't have three choices with a valve with two positions!
>
All together now - OH YES YOU CAN!! You're forgetting that the pump also
comes into the equation, but - in a gravity HW and pumped CH system
(which is where C-Plan is used) is only used for the CH. Thus:
Boiler on, Valve open, pump off - HW only
Boiler on, valve closed, pump on - CH only
Boiler on, valve open, pump on - both together
*I* make that *three* - what say *you*?
Presumably your system is fully pumped and is thus not relevant to a
discussion about C-Plan.
>> BUT, convert it to a C-Plan, and that all changes. A C-Plan system has a
>> motorised valve in the gravity HW circuit and a thermostat on the HW
>> cylinder. The auxiliary switch on the valve (which needs to be of the
>> change-over variety) is wired in a cunning way which provides the
>> following:
>> HW only: Valve opens, boiler runs until cylinder stat satisfied, then
>> boiler shuts down
>> CH only: Valve closes, boiler and pump run until room stat satisfied,
>> then boiler and pump shut down
>> Both: Valve opens, boiler and pump run. As soon as HW or CH demand
>> satisfied, system operates as per CH only or HW only, as appropriate.
>> When both demands are satisfied, the system shuts down.
>
> What causes the difference in operation between HW only and HW + CH?
>
The PUMP - see above. If you want to understand it, you'll need to study
the C-Plan circuit diagram shown in the reference above. The valve's
auxiliary change-over switch is the cunning bit to watch. When there is
only a CH demand - so that the valve is closed - the programmer/room
stat switch the pump and the contacts in the valve switch the boiler.